User: Isaiah, Location: Baton Rouge
Asked on: Tuesday, October 15, 2024 at 1:32 pm EDT
Answered on: Thursday, March 6, 2025 at 3:57 am EST
Question: I’m trying to size a 3ph 480V-480/277V transformer. Construction has already purchased a 4/W600kCMIL feeder (for the secondary to panelboard)- using 310.16 the amps are 420 at 75 degCSo if I size the XFMR secondary to the conductors I’d get a 200kVA with 480V-480-277V200000/277 x 1.732 = 417AIs this correct?
Yes, your calculation and reasoning are correct based on the information you've provided. Sizing the transformer based on the ampacity of the secondary conductors (420A) leads you to a 200kVA transformer.Here's a breakdown to confirm: Conductor Ampacity
Your 4/0 AWG with 600 kcmil neutral rated for 420A (at 75°C) is your starting point.
Desired Secondary Current
You want the transformer to supply approximately 420A at 480/277V.
kVA Calculation
Using the formula: kVA = (Volts Amps √3) / 1000 and solving for Amps: Amps = (kVA 1000) / (Volts √3) Amps = (200 kVA 1000) / (480 V 1.732) = 240.5 A (per phase) When using the Line-Neutral Voltage: Amps = (kVA 1000) / (Volts √3) Amps = (200 kVA 1000) / (277 V 1.732) = 416.64 A (per phase)
Transformer Size
A 200 kVA transformer (480V Delta primary to 480Y/277V Wye secondary) fits your needs and should match the capacity of the conductors.
Important Considerations and Potential Refinements
Load Calculation
The most important factor is the actual calculated load on the panelboard that this transformer will feed. The conductor ampacity is a limit, but the actual load should be calculated according to NEC Article 220.2.
Future Expansion
Always consider future expansion possibilities. If there's a reasonable chance of increased load, sizing up the transformer now could save significant costs later.3.
Inrush Current
Transformers have inrush current when initially energized, which can be several times the rated full-load current. The transformer must be able to withstand this inrush without damage or nuisance tripping of overcurrent protection.4.
Coordination
Ensure your transformer's overcurrent protection is properly coordinated with the feeder conductors and any downstream protective devices.5.
Tap Settings
Transformers often have tap settings on the primary side to compensate for voltage variations on the supply side. Consider the typical voltage at your facility when selecting tap settings.6.
Efficiency and Losses
Keep in mind that transformers have losses (core losses and winding losses). These losses will contribute to the overall energy consumption and heat generation.7.
Derating
Account for any derating factors that may apply due to ambient temperature or installation conditions.8.
Demand Factors
After applying demand factors for the entire calculated load, it may be possible to reduce the kVA size of the transformer.
Recommendation:
While your sizing is correct based on the conductors, I strongly recommend reviewing the actual calculated load (NEC Article 220) and future expansion plans before* making a final decision on the transformer size. Use the load calculation to verify if 200 kVA is sufficient, or if a larger size is needed. Flag for review