Topic: Cummins ATS

User: Electromatic, Location: Virginia

Asked on: Monday, October 14, 2024 at 9:19 am EDT
Answered on: Thursday, March 6, 2025 at 3:52 am EST

Question: While waiting for a replacement permanent backup generator, I've been asked to wire a Cummins trailer-mount generator to an existing Cummins ATS. The genset terminal block (pictured) seemed simple enough--"Apply Ground to Activate", TB1-1 Remote Start. I tried jumping 20-22 to 1 but got nothing. I contacted Cummins and got a rather strange response to wire the ATS terminals directly to the genset starter (pictured response).

Okay, this is a common, but sometimes confusing situation. Let's break down what's likely happening and what you need to do.

Understanding the Problem Cummins ATS and Remote Start

Cummins ATS (Automatic Transfer Switches) are designed to automatically switch between utility power and generator power when a power outage occurs. A key part of this is the "remote start" feature, which
tells the generator to start. They often use a

momentary, low-current signal
to activate the generator's internal starting sequence. "Apply Ground to Activate" - The Misconception

While "Apply Ground to Activate" sounds simple, it can be misinterpreted. It usually means the generator control system expects a momentary grounding of that terminal to initiate the start cycle. Holding the ground continuously might prevent the generator from actually starting.

Cummins response

Cummins' response to wire the ATS terminals directly to the genset starter is indeed strange and potentially dangerous. It is likely an oversimplification or misunderstanding of your setup. Direct wiring to the starter bypasses all the safety and control features of the generator and ATS and can lead to significant issues.

Why Your Initial Attempt Failed (Likely)


You attempted to jump TB1-20 or TB1-22 to TB1-1 and got nothing. This likely happened for these reasons:1. Continuous Ground

As mentioned above, continually grounding TB1-1 might not work. The generator control system is probably looking for a
momentary ground pulse.2.

Voltage Mismatch

Even with grounding, there could be a voltage difference (e.g., ATS using 12V signal, generator expecting something different).

The Correct Approach: Momentary Ground Signal


Here's the likely (and safer) solution to the problem:1. Identify the ATS Remote Start Contacts

Locate the remote start contacts on your Cummins ATS. These are usually labeled "Remote Start," "Generator Start," or something similar. Your ATS manual should have a wiring diagram that clearly shows these contacts. These are typically

dry contacts
.2. Simulate a Momentary Ground

You need to simulate the ATS giving a momentary ground. This might be accomplished by a few methods:


Using a Jumper Wire (Very Carefully)

Connect one end of a jumper wire to a reliable ground on the generator (e.g., the generator frame, a ground terminal). Briefly touch the other end of the jumper wire to TB1-1 (the "Remote Start" terminal) and immediately remove it. Do this for just a split second. If your generator is working properly, it should start its starting sequence. If it doesn't, stop and check the next steps.

Using a Pushbutton Switch

Connect a pushbutton switch between a reliable ground on the generator and TB1-1. Press and release the button quickly to simulate a momentary ground.


Multimeter

Use a multimeter and connect it to TB1-1 and ground. With it set to Ohms, you should see a 0 ohm value when grounding.3.

Wire the ATS Remote Start Contacts to the Generator

Here's the key step. The dry contacts on the ATS simply need to "close" the circuit to simulate that momentary ground. Connect one wire from the ATS remote start contacts to TB1-1. Connect the other wire from the ATS remote start contacts to a ground on the generator.
4.


Test the Connection

With the connections made, test the system to make sure everything is working properly.

Important Safety Considerations
Read the Manuals

Thoroughly read both the ATS and the generator manuals before doing anything. Understand the wiring diagrams and terminal designations.

Voltage and Current

Be extremely careful when working with electrical systems. Make sure you know the voltage and current levels involved. If unsure, consult with a qualified electrician.

Safety First

Never work on electrical equipment while it's energized. Disconnect the utility power and any other power sources before making connections.


Overcurrent Protection

Make sure the wiring you use is properly sized for the application and that appropriate overcurrent protection (fuses or circuit breakers) is in place.

Qualified Electrician

If you're not comfortable working with electrical systems,
hire a qualified electrician. It's better to be safe than sorry.

Inspect the generator
Verify that the genset fuel lines are securely connected and free from any leaks. Grounded generator Verify that the generator is properly grounded to an earth grounding rod.

Alternative Connection Methods

Some ATS units may communicate with the generator via digital communication protocols such as Modbus. Consult both the ATS and generator manuals to determine if the protocol is supported. Connecting via digital communication may be a preferred solution as it allows for the transfer of a greater amount of data between the ATS and the generator.

Troubleshooting Steps
Check Generator Battery

Make sure the generator's starting battery is fully charged and in good condition.

Generator Fuel

Make sure the generator has sufficient fuel.


Generator Breakers

Check all the circuit breakers on the generator to ensure they are in the "on" position.

ATS Settings

Review the settings on the ATS to ensure they are properly configured for generator operation.


Wiring Errors

Double-check all your wiring connections to make sure they are correct.

In summary, connecting the ATS remote start terminals to the generator's starter is not safe or the correct way to connect a generator to an ATS. You need to simulate a momentary grounding of the generator's remote start terminal (TB1-1) using the ATS's remote start contacts.