Topic: Bus Drop Wiring

User: Rotato, Location: Indiana

Asked on: Wednesday, October 9, 2024 at 3:30 pm EDT
Answered on: Thursday, March 6, 2025 at 3:41 am EST

Question: Started at a new factory not to long ago. Trying to get educated on Buss Drops. Specifically wiring methods from bus drop through plugs to a machine. Machinery is meant to be semi-permanent (interchangeable eventually). They're using bus drop cable and bus drop clamps at the ceiling. Just not sure about using plugs for feeders to semi-permanent machinery and how your supposed to enter the machinery with bus drop cable. Is a cord grip enough or are there specific cord grips for this type of installation?Last place I worked at used conduit everywhere.Where can I find the relevant codes for these types of installations in the NFPA 70 or NFPA 79.

Okay, let's break down the code requirements and best practices for wiring from bus drops to semi-permanent machinery using plugs, focusing on NFPA 70 (NEC) and NFPA 79 (Electrical Standard for Industrial Machinery).

Key Considerations & Code References1. Flexibility & Disconnect Means

The core of your question revolves around the balance between providing a flexible connection for future interchangeability and ensuring compliance with code requirements for disconnect means and wiring methods.2.

Article 400 (Flexible Cords and Cables)

This article is crucial. It dictates where flexible cords can and can't be used. Flexible cords aren't typically permitted for permanent wiring.

400.8 Uses Not Permitted.
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following: (1) As a substitute for the fixed wiring of a structure. (2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors. (3) Where run through doorways, windows, or similar openings. (4) Where attached to building surfaces. (5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings. (6) Where installed in raceways, except as otherwise permitted in this Code. 400.7 Uses Permitted. Flexible cords and cables shall be used only for the following: (A) Pendants. (B) Wiring of Luminaires. (C) Connection of Portable Equipment. This is key to your situation. If your machinery qualifies as "portable," this is your pathway. However, be very cautious about interpreting "portable." Generally, this means easily movable by one person without tools. Heavy machinery, even on wheels, often doesn't qualify. (D) Connection of Stationary Equipment to Facilitate Their Frequent Inter-change. This is also key and likely the most applicable. "Frequent Interchange" is the loophole that allows this type of connection. You'll need to justify "frequent." (E) Prevention of the Transmission of Noise or Vibration. (F) Appliances Where the Fastening Means and Mechanical Connections Are Specifically Designed to Permit Ready Removal for Maintenance and Repair, and the Appliance Is Intended or Designed for Frequent Inter-change. (G) Data Processing Cables as Permitted by 645.5. (H) Connection of Moving Parts. (I) Where Installed in Accordance with 368.56(B).3. Article 368 (Busways)

This is the core of your installation method.

368.56 Uses Permitted as Flexible Connections.
Suitable cord assemblies shall be permitted as flexible connections to busways for the connection of equipment, provided all the following conditions are met: (1) The length of the cord from the busway plug-in device to the supply terminals of the equipment does not exceed 1.8 m (6 ft). This is a hard limit. (2) The cord is of a type listed for extra-hard usage. Look for cable marked with "SOOW" or similar ratings on the cable jacket. (3) The cord contains an equipment grounding conductor. This is the green (or green/yellow) wire. (4) The cord is terminated with listed fittings. (5) Strain relief is provided at the cord connection to the busway and at the equipment. This is where your cord grips become critical. (6) The busway plug-in device is rated to handle the overload current of the equipment it supplies.4.

Article 430 (Motors, Motor Circuits, and Controllers)

If your machinery is motor-driven (very likely), this article comes into play. You'll need to ensure proper overload protection, disconnect means within sight of the motor (or lockable), etc.5.

Article 440 (Air-Conditioning and Refrigeration Equipment)

Similar to Article 430, if your machines contain AC or refrigeration equipment, you'll need to comply with this article.6.

Article 670 (Industrial Machinery)

This article covers the general electrical requirements for industrial machinery.7.

NFPA 79 (Electrical Standard for Industrial Machinery)

This standard
supplements the NEC (NFPA 70) and provides much more specific guidance for industrial machinery. NFPA 79, Section 5.3.
2.1 - Addresses the use of flexible cords and cables for machine wiring. It echoes the NEC's limitations and emphasizes proper strain relief and protection against physical damage. NFPA 79, Section 5.3.4 - Provides requirements for conductors and cabling used within machines, including types of insulation and routing. NFPA 79, Section 5.2 - Covers disconnect means and control circuit requirements. NFPA 79, Chapter 13 (Supply Circuit Conductors) - provides information on the size of the supply conductors based on the load of the machine. NFPA 79, Chapter 14 (Overcurrent Protection) - provides information on types and sizes of overcurrent protection. NFPA 79, Chapter 15 (Control Circuit Conductors) - provides guidance on sizing control circuit conductors.


