Topic: TC-ER

User: jes25, Location: Midwest

Asked on: Friday, October 11, 2024 at 6:54 pm EDT
Answered on: Thursday, March 6, 2025 at 3:48 am EST

Question: This picture has a run of TC ER ran from the cable tray to the devices. In between the device and tray there is a section raceway you can see for support of the cable. Do you think this is acceptable per the NEC? Please provide reference.

Okay, let's analyze this situation based on the NEC, assuming you're describing a typical scenario of TC-ER cable running from a cable tray, transitioning through a raceway section for support, and then connecting to devices.

My Assessment

Based on common interpretations and application of the NEC,

this is generally considered acceptable IF done correctly and meets all applicable code requirements.
The key aspects are ensuring proper support, protection, and compliance with the cable's listing.

NEC References and Reasoning

Here's a breakdown of the relevant NEC sections and why this can be permissible:1.

NEC 336.10 Uses Permitted

This section outlines where TC-ER cable is allowed. In general, TC-ER cable is permitted for: (1) For exposed or concealed work, in dry or wet locations. (2) In cable trays. (3) In raceways. (4) Direct buried where identified for the use. (5) As aerial cable on a messenger.2.

NEC 336.12 Uses Not Permitted

This section outlines restrictions, which are generally related to physical damage concerns.3.

NEC 392 Cable Trays

TC-ER is listed for use in cable trays.4.

NEC 392.8(E) Single Conductors and Cable Support

This section is really the key. It states:
"Single-conductor cables and multiconductor cables shall be supported and secured to the cable tray in accordance with 392.30(B)." "Multiconductor cables rated 600 volts or less shall be permitted to be installed without being secured to the cable tray where the cables are installed in accordance with 392.8(E)(1) through (E)(3)." The cable is continuously accessible for its entire length without removing or disturbing any permanent parts of the building structure. The cable is installed in a single layer. The cable is secured at intervals not exceeding 6 feet.5.

NEC 392.30(B) Securing and Supporting

This section further details how cables need to be secured and supported
within the cable tray.

Why the Raceway Can Be Helpful (and Usually Necessary)



Physical Protection

TC-ER cable, while robust, can be vulnerable to physical damage near connection points. A short section of raceway (e.g., EMT, rigid conduit, etc.) provides added protection against impacts and abrasion.

Strain Relief

The raceway, when properly installed and the cable is properly secured within it, can provide strain relief for the conductors at the device terminals. This is
critical. Without strain relief, the connections at the device can loosen over time, leading to failures.

Support

The raceway can serve as a physical support for the cable, especially if the cable run is long or subject to movement. This is essential between the tray and the point where the cable terminates at the device.

Critical Considerations & How to Make it Code-Compliant


Listing and Labeling

The TC-ER cable MUST be clearly marked as TC-ER (Tray Cable - Exposed Run). This is your first check.2.

Proper Raceway Selection

Choose a raceway type appropriate for the environment (e.g., EMT for dry indoor locations, rigid metal conduit for corrosive environments).3.

Securement Within the Raceway

The cable MUST be properly secured within the raceway, especially at the point where it exits the raceway and enters the device enclosure. Use appropriate cable connectors (e.g., strain relief connectors, cord grips) that are listed for use with TC-ER cable. This is often overlooked, but it is very important to minimize stress on the conductors at the termination.4.

Raceway Support

The raceway itself must be properly supported according to NEC Article 344, 352, or whichever article covers the specific raceway type being used.5.

Bending Radius

Adhere to the cable manufacturer's bending radius requirements to avoid damaging the cable.6.

Fill

Ensure the raceway fill does not exceed the limits specified in the NEC.7.

Grounding

Properly ground the metal raceway (if metal) according to NEC Article 250.8.

Exposed Run Requirements

Ensure the "exposed run" portion of the TC-ER cable run meets all the requirements of 336.10.
9.


Support Intervals Outside Raceway

Pay close attention to NEC 336.30 for support requirements for the TC-ER cable after it leaves the raceway and approaches the device.

In summary:
Running TC-ER cable from a cable tray, through a short section of raceway, to a device is often permissible under the NEC, BUT it requires careful attention to proper support, securement, protection, and grounding. The raceway is frequently used for strain relief and physical protection as it enters the device. Make sure all components are properly listed and installed according to the NEC. Always consult with your local electrical inspector for specific interpretations in your jurisdiction.Without seeing the picture, I can only provide general guidance. If you provide the picture, I can give you a more specific assessment of the installation. Flag for review