Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: EMT

User: HarveyDC, Location: Valdosta, Ga

Asked on: Saturday, October 12, 2024 at 4:19 pm EDT
Answered on: Thursday, March 6, 2025 at 3:50 am EST

Question: I'm learning about this trade. I have seen a EMT pipe running down vertically and supported to the frame of a stationary window (a big glass panel in restaurant) so does that violates any NEC code?

Yes, supporting EMT (Electrical Metallic Tubing) conduit from a window frame, especially a stationary glass window in a commercial setting like a restaurant, is likely a violation of the National Electrical Code (NEC) for several reasons: 1. Mechanical Strength and Support (NEC 314.17(C))

The NEC requires that conduit and its associated equipment (boxes, fittings, etc.) be securely fastened and supported. A window frame, particularly a large glass panel, is generally

not designed or intended to provide the necessary structural support
for electrical conduit. The vibrations, stress, and weight of the conduit, especially if it contains multiple conductors, could compromise the integrity of the window frame or the glass itself. 2. Non-Electrical Equipment (NEC 110.3(B) and 300.11(A))

NEC 110.3(B) mandates that electrical equipment be installed and used according to its listing and labeling. Window frames are obviously not listed or labeled as supports for electrical conduit. NEC 300.11(A) generally prohibits using raceways, cables, or equipment supports as a means of supporting other nonelectrical systems. While the rule is about electrical supporting non-electrical, the principle is that electrical systems should have dedicated, appropriate support.

3. Potential for Damage (NEC 300.4)

Fastening conduit to a window frame, especially using methods like drilling, screwing, or clamping, could damage the window frame, weather seals, or the glass itself. This creates a potential safety hazard and violates the NEC's requirement to protect conductors and equipment from physical damage.

4. Improper Workmanship and Aesthetics

Attaching conduit to a window frame is generally considered unprofessional and aesthetically unpleasing. Electrical installations should be neat, workmanlike, and follow industry best practices.

Acceptable Methods of Support

The NEC provides a variety of acceptable methods for supporting EMT conduit, including:

Conduit Straps and Clamps

Using listed conduit straps and clamps specifically designed for EMT.


Stand-off Supports

Mounting conduit to walls or ceilings using stand-off supports.*

Independent Supports

Providing dedicated supports, such as Unistrut channels or threaded rods, anchored to the building structure.

In summary,
supporting EMT conduit from a window frame is a poor practice that violates the NEC due to inadequate mechanical support, potential damage, and general disregard for proper installation methods. A qualified electrician should be consulted to provide a safe and compliant alternative support system.Always check your local codes as they can be more stringent than the NEC. Flag for review

Previous Question Next Question