Topic: Short circuit current calculation at MV bus (34.5kV), Tesla Megapack

User: adityalagudu3291, Location: Austin

Asked on: Tuesday, October 15, 2024 at 11:04 am EDT
Answered on: Thursday, March 6, 2025 at 3:57 am EST

Question: In the process of calculating SCC at MV bus for a BESS plant. Utility POI fault current is at 40kA. Our only MPT size is 230/34.5, 210/280/350MVA, %Z = 10.5 @210MVA. Based on this the SCC at MV bus is coming around 30kA.From the BESS Inverter side planning to use TESLA MP2XL megapack rated for 1100KVA, 480V, 979kW and MP2XL qty is 300. What is the Short circuit current contribution by all these Inverters at the MV bus level?

Okay, let's break down the short-circuit contribution from the Tesla Megapack MP2XL inverters at your 34.5kV MV bus. Here's a step-by-step approach, along with considerations and assumptions

1. Megapack Inverter Contribution (Per Unit):
Typical Assumption

Inverters contribute a limited amount of fault current, usually expressed as a multiple of their rated current. A common and relatively conservative assumption is that an inverter can contribute 1.1 to 1.2 times its rated current during a fault.


Inverter Rated Current (at 480V)

`I_rated = S_rated / (V_rated sqrt(3))` `I_rated = (1100 kVA) / (0.48 kV sqrt(3))` `I_rated ≈ 1323 Amps`

Inverter Fault Current Contribution (Per Unit)

Let's use the 1.1 pu assumption. `I_fault_pu = 1.1 pu`

Inverter Fault Current (Amps)

`I_fault = I_rated I_fault_pu` `I_fault = 1323 A 1.1` `I_fault ≈ 1455 Amps`

2. Total Inverter Contribution at 480V (All 300 Megapacks)

`I_fault_total_480V = I_fault Number_of_Inverters` `I_fault_total_480V = 1455 A 300` `I_fault_total_480V ≈ 436,500 Amps`

3. Megapack contribution at 34.5kV
`Sbase_bess = 300 units 1.1MVA/unit = 330 MVA` `Ibess = Sbase_bess / (34.5kVsqrt(3)) = 5526 Amps` `Zbess = V^2/S = 34.5^2/330 = 3.6 ohms` `Zinv_pu_bess = Zbess Ibess / V = 3.6 5526/ (34.5kV) = .579 pu` `SCC_bess = Ibess / Zin = 5526 A / .579 pu = 9544 Amps`4. Total SCC Calculation at the MV Bus Utility SCC

40 kA at MV Bus

BESS SCC Contribution

9.544 kA at MV Bus


Total SCC

Utility SCC + BESS SCC Contribution

Total SCC

40 kA + 9.544 kA =

49.544 kA
Important Considerations and Caveats



Inverter Impedance Data

Ideally, get the actual impedance data (%Z or X/R ratio) from Tesla for the Megapack MP2XL. This will give you a more accurate fault current contribution. If this impedance is provided, it should be calculated as follows: `Z_inverter = V_base^2 / S_base` (where V_base is the inverter voltage (480V), and S_base is the inverter MVA rating (1.1 MVA). You might have to convert this to a per-unit impedance using a common system MVA base.

Transformer Impedance

Your MPT impedance of 10.5% is crucial. Make sure this is correct and on the correct MVA base (210 MVA).

Upstream Utility Impedance

The utility's 40 kA SCC value at the POI implies a certain impedance. Make sure you understand how that value was determined (e.g., from a utility short-circuit study). It is usually assumed the utility is an infinite source.


X/R Ratios

For a more accurate calculation, especially for protective device coordination studies, you need to consider the X/R ratios of the inverter, transformers, and utility. This affects the asymmetrical fault current.

Fault Type

Three-phase faults are usually the highest magnitude, so that's the common case to analyze. However, you might also need to consider single-line-to-ground (SLG) faults.


Decremental Effects

The inverter's fault current contribution might decay quickly in the first few cycles after the fault initiation. This is important for coordinating overcurrent protective devices.

In summary, you need to gather the following to accurately calculate SCC:
1. Inverter Fault Current Contribution (Actual Data)2. Utility SCC at the POI (Typically provided by the utility)3. Transformer Impedance (MPT) Flag for review