User: Mdsparky, Location: massachusetts
Asked on: Friday, October 11, 2024 at 6:50 am EDT
Answered on: Thursday, March 6, 2025 at 3:46 am EST
Question: I believe New Hampshire is currently enforcing the amended 2020 NEC and that they have amended 210.8(B) to remove the protection 250 volt receptacles . which means a receptacle for range in a kitchen does not require GFCI protection in New Hampshire. Is this correct?
You are correct. New Hampshire is enforcing the 2020 NEC with amendments, and you are also correct about their specific amendment to 210.8(B).Here's a breakdown: 2020 NEC
The 2020 National Electrical Code, as written, generally requires GFCI protection for 250-volt receptacles in specific locations, including kitchens.
New Hampshire Amendment to 210.8(B)
New Hampshire has amended Section 210.8(B) of the 2020 NEC. This amendment removes the GFCI protection requirement for 250-volt receptacles in dwelling unit kitchens that supply ranges, ovens, and cooktops.
Effect of the Amendment
Because of this amendment, a standard 250-volt receptacle serving an electric range in a residential kitchen in New Hampshire does not currently require GFCI protection.
Important Considerations
Always Verify
While I am confident in this information based on my knowledge of the NEC and New Hampshire's amendments, double-check with the New Hampshire State Electrical Board or your local electrical inspector to ensure this is the current interpretation and enforcement policy. Regulations can change.
Manufacturer's Instructions
If the range or cooktop manufacturer requires GFCI protection, that requirement supersedes the relaxed code requirement in New Hampshire.
Best Practice: Even if not required by code, installing a GFCI receptacle could still be considered a best practice for enhanced safety, but it is not mandatory due to the New Hampshire amendment. Flag for review