Question: Can the demand factor shown on table 220.8 be used for Electrical Vehicle Chargers if they are being fed from the dwelling panels?
No, the demand factors in Table 220.8 of the NEC (National Electrical Code) are not applicable to electric vehicle (EV) chargers in dwellings.Here's why: Table 220.8 covers Range, Counter-mounted Cooking Units, Wall-mounted Ovens, and Other Cooking Appliances over 1.75 kW Rating. EV chargers don't fall into any of those categories. The table is specifically designed for cooking appliances. EV Chargers are a Significant Load
EV chargers are typically high-demand, continuous loads. They can draw significant current for extended periods. Applying the demand factors from Table 220.8 would likely underestimate the actual load on the dwelling service and feeder.
Specific EV Charger Load Calculations
The NEC has specific requirements for calculating the load of EV chargers. Article 625 (Electric Vehicle Charging Systems) and Section 220.14(H) provide guidance.
How to Calculate EV Charger Load
The basic rule is to size the circuit and feeder for the
continuous load of the EV charger at 125%. This is often the starting point for load calculations.1. Determine the Charger Output
Find the charger's output in kilowatts (kW) or amperes (A) at the voltage being used (e.g., 240V).2.
Calculate Amperes (if given kW)
If the charger output is given in kW, calculate the amperes using the formula: Amps = (kW 1000) / Voltage3.
Multiply by 125%
Multiply the calculated amperage by 1.25 to account for the continuous load requirement. This gives you the minimum circuit ampacity.
4.
Consider Multiple Chargers
If you have more than one EV charger, the NEC has specific rules in Section 220.87 to determine if demand factors can be applied, and under what conditions. This is crucial to avoid undersizing the service and feeder.
Important Considerations and NEC References
Article 625 (Electric Vehicle Charging Systems)
This article is the authority on EV charger installations.
Section 220.14(H)
This addresses specific load calculation rules for EV chargers.
Section 220.87 Demand Factors for Electric Vehicle Supply Equipment
This section addresses if, and how demand factors may be applied.
Load Management Systems
Consider using load management systems, especially if you have multiple EVs or a limited service capacity. These systems intelligently distribute power to the chargers, preventing overloads.
Local Codes
Always check with your local electrical inspector, as they may have specific requirements or amendments to the NEC.
In summary, Table 220.8 is not applicable to EV chargers. You must follow the specific requirements in Article 625 and Section 220.14(H) and Section 220.87 to calculate the load correctly. Failing to do so can result in an undersized service, overloaded circuits, and potentially dangerous conditions. Consulting with a qualified electrician is highly recommended. Flag for review