Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Disconnect from 200amp transfer switch

User: Lifetime44, Location: Palm Coast

Asked on: Monday, October 14, 2024 at 5:28 pm EDT
Answered on: Thursday, March 6, 2025 at 3:54 am EST

Question: So I have two parallel 200 amp main Breakers off of a meter/main. I am installing those on two 200 amp transfer switches to feed the main panels but there are four Breakers in the meter main that are not protected by the 200 amp main Breakers on the load side of the bus bar. One of the breakers happens to be a 90 amp two pole breaker that feeds a sub panel in the house that will need to be on generator power. But since it's not protected by the 200 amp Breakers, that will be the load of the transfer switch. It will not have power when generator is running... Would I be able to tap off of the 200 amp load of the transfer switch and install the #2 Thhn on the load side of 100 amp disconnect next to the transfer switch? Any ideas would help. Thank you

Okay, let's break this down to ensure a safe and code-compliant solution. What you're describing is a situation where you want to ensure a specific subpanel, currently fed from an unprotected breaker in your meter/main, receives generator power when your transfer switch is active.

Here's the core issue

The 90A breaker feeding the subpanel is not downstream of the 200A main breaker that your transfer switch controls. This means when the generator is running and the transfer switch has switched over, that 90A breaker and the subpanel it feeds will be dead.

Proposed Solution Analysis

Your idea of tapping off the load side of the 200A transfer switch sounds like it could work, but there are crucial considerations:1.

Load Calculation

The most important thing is to determine the load of your 90 amp breaker. That will determine the size of the tap you need and whether you can tap off of your transfer switch.2.

Code Compliance (NEC 240.21(B))

This section of the National Electrical Code (NEC) deals with "Feeder Taps." It allows you to tap conductors from a larger feeder (in this case, the load side of your 200A transfer switch) if certain conditions are met. The length of the tap conductors, their ampacity, and the overcurrent protection all matter.

Tap Conductor Ampacity

The tap conductors (#2 THHN in your proposal) must have an ampacity
at least equal to the rating of the overcurrent device at the end of the tap (your proposed 100A disconnect). #2 THHN is typically rated for 95A at 75°C, which may work depending on the load calculation.

Tap Length

The tap length is critical. There are different rules depending on the length:

10-Foot Tap Rule

If the tap conductors do not exceed 10 feet in length, are enclosed in a raceway, and have an ampacity not less than 1/10 the rating of the feeder (200A in your case), then you can tap. In your case, the conductors need to be rated at a minimum of 20 amps, and in a raceway.
25-Foot Tap Rule

If the tap conductors do not exceed 25 feet in length, are protected from physical damage, and the ampacity of the tap conductors is not less than 1/3 the rating of the feeder (200A), you can tap. In your case, the conductors need to be rated at a minimum of 66.6 amps.

Overcurrent Protection

The tap conductors must terminate in an overcurrent protection device (your proposed 100A disconnect) rated to protect the conductors and the load.3.

Physical Installation



Tap Connectors

Use listed and labeled tap connectors suitable for the size and type of conductors being connected. Wire nuts are generally not acceptable for tapping into large conductors like this. Use split-bolt connectors or insulated tap connectors designed for this purpose.

Disconnect Placement

Place the 100A disconnect immediately adjacent to the tap point from the transfer switch output, if possible, to minimize the tap conductor length.

Revised Approach (Recommended)

Considering the complexities of tap rules, the simplest and
safest approach is often the best:1.

Move the 90A Breaker

The
ideal solution would be to move the 90A breaker that feeds the subpanel to a location downstream of the 200A main breaker that feeds the transfer switch. This might involve some rewiring within your meter/main panel, but it ensures that the subpanel is always powered by either the utility or the generator when the transfer switch is active. If you do this, consult with a licensed electrician to ensure that you have enough breaker slots and that the load calculations for the panel still work.2.

Add a Sub-Feed Lug Kit to the Main Breaker
Another solution may be to add a sub-feed lug kit. A sub-feed lug kit allows you to land conductors that are not protected by the 200 amp main breaker. You would need to run that breaker to a junction box and then to the transfer switch. This ensures that the sub panel is on generator power and protected by the 200 amp main breaker.

Important Considerations



Load Calculation is KEY

Before making
any modifications, perform a thorough load calculation for both the existing 200A panels and the subpanel fed by the 90A breaker. Ensure that the existing service and generator can handle the total load.

Local Codes and AHJ

Always consult with your local electrical inspector (Authority Having Jurisdiction - AHJ) before making any changes to your electrical system. They may have specific requirements or interpretations of the NEC that you must follow.

Qualified Electrician

It's
highly recommended that you hire a licensed and experienced electrician to perform this work. Electrical work can be dangerous, and improper wiring can lead to fire or electrocution hazards.

In Summary:


While tapping off the load side of the transfer switch
might* be possible, it's complex and requires careful attention to NEC tap rules. Moving the 90A breaker (if feasible) is the preferred solution. Adding a sub-feed lug kit is also an alternative. Always prioritize safety and code compliance, and consult with a qualified electrician. Flag for review

Previous Question Next Question