Regarding Plugs & Receptacles


General Rule

Plugs and receptacles are permitted for "portable" or "frequently interchanged" equipment, but you MUST use the correct type and rating.

NEMA Configurations

Use the correct NEMA plug/receptacle configuration for the voltage, amperage, and number of poles/wires required. Using the wrong type is a code violation and a safety hazard. Common examples:
L5-30: 30A, 125V Locking Plug L6-30: 30A, 250V Locking Plug L14-30: 30A, 125/250V Locking Plug

Locking vs. Non-Locking

Locking plugs (the "L" in the NEMA designation) are highly recommended in industrial environments to prevent accidental disconnection.


Wet Locations

If the area is damp or wet, use plugs and receptacles rated for wet locations.

Grounding

Ensure the plug and receptacle are properly grounded. This is absolutely critical for safety.

Entering the Machinery


Cord Grips (Strain Relief)

This is the key. You must use proper cord grips wherever the flexible cord enters the machine enclosure.

Purpose

Cord grips provide strain relief to prevent tension on the conductors inside the machine. They also seal the entry point to prevent dust, moisture, and other contaminants from entering.


Types

Choose cord grips specifically rated for the cable you're using (diameter, cable type). Common materials include nylon, metal, and liquid-tight versions.

Liquid-Tight

If the area is wet or oily, use liquid-tight cord grips.


Proper Installation

Install cord grips according to the manufacturer's instructions. Don't overtighten.

Alternatives to Flexible Cord (If You Can't Justify "Frequent Interchange")

Flexible Metal Conduit (FMC) or Liquidtight Flexible Metal Conduit (LFMC)

These are raceways. You run individual THHN/THWN conductors
inside the conduit. This is a more robust and code-compliant solution if you can't justify the use of flexible cord. Use appropriate fittings to connect the conduit to the bus drop tap and to the machine enclosure.

Surface Metal Raceways (Wiremold)

If you have a need to protect the wiring on the wall or the machine's enclosure this may be an option.

Example Installation Scenario1.

Bus Drop

Bus drop cable is suspended from the ceiling using bus drop clamps.2.

Bus Plug

A bus plug is installed on the busway, providing a circuit breaker or fused disconnect. The bus plug should be properly sized for the load of the machine.3.

Flexible Cord

An extra-hard usage flexible cord (e.g., SOOW) of the correct gauge is connected to the bus plug. The length of the cord must be 6 feet or less (1.8m).
4.


Cord Grips

Cord grips are installed at both ends of the flexible cord – at the bus plug and where the cord enters the machine enclosure.5.

Plug and Receptacle

A properly rated and configured plug is attached to the end of the flexible cord, and a matching receptacle is mounted on the machine enclosure (or sometimes on a short "pigtail" of wire extending from the machine). Locking plugs are preferred.6.

Internal Wiring

Inside the machine, the conductors from the receptacle are connected to the machine's electrical components according to NFPA 79 and the machine's design.

Important Considerations

Local AHJ (Authority Having Jurisdiction)

Always consult with your local electrical inspector (AHJ). They have the final say on whether your installation meets code. Show them your plans and be prepared to justify your approach.

Documentation

Keep detailed records of your electrical installations, including wiring diagrams, component specifications, and inspection reports.

Qualified Personnel

Ensure that all electrical work is performed by qualified and licensed electricians.

Steps to Take1.

Review NFPA 70 & NFPA 79

Get your hands on the latest editions and thoroughly review the articles and sections mentioned above.2.

Assess "Frequent Interchange"

Can you
honestly justify that the machinery will be frequently interchanged? If not, consider using FMC/LFMC.3.

Create a Detailed Plan

Design your bus drop-to-machine connections, specifying all components (cable, cord grips, plugs, etc.) and wiring methods.4.

Consult with the AHJ

Present your plan to the electrical inspector and get their feedback.5.

Implement and Document:
* Perform the installation to code, and keep detailed records.By carefully considering the code requirements, using the correct components, and consulting with the AHJ, you can create safe and compliant bus drop connections for your semi-permanent machinery. Good luck! Flag for review

Previous Question Next Question