Topic: Bizarre ACH550 VFD Control Situation.

User: TwoBlocked, Location: Bradford County, PA

Asked on: Sunday, October 13, 2024 at 8:04 am EDT
Answered on: Thursday, March 6, 2025 at 3:50 am EST

Question: We will have another go at this Monday, but thought you fine folks would be interested. Got an ABB ACH550 that is being switched from hard wire to RS-485/Modbus control as part of a PLC upgrade. I've been doing the wiring while a gal is doing the programming, but we help each other out.Soooo, comes commissioning time and we are trying to get the VFD to run with the help of tech support (This parameter, that parameter, the other parameter, nothing works, thanks for your help, good-bye...) RS-485 is working fine. The speed command on the keypad is changeable from the PLC when in "AUTO" on the keypad (while not changeable from the keypad) but won't start. However, when in "OFF" on the keypad, the PLC cannot change the speed command (while the keypad can), but can start the VFD!In other words, when the PLC can change the speed command (in AUTO) it cannot start the VFD, and the keypad cannot start the VFD nor change the speed command. But when the PLC can start the VFD (in OFF) it cannot change the speed command, but the keypad can change the speed command (but not start the VFD.)Not asking for advice at this point, just sharing a bizarre situation. I'm working on a spreadsheet app where I can enter the hexadecimal values of the Command Words and Status Words from the RS-485/Modbus comms as displayed on the keypad and see which bits are ON or OFF and what they control or indicate.

This is a bizarre situation! It sounds like you're caught in a weird conflict of control authority depending on the keypad position. It's definitely valuable to document and analyze the behavior like you are.Here are some thoughts on why this might be happening and what to look for in your parameter review, even though you're not asking for advice: Control Location Parameters

The ACH550 has multiple parameters that define where the drive gets its start/stop command and its speed reference. You need to make absolutely sure these are all set to RS-485 when you want the PLC to control everything. Some key parameters to double-check (these numbers might vary slightly depending on your specific firmware version, but the concepts are the same):
`10.01 Ext1 Command Source`: This controls the source of the Start/Stop/Direction commands. This

must
be set to `Fieldbus`. `11.03 Reference Select`: This parameter dictates where the drive is getting its speed reference. It should be set to `Reference 1` for Modbus control. `11.04 Reference 1 Selection`: This parameter dictates what is feeding Reference 1, this should be set to `Fieldbus Ref 1`. Fieldbus Addressing and Communication

The fact that you can change the speed setpoint
sometimes and start the drive sometimes suggests your Modbus communication is generally functional, but there's likely a misunderstanding in how you are controlling the start/stop command.

Command Word Interpretation

The ACH550 Command Word is key here. Ensure the PLC is sending the correct bits to start/stop, reset faults, etc. This is where your spreadsheet analysis will be crucial. Pay particular attention to the "Control Word" and "Reference Value" registers. Also, check if there is a "Process Data Register" or similar where additional commands can be sent. Start/Stop Bit(s): Make sure these bits are being toggled correctly by the PLC.

Keypad Priority

The fact that the keypad has some control depending on its position suggests there might be a parameter that gives the keypad priority under certain conditions. Look for anything related to "Keypad Control" or "Local/Remote Select" and its interaction with the fieldbus settings.

Parameter Groups

Some ABB drives have parameter groups (like "Standard Macro" or "User Macro"). These pre-configured groups can sometimes override individual parameter settings. If one of these is active, it might be interfering with your desired RS-485 control.


Faults and Interlocks

Check for any fault codes or interlock conditions that might be preventing the drive from starting in AUTO mode. Even if there are no visible faults, there might be internal flags set that are preventing operation.*

Firmware Version:
Very occasionally, firmware bugs can cause strange behavior. If all else fails, check the firmware version and see if there are any known issues related to RS-485 control.Keep us updated on what you find on Monday! Flag for review