User: TJNII, Location: Ohio
Asked on: Wednesday, October 9, 2024 at 9:48 pm EDT
Answered on: Thursday, March 6, 2025 at 3:42 am EST
Question: I'm working on a service upgrade where we're upgrading to two 200A services from a single 320A meter. As part of this install we're installing two service entry rated transfer switches between the meter and the panels to provide generator power during outages. The transfer switches are double pole units that break the hots only, the neutral connection is just a bus. Using the service entry rated switches I don't believe it's possible to directly connect both switches to the generator without a code violation on the neutral. I'm working with an electrician, but he doesn't have an answer to how this issue should be resolved. I also called Generac tech support who was also unable to advise. I'd like a verification from the experts here that my understanding is correct before I engage in expensive or unusual solutions.Grounding is left out of scope of this discussion as the neutral alone has code compliance issues, before adding the complexity of bonding.Control wiring is out of scope.Imagine the equipment laid out as so:Code:
You've correctly identified a potential issue with the neutral connection in your scenario. Let's break down why, and then explore potential solutions.
The Problem: Parallel Neutral Paths
The core issue is the parallel neutral paths you create when connecting a single generator to two service-rated transfer switches with a common neutral bus. Here's why this violates the NEC: NEC 310.10(H)(3) Parallel Conductors in Electrical Systems. While this section speaks to sizing requirements of phase conductors and neutrals installed in parallel, it implicitly prohibits creating parallel neutral paths with different impedance. NEC 250.36(A) Grounded Systems. This section requires "A grounded conductor shall be installed with each alternating-current circuit and shall be identified as specified in 200.6." While not as direct, this section states the requirement for a single neutral per circuit.
Why Parallel Neutrals are Problematic
Even though your electrician may not have seen a problem in the past, it doesn't mean that there isn't one. It's very common for even seasoned electricians to overlook this fact. Unequal Current Distribution
The neutral current from the generator will divide between the two neutral paths based on their impedance. Since the length of wire, connection tightness, and other factors will never be perfectly equal, one neutral path will carry more current than the other. This can lead to overloading of one neutral conductor, even if the total generator current is within the combined rating of the neutrals.
Increased Voltage Drop
Unequal current distribution will lead to increased voltage drop.
Harmonic Current Issues
If your load includes non-linear loads (common with modern electronics), the harmonic currents in the neutral conductor can be significantly higher. Unequal sharing of these harmonic currents can exacerbate the overloading issue.
Acceptable Solutions
Here are a few options to address this situation, starting with the best and most compliant:1. Two Generators, One Per Transfer Switch
This is the cleanest and most straightforward solution. Each transfer switch gets its own dedicated generator, eliminating the parallel neutral problem entirely. This is the most costly option, but the most NEC compliant.2.
Ganged Transfer Switch
Replace the two transfer switches with a single, properly sized transfer switch that serves both panels. This eliminates the parallel neutral paths because there is only one switch and one neutral connection to the generator. This is the most common solution.3.
Isolating (4-Pole) Transfer Switches
The best solution would be to use 4 pole transfer switches. This solution keeps your original install design while maintaining compliance. By switching the neutral as well as the hots, you ensure that only one neutral path is active at a time. This completely isolates the neutral of the service coming in from the street from the neutral of the generator, preventing any parallel paths.
Important Considerations Coordination
Ensure the generator you select is appropriately sized for the combined load of both panels.
Local Codes
Always verify your proposed solution with your local electrical inspector before* proceeding. They have the final say on code compliance in your jurisdiction.
Recommendation
I believe that using two 4 pole service entry rated transfer switches will be the best method of resolving the parallel neutral pathing. This install is also the most flexible in terms of future changes. By using two service entry rated transfer switches, the home is not only protected from back feed from the generator, but is also isolated from back feed to the grid, regardless of the position of the utility disconnect.
Disclaimer: This information is for general guidance only. Always consult with a qualified and licensed electrician for any electrical work. Flag for review