Question: So, Can someone break this down for me.Situation:You have a single phase 480V to ??? transformer. This transformer is for a resistance welder. You remove one leg on the primary side of the transformer, but the other leg is still attached and is hot. On the secondary side. There is 66V to Ground. There is no ground involved on the transformer but the rest of the machine is grounded. The hot leg is straight from the incoming to the transformer. The SCR for the other leg is off when checked.Question:Is this 66V to ground hazardous?Thoughts:My initial thoughts were yes. Thought was if you have a difference in voltage and continuity then you get current flow. But after thinking about it. If you don't have any current flow in the primary side of the transformer. Would you be able to move current in the secondary side?

Okay, let's break this down step by step. This is an interesting scenario and highlights some important electrical safety principles.

Understanding the Setup Single-Phase 480V Transformer

You have a transformer stepping down 480V to a lower voltage (we don't know the exact secondary voltage, but it's designed for the welder). Single-phase transformers have two primary windings and two secondary windings, connected to a magnetic core.


Resistance Welder

These welders work by passing a high current through the metal pieces being joined. They require significant current at a relatively low voltage.

One Primary Leg Removed, One Hot

This is the critical problem. You've disconnected one of the 480V legs feeding the
primary side of the transformer, but the other leg is still connected and energized.

SCR (Silicon Controlled Rectifier)

You have SCR controlling one of the legs that is disconnected,

66V to Ground on the Secondary

This is what you're measuring. You're using a voltmeter, placing one lead on a point in the
secondary circuit and the other on a known good ground point within the machine.

Transformer Not Grounded (Directly)

The transformer casing itself isn't directly connected to ground. However, you mention the rest of the machine is grounded, which is important.

The Key Issue: Capacitive Coupling and Stray Voltage


The 66V you're measuring isn't likely due to the transformer actively stepping down voltage with a closed primary circuit. Instead, it's almost certainly due to capacitive coupling and stray voltage. Here's why:1. Capacitive Coupling

Even though the primary circuit is "open" (one leg disconnected), the primary windings of the transformer are physically close to the secondary windings. They are separated by insulation and the transformer core, forming a capacitor. Capacitance allows AC voltage to "leak" or "couple" from the energized primary winding to the secondary winding. The amount of voltage that leaks depends on the quality and size of the capacitor, as well as the frequency.2.

High Impedance Path to Ground

Your voltmeter is a very high impedance device. It detects a voltage by measuring the potential difference between two points. Even a very small current flowing through a very high impedance can register a significant voltage. The path from the secondary winding, through the machine's internal wiring and components, to the ground point you're using, likely represents this high impedance path.3.

No Primary Current Flow (Essentially)

With one leg of the primary disconnected, you essentially have an open circuit. Very little actual current can flow in the primary winding. A tiny bit of current might flow due to the primary winding's capacitance (acting as a capacitor connected to the hot leg), but this current will be very small.

Is 66V Hazardous?
Yes, it can be hazardous. Here's why: Perception Threshold

While 66V is below the commonly cited "50V as the threshold for hazardous voltage," it's still
enough to be felt and cause a startle reaction. A startle reaction near welding equipment or other machinery can lead to secondary accidents.

Under the Right Conditions, Current Can Flow

While the current available is likely very limited, under the right conditions, even a small current can be dangerous. If someone with wet or sweaty skin touches a conductive part of the secondary circuit, they could provide a lower impedance path to ground. This can increase the current flow through their body.

"Let-Go" Threshold

The real danger isn't necessarily the initial shock, but the ability to
let go. Current levels above the "let-go" threshold can cause muscle contractions, making it impossible to release your grip on the energized object. This can prolong exposure and increase the risk of injury.

Fault Conditions

The 66V indicates a fault or abnormal condition. It's a warning sign that something isn't right. Ignoring it could lead to more serious problems later, including insulation breakdown and higher voltage leakage.

Compliance

Safety standards generally frown upon exposed voltage like this. There are often regulations requiring voltage to be below a certain threshold to be considered safe to touch.

Answering Your Question Directly

You asked: "If you don't have any current flow in the primary side of the transformer. Would you be able to move current in the secondary side?"The answer is: Technically, yes, a
very small amount of current can be induced in the secondary side due to capacitive coupling from the energized primary leg. This small current, finding a high-impedance path to ground, can register as 66V on your voltmeter. While the current available is limited, it's still potentially hazardous under the right circumstances.
Recommendations
1. Isolate the Transformer Immediately

The safest course of action is to disconnect the remaining energized primary leg. Lockout/Tagout (LOTO) procedures should be followed.2.

Troubleshoot the Transformer and Welder

Determine why there's voltage on the secondary side with the primary "open." Check the insulation resistance of the transformer windings (primary to secondary and primary to core). Look for any signs of insulation breakdown.3.

Grounding

Ensure the transformer frame and the welder chassis are properly grounded according to applicable electrical codes. This will provide a low-impedance path to ground, which can help to mitigate the risk of stray voltage and provide a return path for fault currents.4.

Consult a Qualified Electrician

It's highly recommended to have a qualified electrician investigate the situation. They have the expertise and test equipment to properly diagnose the problem and ensure the welder is safe to operate.

In summary, the 66V to ground you're measuring
is* a potential hazard, and you should take immediate steps to isolate the equipment and troubleshoot the problem. Do not assume that because the primary circuit is "open," the secondary side is safe. Capacitive coupling and stray voltage can create dangerous conditions. Flag for review