Question: Hello,I am new to this forum, so please don't beat me up too much for asking silly questions.Ok, we have a client that is installing flexible cables (SOOW #12 AWG) in a hazardous location (Class1/Division1) with Hawke 753 cable glands at either end of the cable. They chose to use this type of cable instead of metallic conduit with seals, because they are worried about water ingress in hard conduit, as this area is prone to flooding.link for wire - https://www.prioritywire.com/pages/copper_portable_soow12.phplink for gland - https://hubbellcdn.com/specsheet/HHI-HKE-Mult-753-NEC-COMPLIANT-GLAND-SPEC-UK-2023 V13.pdfThe problem that we seem to be having is that one of the cables for this application needs to be designed for CANbus communication, and I cannot seem to find any Cl1/Div1 CANbus cables.I found what appears to be Ethernet cables for Cl1/Div1, but the impedance is not the same for these Ethernet conductors when compared to the 120 Ohm CANbus requirement, so I think that I will have to keep looking.
Welcome to the forum! Don't worry about asking questions, that's what we're here for. Hazardous locations can be tricky.Let's break down the problem and explore some potential solutions. Your concerns are valid, especially regarding the impedance mismatch between Ethernet cables and CANbus requirements. Just throwing an Ethernet cable in there won't work.Here's a structured approach
Understanding the Problem:
Hazardous Location
Class 1, Division 1 is a very stringent environment. Any equipment installed must be certified and intrinsically safe or explosion-proof.
SOOW Cable
While suitable for flexible connections, SOOW cable itself is not intrinsically safe or explosion-proof. The Hawke glands are designed to maintain the explosion-proof integrity of the enclosure, provided the cable is suitable for the application.
CANbus
CANbus requires specific impedance (typically 120 ohms) and often twisted-pair construction for noise immunity.
Water Ingress Concerns
This is a valid concern, but it should be addressed in the selection of suitable sealing methods, rather than abandoning intrinsically safe design.
Key Issues & Solutions
SOOW Cable Suitability
This is the biggest question mark. While the Hawke 753 glands are explosion-proof cable glands, the SOOW cable itself needs to be assessed and approved for use in a Class 1, Division 1 environment when used with those glands. It is extremely unlikely that an SOOW cable is suitable for Class 1, Division 1, even with the Hawke glands.
Confirm the cable's suitability with the Hawke gland manufacturer and/or a qualified third-party certification agency. They would need to verify that the gland, when used with the specified SOOW cable, maintains the explosion-proof integrity of the enclosure. Without this, you have a fundamental violation of hazardous location standards.2. Finding a CANbus Solution
Here are a few strategies:
Intrinsically Safe CANbus Cables
This is the ideal solution. While hard to find pre-made, look for manufacturers that specialize in intrinsically safe (IS) instrumentation cables. Search terms like "intrinsically safe instrumentation cable," "hazardous location CANbus cable," or "Class 1 Division 1 instrumentation cable." You might need to work with a supplier to create a custom cable. Look for cables that are specifically certified for intrinsically safe applications. The cable must be certified for use in the specific hazardous area classification.
Intrinsic Safety Barriers
This is a common approach. Instead of trying to run hazardous-area-rated CANbus cable all the way, run standard CANbus cable to a suitable point outside the hazardous area, then use intrinsically safe barriers to isolate the hazardous area CANbus segment. Here's how it works: Install an intrinsically safe barrier (e.g., from Pepperl+Fuchs, MTL, or R. Stahl) at the boundary of the hazardous area. This barrier limits the voltage and current that can enter the hazardous area, preventing ignition. Run standard CANbus cable (with the correct impedance) up to the safe side of the barrier. Run intrinsically safe-approved CANbus cable (short run) from the barrier to your CANbus devices within the hazardous area. Again, this cable needs to be specifically certified for IS applications. You may need to specify the cable to be used with the IS barrier manufacturer to ensure compatibility. This isolates the hazardous area electrically, allowing the use of standard CANbus technology in the safe area.
Explosion-Proof Enclosures with Standard CANbus Cable
If you can mount an explosion-proof enclosure close enough to your CANbus devices, you can run standard CANbus cable within the enclosure. The enclosure needs to be properly sealed with explosion-proof fittings. This is often less desirable due to space constraints and installation complexity.
Fiber Optic CANbus
Consider converting the CANbus signal to fiber optic outside the hazardous area. Fiber is intrinsically safe (since it doesn't carry electrical current), and then you convert the signal back to CANbus on the other side. This requires more complex electronics.3.
Addressing Water Ingress
The concern about water ingress is valid, but you need to solve it within the confines of the hazardous location requirements.
Proper Conduit Seals
Use properly installed and maintained conduit seals. These are designed to prevent the passage of gases, vapors, and flames through the conduit system. If installed correctly, they also prevent water ingress. Consider using sealing compounds specifically designed for wet environments.
Cable Gland Selection and Installation
Choose cable glands specifically rated for environmental protection (e.g., IP68). Ensure they are properly installed according to the manufacturer's instructions. This is critical for preventing water ingress.
Drainage
Provide adequate drainage for the conduit system. This can be done through drain seals or strategically placed drain holes (check code requirements).
Consider Pre-Wired Solutions
Explore vendors offering pre-wired junction boxes and enclosures rated for hazardous locations and environmental protection. These can save time and ensure proper installation.
Recommendations
Consult with a Hazardous Location Expert
This is crucial. Engage a qualified electrical engineer or consultant experienced in hazardous location design and installation. They can help you select the right equipment and ensure compliance with all applicable codes and standards (NEC 500-505).2.
Contact Cable and Gland Manufacturers
Talk to the technical support teams at Hawke and the CANbus cable manufacturers you're considering. They can provide guidance on cable selection, gland compatibility, and installation procedures.3.
Document Everything
Maintain detailed records of all equipment selected, installation procedures, and certifications. This is essential for safety and future maintenance.4.
Avoid SOOW for Class 1 Div 1 if possible: SOOW cord isn't typically considered suitable for use in Class 1 Div 1 without additional measures or certifications. It is likely that the SOOW cable violates basic code.
In summary: The SOOW cable used in the environment is of great concern. While the Hawke 753 cable glands are explosion-proof, the SOOW cable itself is not. Ensure that all installed products have the required hazardous location ratings. Given the Class 1, Division 1 environment and the CANbus requirements, you should consult a qualified expert to review the installation, and select the right hazardous-location-approved components. You'll likely need intrinsically safe barriers or specialized hazardous-location-rated CANbus cable. Flag for review