Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Light Pole Receptacle

User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, October 15, 2024 at 8:04 am EDT
Answered on: Thursday, March 6, 2025 at 3:56 am EST

Question: Have a job that is being bid in the design stage(not fully designed). There are a lot of light pole with a receptacle on them. They said to figure two conduits to the light pole. One for the light and one for the receptacle. Is that a bad design? I understand if they come from different panels then they may need to be feed from separate conduits.

You're right to question this design. Here's a breakdown of why running separate conduits for the light and receptacle on a light pole, especially in the design stage, is potentially problematic and some alternatives to consider

Why It's Potentially a Bad Design:
Increased Cost



Materials

More conduit, more wire, more fittings (connectors, couplings, etc.).

Labor

More trenching, more conduit bending/installation, more wire pulling, more connections.


Maintenance

Double the conduits to maintain.

Underutilization

If both the light and receptacle are powered from the
same panel, you're essentially running redundant neutrals and grounds. This is unnecessary use of resources.

Trenching Congestion

Multiple conduits in the same trench can get crowded, making installation and future repairs more difficult, especially if other utilities are present.

Limited Capacity

Depending on the size of the pole base and handhole, fitting two conduits and all the associated wiring can be a challenge.


Code Compliance (Potential Issues)

While it's not inherently a code violation if done correctly, it can create situations where you're more likely to have violations (e.g., conduit fill, grounding, proper bonding).

Potential for Confusion

Having separate conduits can lead to confusion during maintenance and troubleshooting.

When Separate Conduits
Might Be Justified (and even then, alternatives may be better)



Different Voltage Systems

If the lighting is on a different voltage (e.g., 480V) than the receptacle (e.g., 120V or 240V), then separation is necessary.

Different Panels (and Isolation Required)

If the light and receptacle are fed from
different electrical panels, and the design intends to prevent a fault on one circuit from affecting the other, separate conduits could be used. However, even then, you could still run them in a single conduit as long as the cables/conductors are rated for the highest voltage present.

Specific Local Codes or Client Requirements

Some jurisdictions or clients may have specific requirements for separation. You need to verify this.

Future Expansion

If there are definite plans for significantly upgrading the receptacle's power requirements in the near future, installing a separate, larger conduit now might save money later. However, assess if this is truly cost-effective.


High Amperage

If the receptacles are for high amperage loads, it might be more cost effective to keep them separate from the light fixtures

Better Alternatives (Assuming Both Circuits are Fed From the Same Panel and Voltage)


Single Conduit, Shared Neutral/Ground

This is usually the most efficient and cost-effective approach. Run a single conduit from the panel to the pole base and use a multi-conductor cable or individual conductors rated for the voltage, containing: Phase conductor for the light. Phase conductor for the receptacle. Shared neutral conductor (sized appropriately for the total load). Shared grounding conductor (sized appropriately for the total load).

Important Considerations for Single Conduit



Neutral Sizing

The neutral conductor must be sized to handle the potential imbalance of the light and receptacle loads. If there are significant nonlinear loads (e.g., LED lighting with high harmonic distortion, electronic equipment plugged into the receptacle), you might need to increase the neutral size. Consider the requirements of NEC 220.61.


Voltage Drop

Calculate voltage drop for both the lighting and the receptacle circuits. The single conduit option can sometimes reduce voltage drop compared to two separate runs of smaller conductors, but you need to verify.

Conduit Fill

Make sure the conductors fit within the conduit's allowable fill percentage according to the NEC.2.

Hybrid Approach (If Necessary)

If you are running a second circuit, it might be worth investigating whether a multi-circuit conductor is the better choice, rather than running a dedicated set of single conductors, it might make more sense to run one conductor with multiple circuits, rated for all of the uses in question.

Recommendations for the Design Stage


Question the Requirement

Directly ask the client or design engineer
why* they specified two conduits. Understand the rationale behind the decision. Point out the increased cost and potential inefficiencies of the two-conduit design if the circuits are from the same panel and voltage.2.

Propose Alternatives

Present the single-conduit (shared neutral/ground) option as a more cost-effective and efficient solution. Back up your proposal with calculations (conduit fill, voltage drop, neutral sizing).3.

Consider Future Needs

Discuss any potential future expansion plans for the receptacle power. If significantly higher power is anticipated, a larger conduit might be warranted, but not necessarily a separate conduit for the light.4.

Check Local Codes

Confirm that your proposed design complies with all applicable local codes and regulations.5.

Value Engineering

Suggest that this item be considered for value engineering. A simple change to a single conduit system can save a significant amount of money on a project with many light poles.6.

Life-Cycle Cost Analysis:
If possible, present a life-cycle cost analysis comparing the two-conduit vs. single-conduit options. Consider installation costs, energy efficiency (due to reduced voltage drop), and long-term maintenance costs.By being proactive and presenting a well-reasoned alternative, you can potentially save the client money, simplify the installation, and create a more efficient and maintainable system. Flag for review

Previous Question Next Question