Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Voltage Drop

User: Jimmy7, Location: Boston, MA

Asked on: Thursday, October 10, 2024 at 7:43 pm EDT
Answered on: Thursday, March 6, 2025 at 3:45 am EST

Question: Do you determine voltage drop by the actual load? Meaning, if I ran a 120 volt, 20-amp circuit I determine the voltage drop off the actual load, not the 20 amp ocpd correct? If this is the case, for design purposes how long can you run the following1. 20-amp 120 volt circuit for receptacles (When you're not exactly sure what is going to be plugged in)?2. 15-amp 120 volt for receptacles (When you're not exactly sure what is going to be plugged in)?

You are correct. Voltage drop calculations should be based on the expected load, not the overcurrent protection device (OCPD) rating. Using the full OCPD rating would almost always result in an excessively conservative (and possibly impractical) wire size.Here's a breakdown of how to approach this, and then we'll get to the practical lengths for your scenarios

Understanding Voltage Drop and Load Calculation
Voltage Drop

Voltage drop is the reduction in voltage as electricity travels through a wire. Excessive voltage drop can cause appliances to malfunction, motors to overheat, and lights to dim.


Load Calculation

The key is to estimate the continuous load you expect on the circuit. Continuous loads are those expected to operate for 3 hours or more. Non-continuous loads will have less of an impact on voltage drop.

How to Estimate Load When You Don't Know the Exact Appliances


This is a common scenario, especially for general-purpose receptacle circuits. Here's a practical approach:1. Consider the Intended Use

What is the room or area for? This gives you a clue about likely loads.

Living Room/Bedroom

Lamps, TVs, phone chargers, small electronics. Less likely to have heavy, continuous loads.


Kitchen

Small appliances (toaster, blender, coffee maker), potentially a microwave. More likely to have intermittent but larger loads.

Office

Computers, printers, desk lamps. Moderate loads, potentially more continuous.


Workshop

Power tools, lighting. Likely to have heavier, intermittent loads.2.

General-Purpose Receptacle Load (NEC 220.14(I))

The NEC requires you to figure general-purpose receptacle circuits at 180 VA minimum.3.

Diversity/Demand Factors (Advanced)

In large installations, you can sometimes apply demand factors based on the likelihood that not all receptacles will be used at their full capacity simultaneously. This is more common in commercial or multi-family buildings and requires careful consideration. For a single-family home, it's generally safer to be conservative.

Practical Lengths (Estimated)


To calculate the maximum length, we'll make some assumptions and use a voltage drop calculator. I'll use the following parameters: Voltage Drop Limit

3% is a common target for branch circuits.


Wire Type

NM-B Copper (most common in residential)

Voltage

120V


Power Factor

Assumed to be 0.95 (a reasonable value for many appliances)

Calculator

Using an online voltage drop calculator (available from several electrical manufacturers or websites like Southwire)Here's how we'll proceed:1.

Choose an Assumed Load

Since we don't know the actual load, we'll make a reasonable estimate based on the circuit type.2.

Calculate Maximum Length

We'll use the voltage drop calculator to determine the maximum length of the circuit that keeps the voltage drop below 3% for different wire sizes.

Scenario 1: 20-Amp, 120V Receptacle Circuit
Assumed Load

Let's assume a continuous load of 8 amps (960VA) for this circuit. This is a reasonable estimate for a general-purpose circuit that might power a computer, a lamp, and some other small devices. It's also 40% of the breaker rating (8 amps / 20 amps = 40%).

Wire Size

12 AWG is typical for a 20-amp circuit.Using a voltage drop calculator, with an 8-amp load and a 3% voltage drop limit, the maximum length for 12 AWG wire is approximately

70-75 feet
.

Scenario 2: 15-Amp, 120V Receptacle Circuit
Assumed Load

Let's assume a continuous load of 5 amps (600VA) for this circuit. This is reasonable for a bedroom or a similar room with lighter usage. It's also about 33% of the breaker rating (5 amps / 15 amps = 33%).

Wire Size

14 AWG is typical for a 15-amp circuit.Using a voltage drop calculator, with a 5-amp load and a 3% voltage drop limit, the maximum length for 14 AWG wire is approximately

50-55 feet
.

Important Considerations



Heavier Loads Reduce Length

If you anticipate heavier loads, you must reduce the maximum circuit length or increase the wire size. For example, if you expect a continuous load of 10 amps on the 15-amp circuit, the maximum length will be significantly shorter.

Future Expansion

Consider future needs. If you think the load might increase later, it's wise to run a larger wire gauge now to avoid problems later.


Local Codes

Always follow local electrical codes and regulations.

Dedicated Circuits

For appliances with high power requirements (microwaves, window AC units, etc.), use dedicated circuits. This will eliminate the guesswork involved in estimating general-purpose receptacle loads.


Voltage Drop Calculators

Use a reliable voltage drop calculator and input accurate information. Online calculators are readily available.

Conduit

If the conductors are run in conduit, the values will change

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. Consult with a qualified electrician for your specific project to ensure safety and compliance with all applicable codes.* Flag for review

Previous Question Next Question