Question: I don’t see in 210.12 where bathroom light are on a ARC breaker? Does anybody know where it say’s it in the code book?
You are correct. Bathroom lighting outlets are not specifically required to be on AFCI (Arc-Fault Circuit Interrupter) protection according to NEC 210.12.NEC 210.12(A) generally requires AFCI protection for 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling units. However, the crucial part is where those outlets are located.Here's the breakdown: 210.12(A)
Requires AFCI protection for outlets in
dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas. Bathrooms are NOT listed in the areas requiring AFCI protection under 210.12(A). 210.12(B)
AFCI protection is required for branch-circuit extensions or modifications only if the extension/modification is more than 6 feet.
In summary
While bathrooms require GFCI (Ground Fault Circuit Interrupter) protection for receptacles near sinks (210.8), there is no specific requirement for AFCI protection for lighting circuits within bathrooms in the 2023 NEC (or previous versions).
Important Considerations
Local Amendments
Always check for local amendments to the NEC. Some jurisdictions may have added requirements for AFCI protection in bathrooms.
Specific Equipment
Some specific equipment (e.g., certain types of exhaust fans with lights) might have manufacturer's instructions that require AFCI protection. Always follow manufacturer's instructions.
Best Practices
While not required, some electricians might choose to install AFCI protection on bathroom circuits as a safety upgrade. It's a judgement call and depends on the specific installation and client preferences.Therefore, the answer to your question is:
There is nothing in NEC 210.12 that specifically requires bathroom lighting outlets to be on an AFCI breaker. You need to consult local amendments or manufacturer instructions to determine if there is an AFCI requirement for bathroom lighting in your specific situation. Flag for review