Topic: Surge protection for Multi-family Building

User: zemingduan, Location: Philadelphia,PA

Asked on: Tuesday, October 15, 2024 at 2:11 pm EDT
Answered on: Thursday, March 6, 2025 at 3:57 am EST

Question: The new code requires surge protection for the service for dwelling units. I am curious how do you implement this? For example we are using Square D (EZM series)/Eaton (3MM series) residential group metering with the meter stacks and main section for (60) apt units. The main section is 1600A 3ph with a main circuit breaker. The meter stacks are plugged into both sides of the main section. Is there a SPD can be installed at the main section of the residential meter bank? Or do you install individual SPD at the load center of each apt?Thanks!

You're asking a crucial question regarding surge protection in a multi-dwelling unit building, and the answer depends on the specific code requirements and best practices. Let's break down the options for implementing surge protection on your apartment project using Square D/Eaton equipment

Understanding the NEC and Surge Protection (SPD Requirements)
2020 NEC and Later (230.67)

This is the section of the NEC that you are referencing. It mandates surge protection for dwelling units. The core requirement is that a
Type 1 or Type 2 SPD must be installed in one of the following locations:

At the service equipment

This is at your main disconnect switch, upstream from all overcurrent protection.

On the load side

This is at the panel of each dwelling unit.


Type 1 vs. Type 2 SPD

The key difference is that Type 1 SPDs are designed to be installed without an external overcurrent protective device (OCPD). Type 2 SPDs require an OCPD. Type 1 SPDs are often used at the service entrance because they are directly connected to the electrical system.

Options for Implementing Surge Protection


Let's analyze your situation with Square D and Eaton equipment:1. SPD at the Main Service Disconnect (1600A Main Section)



Feasibility

Yes, this is a viable and often the
most economical approach for large multi-dwelling units. Installing a single, high-capacity SPD at the main service equipment protects the entire electrical system, including all the meter stacks and individual units.

Equipment



Type 1 SPD

These can be connected directly to the service bus bars
without an additional overcurrent protective device.

Type 2 SPD

If you use a Type 2 SPD, you

must
include a properly sized circuit breaker or fuses ahead of the SPD. Considerations for your 1600A Service

You need an SPD rated for a system of this size. Look for models with:


High Surge Current Capacity (kA)

The higher the kA rating, the better the SPD can handle large surges. Look for at least 200kA, but more is better. Consider your local lightning activity and historical surge events.

Voltage Protection Rating (VPR)

This indicates how well the SPD limits voltage during a surge. Lower VPR is better.


Suitable for 3-Phase Systems

Verify the SPD is designed for your 3-phase, 4-wire system (if applicable).

UL 1449 Listed

Ensure the SPD meets safety standards.


Square D Options

Look at the SurgeLogix series, or the PowerLogic series.

Eaton Options

Look at the
Eaton SPD Series or Cooper Bussmann Surge Protective Devices.

Installation

This typically involves connecting the SPD to the main service bus bars. Always de-energize the main service before working on it. Hire a qualified electrician experienced with high-current service entrances. The neutral and ground connections are critical. Follow the manufacturer's instructions precisely.

Advantages



Cost-Effective

Single, centralized SPD is generally cheaper than installing individual SPDs in each unit.

Easier Maintenance

Only one SPD to monitor and maintain.


Comprehensive Protection

Protects all downstream equipment, including meter stacks and individual panels.

Disadvantages



Single Point of Failure

If the main SPD fails, the entire building is unprotected until it's replaced. (However, most SPDs are designed to fail in a "safe" mode, often disconnecting themselves).

Less Specific Protection

May not provide the
absolute best protection for sensitive electronics in each unit (compared to individual SPDs) if the units have high surge generating sources.2.

SPD at Each Apartment's Load Center



Feasibility

Yes, this is also a code-compliant option.

Equipment

Use a
Type 2 SPD designed for residential load centers. These are typically compact, DIN rail-mounted units.

Installation

Each SPD is wired into the apartment's electrical panel, typically connecting to a dedicated circuit breaker.

Advantages



More Targeted Protection

Provides protection closer to the point of use, which can be beneficial for sensitive electronics.

Redundancy

If one SPD fails, the other units are still protected.


Disadvantages



Higher Cost

Requires 60 SPDs (one for each unit), significantly increasing the cost of materials and labor.


More Maintenance

60 SPDs to inspect and maintain.

More Labor for Installation

Installing 60 SPDs takes considerably more time.3.

Combination Approach



Feasibility

You could install a Type 1 or 2 SPD at the main service and Type 2 SPDs at some or all of the apartment load centers.

Advantages

This provides the highest level of protection, with multiple layers of defense against surges.


Disadvantages

This is the most expensive option and may be overkill unless the specific building has a high risk of surges.

Recommendation



Start with the SPD at the Main Service Entrance

Given the number of units (60), installing a high-quality, high-capacity Type 1 or Type 2 SPD at the 1600A main section is generally the most cost-effective and practical approach. Choose an SPD with a high surge current rating (e.g., 200kA or higher) and a low voltage protection rating. Make sure it's properly installed by a qualified electrician.


Consider Individual SPDs if...
After reviewing the cost of the main service entrance SPD, consider individual Type 2 SPDs at the load center of each unit if: Your client demands the highest possible level of protection. The building is in an area with extremely high lightning activity. The building houses sensitive electronic equipment that requires extra protection. The cost difference between one large and 60 small ones is negligable.

Important Considerations



Coordination

When using multiple SPDs in series (main and individual units), ensure they are properly coordinated. This usually means that the upstream SPD (at the main service) has a higher surge current capacity than the downstream SPDs (in the units). Consult with the SPD manufacturers for specific recommendations.


Grounding

Proper grounding is essential for surge protection to work effectively. Ensure the grounding system meets all applicable code requirements.

Local Codes and AHJ

Always check with your local Authority Having Jurisdiction (AHJ) for any specific requirements or interpretations of the NEC. They may have additional rules or preferences regarding surge protection.

Professional Installation

Surge protection devices should be installed by a qualified and licensed electrician who is familiar with the NEC and local codes.

Steps to Take


Consult with the AHJ

Discuss your plans with the local electrical inspector to ensure compliance.2.

Get Quotes

Obtain quotes from Square D, Eaton, and other SPD manufacturers for suitable Type 1 and Type 2 SPDs. Compare the specifications and prices.3.

Engage a Qualified Electrician

Hire an experienced electrician to perform the installation according to the manufacturer's instructions and all applicable codes.4.

Document Everything:
Keep records of the SPDs installed, the installation date, and any maintenance performed.By carefully considering these factors and following best practices, you can effectively implement surge protection for your multi-dwelling unit building. Remember, safety and code compliance are paramount. Flag for review