Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Lights

User: hhsting, Location: Glen bunie, md, us

Asked on: Monday, October 14, 2024 at 1:51 pm EDT
Answered on: Thursday, March 6, 2025 at 3:53 am EST

Question: I have 60A breaker in Emergency Panelboard that feeds fire alarm, corridor light and jts fused disconnect. It is very old building.The feeder cable size is 4#4 + 10 awg ground.My concern is what is the maximum size breaker can the light circuit be fed from? I don't see it in NEC 2017

Okay, let's break down this scenario and discuss the implications of tapping off your emergency panel's 60A breaker for a lighting circuit in an old building.

Understanding the Situation Emergency Panelboard

This is a critical panel supplying essential loads during a power outage.


60A Breaker

This is the overcurrent protection for the entire feeder circuit from the panel.

Feeder

4 #4 AWG conductors + #10 AWG ground. Copper conductors unless otherwise noted.


Loads



Fire Alarm

A life safety system - Very important.


Corridor Lights

Emergency lighting - Essential for egress.

JTS Fused Disconnect

This likely feeds some other critical load, but without knowing what it is, it's hard to be specific.


Old Building

This introduces potential issues like outdated wiring methods, possible deterioration, and limited documentation.

Question

You want to know the
maximum breaker size you can use to feed the corridor lighting portion of this existing circuit.

Key Considerations and NEC Implications (NEC 2017)
1. Feeder Capacity

#4 AWG Copper conductors (assuming THHN/THWN insulation, most common) are typically rated for 70 Amps at 75°C as per NEC Table 310.15(B)(16) (formerly Table 310.16). However, the 60A breaker is the limiting factor for the entire feeder. You cannot exceed 60A total for all loads fed by this circuit. The #10 AWG ground is adequate for a 60A circuit (NEC Table 250.122).
2.


Overcurrent Protection and Tap Rules (NEC 240.21)

This is the key area of concern. You're essentially creating a "tap" from the 60A feeder to supply the lighting circuit. NEC Article 240.21 covers tap conductor rules.

Without much more information, it is difficult to determine if a "tap rule" exists for your installation
3. Load Calculations (NEC Article 220)



Critical

You must perform a load calculation to determine the actual ampacity required for the fire alarm system, the existing JTS fused disconnect load, and the corridor lights. This calculation will determine how much "spare" capacity is on the 60A circuit. You'll need to know the VA (Volt-Amps) or wattage of each load. Emergency lighting loads are typically calculated at 125% of their continuous load (NEC 220.18).
4.


Voltage Drop (Informative Annex C)

In long runs, voltage drop can be a problem. You want to minimize voltage drop to ensure proper operation of the lights.5.

Dedicated Circuits and Fire Alarm Systems (NEC 760)

Fire alarm circuits ideally should be on dedicated circuits. It is best practice not to share a circuit with lighting.

Sharing a circuit can compromise the reliability of the fire alarm system.
NEC 760.41 and similar sections require careful attention to power source requirements for fire alarm systems.
6. Emergency Lighting Requirements (NEC 700)

NEC Article 700 outlines requirements for emergency systems, including lighting. Make sure the lighting circuit meets these requirements (e.g., illumination levels, transfer switches, etc.).7.

Existing Conditions and Code Compliance

Being an "old building" does not automatically exempt you from code compliance. Any modifications or additions must comply with the current adopted code or at least be brought up to a level of safety that is acceptable to the Authority Having Jurisdiction (AHJ). If the existing installation was originally code-compliant, you might be able to grandfather certain aspects, but any modification triggers the need to evaluate the entire system.

Steps to Determine the Maximum Breaker Size for the Lighting Circuit
1. Load Calculation

Perform a detailed load calculation for
all loads on the 60A circuit. Get the nameplate data (voltage, current, VA, watts) for the fire alarm system, the JTS load, and the corridor lights. Use NEC Article 220 methods.2.

Available Capacity

Subtract the total calculated load from the 60A breaker rating. This is your
available capacity for the lighting circuit.3.

Tap Rules

Evaluate if the length and location of the conductors meet requirements for any of the tap rules in NEC 240.21.
4.


Overcurrent Protection

The breaker protecting the lighting circuit
must be sized to protect the lighting circuit conductors (typically #12 or #14 AWG for lighting). Use Table 310.15(B)(16) to determine the ampacity of the lighting circuit conductors.

The breaker cannot exceed the conductor ampacity.
5. Dedicated Circuit (Best Practice)

If at all possible, install a
separate circuit for the corridor lights from the emergency panel. This provides the best reliability and isolation.

Example Scenario (Hypothetical)
60A Breaker Fire Alarm Load: 10A Continuous JTS Load: 20A Continuous Available Capacity: 60A - 10A - 20A = 30AIf you were using #12 AWG conductors for the lighting circuit (rated for 20A at 75°C), the maximum breaker size you could use would be 20A, assuming the tap rules are met and the load calculation for the lights doesn't exceed 20A. However, if the tap rules cannot be met, you can not tap the circuit at all.

Important Considerations and Warnings
Fire Alarm System

Do not compromise the fire alarm system! Consult with a fire alarm technician before making any changes.

AHJ

Always consult with your local Authority Having Jurisdiction (AHJ) before making any modifications to an emergency system, especially in an old building. They may have specific requirements or interpretations.

Qualified Electrician

This work must be performed by a qualified and licensed electrician. Electrical work can be dangerous, and improper modifications can create safety hazards.*

Documentation

Document all changes and provide updated electrical drawings.

In summary, you must perform a load calculation, determine if the tap rules can be met, and select a breaker size that protects the lighting circuit conductors and doesn't exceed the available capacity on the 60A feeder. Consider a dedicated circuit for the lights to improve reliability, and always consult with the AHJ.
Flag for review

Previous Question Next Question