Question: Hello. I have a 120/208v distribution center. I have these ttwo fixture type that are site lights. What calcution would I use to determine circuit size? Also VD would be an issue as they are 500 to 800' away from source. I'm think I can use 20A breaker(s) but would need ot upsize wire then tap it down at panel and when I branch off to fixtures. Does that make sense?
Okay, let's break down the circuit sizing and voltage drop considerations for your site lights, keeping in mind the long distances involved. Your initial thought about using 20A breakers and upsizing the wire is a good starting point, but we need to do the calculations to confirm.
Here's a step-by-step approach
1. Gather Information (Critical) Fixture Wattage (or Amperage)
The most important piece of information. You absolutely must know the wattage (or amperage) of each individual light fixture. If it's a High-Pressure Sodium (HPS), Metal Halide (MH), or LED fixture, get the
actual input wattage from the fixture's nameplate or specifications. Don't guess. If you have amperage, Wattage = Volts x Amps. Number of Fixtures per Circuit
How many of each fixture type do you plan to put on a single circuit? This is a design decision you'll need to make. More fixtures per circuit will save on conduit and wiring costs, but will increase the load on the circuit and may require larger wire.
Distance
Get the actual distance from your distribution panel to the furthest light fixture on each circuit. This is crucial for voltage drop calculations. If you're running in a loop, use the longest point to the furthest load.
Ambient Temperature
What's the maximum ambient temperature where the wiring will be installed? This affects the ampacity of the conductors. If it's likely to exceed 30°C (86°F), you'll need to adjust the conductor ampacity.
Wiring Method
How will the wiring be run? (e.g., in conduit, direct burial, cable tray). This determines the allowable ampacity of the conductors. If it's conduit, what type of conduit?
Conductor Type
What type of conductor are you planning to use (e.g., THHN, XHHW, USE)? Different conductor types have different temperature ratings and ampacities.
2. Calculate Circuit Load Total Wattage per Circuit
Multiply the wattage per fixture by the number of fixtures on the circuit. Example: If you have 5 fixtures, each drawing 200 watts, the total wattage is 5 200 = 1000 watts.
Calculate Circuit Amperage
Divide the total wattage by the voltage (208V in your case). Then, multiply by 1.25 (125%). This covers continuous loads. Formula: Amps = (Total Wattage / Voltage) 1.25 Example: Amps = (1000 watts / 208 volts) 1.25 = 6.01 amps
3. Determine Minimum Conductor Size (Based on Ampacity) Refer to NEC Table 310.16 (or the appropriate table in your local code) to determine the minimum conductor size required to carry the calculated amperage after any derating factors (ambient temperature, number of conductors in a raceway, etc.). Example: If your calculated amperage is 6.01 amps and you are using THHN conductors in conduit at an ambient temperature of 30°C or less, you might think 14 AWG is sufficient, but this is likely wrong due to voltage drop issues. You'll likely need to upsize significantly.4. Voltage Drop Calculation
This is the critical step given the long distances. Use a voltage drop calculator. There are many free ones online. I recommend Southwire's. You need the following inputs: Voltage
208V (phase-to-phase)
Current
Calculated Amps from Step 2
Distance
Length of the run (one way) in feet
Conductor Size
Start with a reasonable guess (e.g., 12 AWG, 10 AWG, 8 AWG) and iterate.
Conductor Material
Copper or Aluminum (Copper is almost always preferred for long runs).
Power Factor
Estimate the power factor of your fixtures. If you don't know, use 0.85 for inductive loads (like HPS or MH) and 0.95 for LED. A higher power factor means less voltage drop.
Conductors per phase
This should be one.
Allowable Voltage Drop
The NEC recommends no more than 3% voltage drop for branch circuits (NEC 210.19(A) FPN No. 4) and no more than 5% total voltage drop (feeder + branch circuit). For a 208V system, 3% is 6.24V and 5% is 10.4V. Aim for 3% or less on the branch circuit.
Iterate
Keep increasing the conductor size until the voltage drop is within the acceptable limit (3% or less).
5. Overcurrent Protection (Breaker Size) The breaker size must protect the smallest conductor in the circuit. In most cases, this will be the conductors feeding the lights themselves. You can use a larger breaker (e.g., 20A) to protect a larger conductor (e.g., 8 AWG) if you tap down to a smaller conductor (e.g., 12 AWG) close to the load and that smaller conductor is protected by a smaller overcurrent device (e.g., a fuse) at the tap point (NEC 240.21). However, this is cumbersome and prone to errors.6. Tapping Down (If Necessary)
NEC 240.21 governs tap rules. There are specific requirements for the length of the tap conductors, the ampacity of the tap conductors relative to the upstream overcurrent protection, and the location of the overcurrent protection at the tap. Violating tap rules is a common code violation. A safer and often simpler approach is to run the larger conductor the entire distance and connect directly to the fixture. This eliminates the complexity of tap rules.7. Grounding Run an equipment grounding conductor (EGC) along with the circuit conductors. Size the EGC according to NEC Table 250.122, based on the overcurrent protection device (the breaker size).
Your Upsizing and Tapping Idea
Your idea of upsizing the wire at the panel and tapping down closer to the fixtures can work, but it requires careful attention to the NEC tap rules. It adds complexity and potential points of failure/inspection issues.
Example Scenario
Let's say you have 10 LED fixtures, each drawing 100 watts, and the distance to the furthest fixture is 600 feet. You're using THHN copper conductors in conduit.1.
Total Wattage
10 fixtures 100 watts/fixture = 1000 watts2.
Calculated Amperage
(1000 watts / 208 volts) 1.25 = 6.01 amps3.
Ampacity
A 14 AWG THHN conductor is rated for 15 amps in typical conditions. However, voltage drop will be a bigger issue here.4.
Voltage Drop
Using Southwire's voltage drop calculator, for a 6.01 amp load, 600 feet, 208V, Copper conductor: 14 AWG: 14.5% voltage drop (Unacceptable) 12 AWG: 9.1% voltage drop (Unacceptable) 10 AWG: 5.7% voltage drop (Unacceptable) 8 AWG: 3.6% voltage drop (Unacceptable) 6 AWG: 2.3% voltage drop (Acceptable)5.
Conclusion
You would need to use a 6 AWG conductor to keep the voltage drop below 3%. You would then use a 20 amp breaker, assuming there are no other loads on the circuit that would cause it to exceed the 80% rule.
Recommendations
Run Larger Conductors the Entire Distance
For simplicity and to avoid tap rule complications, consider running the appropriately sized conductor (based on voltage drop calculations) the entire distance from the panel to each fixture. This is often the most cost-effective approach in the long run.
Consider Higher Voltage
If feasible, investigate using a higher voltage (e.g., 277V) for the site lighting. This would significantly reduce the current and voltage drop, allowing for smaller conductors. However, it would require different fixtures and may have other cost implications.
Consult with a Qualified Electrician
This is a MUST. Given the long distances and the potential for voltage drop issues, it's crucial to have a qualified electrician review your plans and perform the installation. They can ensure that the wiring is properly sized, installed according to code, and safe.
Important Reminders
NEC Compliance
All electrical work must comply with the National Electrical Code (NEC) and any applicable local codes.
Safety
Electrical work can be dangerous. Always de-energize circuits before working on them, and follow proper safety procedures.
Permitting: Obtain any necessary permits from your local electrical inspector before starting work.This information is for guidance only. You must* consult with a qualified electrician for the final design and installation of your site lighting system. They can perform the necessary calculations, ensure code compliance, and provide a safe and reliable installation. Flag for review