Question: Was replacing a load center at an rv park. Got tone took reading before energizing system.Checking anything to ground and phase to phase.I went and got 230ohms from phase be of one breaker to phase a of another. Both go in seperate pipes.Was puzzled. So unplugged all units. Turned each breaker one at a time to see if I got any back feeding on another breaker. Non…Plugged units in and repeated process. If I did have a phase crossed from breakers I would have saw it here. Non. Took reading to neutral bar. Everything was cool. Turned off all breakers double checked that line in question.Now that is gone????These are direct buried wires each 100 amp breaker feeds two sites.Could it just have been induced voltage causeing that reading from the meter.Using a flukexxfc forgot number.Thought maybe a fault in the ground that go cleared maybe??? Just weird. All working nowAny thoughts

You've described a situation that's definitely puzzling, but the fact that it resolved itself is valuable information. Here's a breakdown of possible causes and what you did right

Possible Causes for the 230 Ohm Reading (Phase A to Phase B of Different Breakers):
Shared Neutral/Ground Issues (Likely Candidate, but you addressed it)

This is a common culprit in RV parks with long runs and multiple connections. While you unplugged all units, a slightly loose neutral connection in the park's wiring
before the load center you were working on could have created a path where current from one phase could bleed onto another. This could be somewhere further up the line feeding the load center. Because the resistance is relatively low (230 ohms), this would suggest a metallic path is present. Unplugging everything reduced the load and might have subtly changed the impedance of the problem connection, temporarily masking it. Even though you addressed this in your testing it is still suspect.



Moisture/Contamination in Conduit or Connections

Water intrusion, especially with mineral content, can create a conductive path between wires, even if the insulation is otherwise intact. This is more likely in direct-buried runs. Heat from a load could have dried up the moisture or changed the conductive properties.

Failing Insulation (Less Likely, but Possible)

Small pinholes or cracks in insulation on the conductors could allow leakage, especially in damp conditions. Again, temperature changes could affect this.


Induced Voltage (Unlikely at that Resistance)

Induced voltage (from magnetic fields around conductors) is possible, but typically results in a very high impedance/resistance reading (megohms, not ohms) when measured with a standard multimeter. 230 ohms is too low to be solely induced voltage.

Transient Voltage from a Device

A capacitor or other component in a plugged-in RV could have temporarily created a conductive path when you first energized the system. Unplugging everything would have cleared this.

What You Did Right



Took Initial Readings (Critical!)

This gives you a baseline to compare against.

Systematic Troubleshooting

Unplugging loads and selectively energizing breakers is the right approach to isolate the problem.


Phase to Neutral Checks

Verifying normal voltage to neutral on each phase is essential.

Double-Checked Connections

Retorquing connections (if applicable) can resolve many issues.


Documenting Readings and Actions

Keeping a record of what you did and the results is important for future reference.

Next Steps and Considerations


Monitor for Recurrence

This is key. The fact that the problem went away doesn't mean it's fixed. Closely monitor the system for any future voltage anomalies, especially under different load conditions.2.

Record Load Center Readings

While everything is working, record the following: Voltage: Phase A to Neutral, Phase B to Neutral, Phase A to Phase B Current: Amperage on each leg of the main breaker with a typical RV park load. You can use a clamp meter. Ground Resistance: Measure the resistance from the ground bar in the load center to a known good grounding point (e.g., a properly driven ground rod).3.

Check and Retorque

Go back over every connection in the load center. Ensure they are clean and properly tightened to the manufacturer's torque specifications.4.

Neutral Bonding

Verify the neutral is only bonded to ground at the service entrance. A secondary bond can create parallel neutral paths which can cause issues. RV Parks often have more than one place where the neutral is bonded to ground which causes many problems.5.

Grounding System Review

RV parks are notoriously prone to grounding issues.


Ground Rods

Ensure all ground rods are properly installed and bonded together.

Grounding Conductor Size

Verify the size of the grounding conductor is appropriate for the size of the service.6.

Consider an Insulation Resistance Tester (Megger)

If you suspect insulation breakdown, a megger applies a high DC voltage to the wires and measures the leakage current. This can often detect subtle insulation problems that a standard multimeter won't find.
This is especially useful if you suspect direct burial cable issues.7.

Documentation

If you have a map of the direct buried conductors that would assist in future trouble shooting.8.

Engage a Qualified Electrician

Direct-buried wire problems in RV parks can be complex and potentially dangerous. If the problem recurs or you're uncomfortable with any of the above steps, it's best to consult a licensed electrician experienced in RV park electrical systems. They can perform more in-depth testing and diagnosis.

In summary

The most likely culprit is a shared neutral or ground issue. Direct buried cable is also suspect. Your systematic troubleshooting was good, but continued monitoring and potentially more advanced testing are warranted to ensure the problem is truly resolved. The RV park environment introduces significant electrical challenges, so a thorough investigation is worthwhile.