Question: Is there an advantage to locating breakers with a high amp draw closer to the main breaker or incoming lugs? 120/240V single phase system.I’ve got a load center with 2 open slots but it’s at the very bottom.It’s for an electric kiln at a residence. I can’t re distribute breakers and get to the top,It’s a 70 amp load.Thanks
There's no significant electrical advantage to placing a high-amp breaker closer to the main breaker or incoming lugs in a properly installed and sized residential panel. Here's why: Busbar Capacity
The busbars inside your load center are designed to distribute the entire panel's rated current evenly. They're sized to handle the total load of all the breakers simultaneously (up to the panel's rating). The location of the breaker on the busbar doesn't matter in terms of the busbar's ability to carry current.
Voltage Drop
In a well-designed electrical system, voltage drop should be minimal regardless of the breaker's position. The relatively short distance across a panel's busbars doesn't introduce significant voltage drop. Wire size from the panel to the kiln is much more important for voltage drop.
Neutral/Grounding
The neutral and grounding connections are common for all breakers. Location within the panel doesn't affect their performance.
However, there are practical considerations unrelated to electrical performance that might influence your decision
Wire Management/Access
Running the heavy gauge wire (likely 4 AWG copper or 2 AWG aluminum for a 70A kiln) to the bottom slots might be more challenging, and can impact neatness. Can you easily route the wire down the side of the panel without creating excessive bends or obstructions?
Code Compliance
Ensure that the wire bends and the amount of wire inside the panel meet electrical code requirements (e.g., minimum bending radius).
Future Expansion
Consider whether the location impacts future panel expansion or access to other circuits. If you plan to add more circuits later, the bottom location might become inconvenient if it's crowded.
Accessibility for Disconnect
Consider the location if you need to disconnect the circuit quickly for maintenance or safety reasons.
In your situation (70A load, open slots at the bottom, inability to redistribute breakers)
Given that you cannot rearrange breakers, and the busbar is designed to handle the load regardless of position, the primary concern becomes:1.
Wire Routing and Connections
Can you safely and code-compliantly route the heavy gauge wire to the bottom slots? This is the most important factor. Make sure you have enough slack and can make secure, proper connections.2.
Panel Fill
Will running the large wire to the bottom create a crowding issue that makes it difficult to work on other circuits?
Recommendation
If you can route the wire to the bottom slots safely and without causing excessive crowding, it's perfectly acceptable to install the 70A breaker there. Just prioritize proper wire management and connections. If routing the wire to the bottom creates significant challenges or potential code violations, consider other options such as:
Subpanel
A subpanel closer to the kiln location could be a more manageable solution, especially if you anticipate adding more circuits for the kiln area in the future.*
Professional Consultation
Consult a licensed electrician. They can assess your specific situation, advise on code-compliant solutions, and ensure the safe and proper installation of the breaker and wiring. Running a 70-amp circuit is not a DIY project if you lack experience. Improper installation can create a fire hazard.
Safety First: Always de-energize the panel before working on any electrical components. If you are not comfortable working with electricity, hire a qualified electrician. Flag for review