Question: You’re supposed to derate romex if you bundle it more than 24”, correct? Does this apply if you’re stapling two romex cables on the flat down to a receptacle box? Isn’t two romex cables carrying 120 volts each actually four current carrying conductors? Or does this not apply to cables stapled down a stud?
You're asking some good questions about Romex (NM-B cable) derating, and it's important to understand the rules to ensure safe wiring. Here's a breakdown
1. The 24" Rule and Bundling:
Yes, the 24" rule is generally correct. The National Electrical Code (NEC) requires you to derate the ampacity (current-carrying capacity) of Romex cables if they are bundled, bundled and insulated, or installed in conduit for more than 24 inches. The NEC is the authority, so refer to your local version (usually based on a recent NEC edition) for the precise language. Why derate? Bundling restricts the ability of the conductors to dissipate heat. More heat means a greater risk of insulation damage and potential fire hazards.2. Romex Stapled to a Stud
Generally, stapling Romex to a stud does help with heat dissipation, but it doesn't automatically eliminate the need to derate. The NEC says you need to derate the cables if they are bundled and insulated, or bundled and in a raceway for more than 24". The key question is if that qualifies as "bundling". Two cables laying flat against a stud are usually considered bundled, but there can be some argument depending on the specific circumstances and how your local inspector interprets the code.3. Two Romex Cables = Four Current-Carrying Conductors? Not always. It depends on the circuit configurations. This is where it gets a little tricky. Let's break it down: Standard 120V Circuit
In a standard 120V circuit, each Romex cable typically has: One hot (black) wire (current-carrying) One neutral (white) wire (current-carrying) One bare or green grounding wire (not current-carrying under normal conditions).
Therefore, two 120V Romex cables would have TWO current-carrying conductors (the black and white wire in each cable) Multiwire Branch Circuit (MWBC)
If you have a multiwire branch circuit, one neutral conductor may be used to power two hot conductors. Two hot conductors on one neutral conductor = two current carrying conductors plus one neutral.
Therefore, if the circuit is a MWBC, then the number of CCC's needs to be calculated Switch Loops (less common these days)
In older wiring, you might find switch loops where a neutral wire is run from the switch to the light. Two hot conductors on one neutral conductor = two current carrying conductors plus one neutral.
Therefore, if the circuit is a switch loop, then the number of CCC's needs to be calculated4. Derating Factors The NEC has tables (typically Table 310.15(C)(1) in the NEC) that specify derating factors based on the number of current-carrying conductors in a raceway, cable, or bundle. Example
Let's say you determine you have four current-carrying conductors. According to the table, you might need to derate the ampacity of the conductors to 80% of their listed value. If you're using 14 AWG Romex (typically rated for 15 amps), you'd have to reduce the allowable ampacity to 15 amps 0.80 = 12 amps. This means you couldn't put it on a 15-amp breaker!
5. Stapling Two Romex Cables on the Flat to a Receptacle Box
This is generally considered bundling, especially in the short run into the box. The inspector could require derating. Best Practice
Keep the length of the bundled portion as short as possible (minimize the distance between the last staple and the box).
Important Considerations and Recommendations
Consult the NEC
The only definitive answer lies in the most recent version of the NEC adopted in your jurisdiction. Get a copy and familiarize yourself with Article 310 (Conductors for General Wiring).
Check with Your Local Inspector
Building inspectors have the final say. It's always wise to discuss your wiring plan with them before you start the work. They can tell you how they interpret the code in your area.
Err on the Side of Caution
If you're unsure, it's always better to over-engineer your wiring and use a larger wire gauge than you think you need. It's safer and can prevent problems down the road.
Avoid Bundling When Possible
The easiest way to avoid derating issues is to separate the cables as much as possible.
In summary: While stapling to a stud helps a little, the fact that you're running two Romex cables together (even if stapled flat) can* create a situation where derating is required, especially within 24" of a box. You need to determine the number of current-carrying conductors, consult the NEC for the correct derating factors, and discuss the situation with your local inspector. Ignoring this can lead to overheating, insulation damage, and potential fire hazards. Flag for review