Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding Neutral and Grounds

User: ddaut, Location: Louisiana

Asked on: Thursday, October 10, 2024 at 9:26 pm EDT
Answered on: Thursday, March 6, 2025 at 3:45 am EST

Question: I see many times where there is a meter and disconnect on the outside of a home. Immediately adjacent on the inside of the home there is an indoor panel with a main disconnect and all the circuit breakers. Most of the time grounds and neutrals are not separated in the inside panel. So they are bonded outside in the disconnect and also bonded inside at the main panel; usually less than 6 feet apart. It’s my understanding that neutrals and grounds should be separated at the first disconnect and stay separated after that. How bad is this and is there an exception to make this code compliant?

You've described a common situation and highlighted a key point of confusion. Here's a breakdown of why it happens, how bad it is, and potential (but limited) solutions

The Situation:
Outside Meter/Disconnect

This is often the service disconnect, meaning it's the point where power enters the building from the utility. At this point, the neutral
is bonded to ground (typically via a grounding electrode conductor to a ground rod, water pipe, or concrete-encased electrode).

Inside Panel (Subpanel)

This panel should be a subpanel if the outside disconnect is indeed the service disconnect. Therefore, grounds and neutrals should be separated. However, you often find them bonded.

Why This is Incorrect (And Why It's Done Anyway)



Code Requirement

NEC (National Electrical Code) requires that the neutral and ground be bonded

only at the service disconnect
. Downstream of the service disconnect (in subpanels), they must be kept separate. Why It's Done (Wrongly)



Ignorance/Mistake

Many people (even some electricians) simply don't understand this crucial rule. They may wire an interior panel as if it
were the service panel, bonding neutral and ground.

"That's How It's Always Been Done"

Sadly, this is a common reason. Older installations may have been done incorrectly, and people perpetuate the error.

Perceived Safety (False Sense)

Some believe that bonding neutral and ground everywhere provides "extra safety." However, it creates dangerous conditions.

Why is it Bad?
Neutral Current on Grounding Conductors

When the neutral and ground are bonded in a subpanel, the neutral current (the current returning from loads) can flow on the grounding conductors (the metal boxes, conduit, equipment grounding conductors, etc.).

Electric Shock Hazard

Any fault in the neutral conductor can electrify grounded metal parts. If you touch a "grounded" appliance and the fault occurs between the main panel and your location you can get shocked.


Electromagnetic Interference (EMI)

Stray neutral current on grounding conductors can create EMI, which can interfere with sensitive electronic equipment.

Nuisance Tripping

Under certain circumstances, it can cause GFCI breakers to trip unnecessarily.


Fire Hazard

In extreme cases, if the neutral connection becomes very poor, a significant amount of current could flow on the grounding conductors, potentially leading to overheating and a fire.

Is There an Exception? (Very Limited)


There's a very limited exception in the NEC (250.32(B) Exception) for existing buildings only where there are no metallic paths between the buildings. This exception essentially allows bonding in a detached building or structure if specific conditions are met (e.g., only one circuit serves the structure, no metallic water piping or gas piping between buildings, etc.). This is a very specific exception and rarely applies to the scenario you described (a panel inside the same building as the service disconnect).How Bad is It?

It's a serious safety issue. It's a code violation and creates a potential shock and fire hazard. It should be corrected.Correction Steps


Identify the Service Disconnect

Confirm that the outside meter/disconnect is indeed the service disconnect.2.

Isolate Neutrals and Grounds in the Subpanel

Remove the bonding jumper (usually a green screw or strap) that connects the neutral bar to the panel enclosure. Ensure that all ground wires are connected to the ground bar, which is bonded to the panel enclosure. Ensure that all neutral wires are connected to the neutral bar, which is now isolated from the panel enclosure.3.

Verify Grounding Electrode System

Ensure that the service disconnect has a proper grounding electrode system (ground rod, water pipe connection, concrete-encased electrode, etc.) connected to the neutral bus.

Important Considerations



Qualified Electrician

This work should be performed by a qualified and licensed electrician. Working with electrical panels can be dangerous, and improper wiring can have severe consequences.

Permitting

Check with your local jurisdiction about permitting requirements for electrical work.


Inspection

After the correction, have the work inspected by a qualified electrical inspector to ensure it complies with the NEC and local codes.

In Summary:


Bonding neutral and ground in a subpanel is generally wrong and dangerous. It violates the NEC and creates a potential shock and fire hazard. Correcting this issue is essential for electrical safety. Flag for review

Previous Question Next Question