Topic: Please explain this 705.12 rule

User: electrofelon, Location: Cherry Valley NY, Seattle, WA

Asked on: Wednesday, October 9, 2024 at 12:22 pm EDT
Answered on: Thursday, March 6, 2025 at 3:40 am EST

Question: (2)Taps. In systems where power source output connections are made at feeders, any taps shall be sized based on the sum of 125 percent of the power source(s) output circuit current and the rating of the overcurrent device protecting the feeder conductors as calculated in 240.21(B).

This section of code describes how to size tap conductors in systems where power is drawn from feeders (main supply lines). Here's a breakdown of the important parts: "Taps": These are conductors that branch off from a larger feeder conductor to supply power to a load (like equipment, appliances, etc.). "Power source output connections made at feeders": This means the connection of the output of a power source(s) to the feeder conductors. "sized based on the sum of": The ampacity (current-carrying capacity) of the tap conductors needs to be large enough to handle the following: "125 percent of the power source(s) output circuit current": This means you take the rated current of the power source output, multiply it by 1.25 (to provide a safety margin), and add that value to the ampacity. "the rating of the overcurrent device protecting the feeder conductors": You also need to consider the rating of the circuit breaker or fuse that protects the main feeder conductors. This value is then added to the ampacity. "as calculated in 240.21(B)": This directs you to another section of the electrical code (240.21(B)) for further guidance and rules on tap conductor protection, allowable tap lengths, and other important considerations.

In simpler terms

When you're tapping off a feeder for power, the wire you use for the tap needs to be big enough to handle the load you're drawing plus account for the protection on the feeder conductors. You also have to oversize the current of the load by 25 percent as a safety factor. You also need to ensure it meets the requirements of section 240.21(B).

Why this is important

This rule is vital for electrical safety because it helps:

Prevent overheating

By sizing the tap conductors appropriately, you avoid overloading them, which can cause them to overheat and potentially start a fire.


Ensure proper overcurrent protection

The taps should be sized in consideration of the existing overcurrent protection so that in case of a short circuit or overload the circuit breaker or fuse will trip to protect the circuit.

Maintain voltage

Properly sized conductors help maintain voltage levels and ensure equipment operates efficiently.

Example (Hypothetical)

Let's say you have a power source with an output circuit current of 20 amps that is tapped onto a feeder. The feeder is protected by a 50-amp circuit breaker.1.

Calculate 125% of the power source output

20 amps
1.25 = 25 amps2.

Add the overcurrent device rating

25 amps + 50 amps = 75 ampsTherefore, the tap conductors in this example would need to be rated for at least 75 amps. You would then select a wire size that has an ampacity of 75 amps or greater, considering the conditions of use (temperature, etc.) and the rules of 240.21(B).

Disclaimer:
This is a simplified explanation. Always consult the full, official electrical code for the specific requirements and interpretations applicable to your situation. It is also highly recommended that you seek the advice of a qualified electrical professional. Flag for review