Question: Never saw that before , but L1-L2-L3 all have 480V between them. L1 to Gnd = 480V, L2 to Gnd = 0 (zero) V, L3 to Gnd = 480VHas anybody successfully been able to hook up any solar inverter to this? maybe the SMA TriPower in particular?https://www.facebook.com/gen819roof...vdryq93QXh9zWTVMNoV8qtjz8Bmk75wn7U82JVmLEUc7l

This sounds like a very unusual (and potentially dangerous) configuration. Let's break down what's being described and why it presents challenges for standard solar inverters.

Understanding the Reported Configuration L1-L2-L3 = 480V

This suggests a 480V three-phase system. Standard enough.


L1 to Ground = 480V

This is where things get strange.

L2 to Ground = 0V

This is highly unusual and problematic.


L3 to Ground = 480V

This continues the unusual pattern.

Why this is Problematic and Likely Unsafe
1. Not a Standard 480V Wye (Star) Configuration

In a typical 480V Wye (Star) system, you'd expect roughly 277V from each phase to ground (480V / √3 ≈ 277V). The 480V between phases is correct, but the voltage to ground is way off.2.

Not a Standard 480V Delta Configuration

A 480V Delta system typically does not have a grounded neutral. If one point of the Delta is grounded, the voltages to ground would be 0V for that point, and 480V for the other two. This would be called a "corner-grounded delta." However, the corner-grounded delta has only 480 volts between phases.3.

Possible Corner-Grounded Delta with Isolation Transformer Issue?
: Someone in the Facebook group suggested this. It might be possible, but it would still be incredibly unusual for a few reasons: Corner-grounded delta systems are rare in modern installations. Even with an isolation transformer, the "normal" thing to do is to establish a proper Wye (Star) configuration on the secondary of the transformer. The whole point of an isolation transformer is to establish a known, predictable grounding arrangement. The isolation transformer would have to be very specifically designed and rated to be corner grounded.4. Major Fault Condition or Wiring Error

More likely, this configuration is the result of a fault condition. A ground fault somewhere in the system (e.g., a short to ground on one of the phases) could potentially cause such voltage readings. It could also be a severe wiring error.5.

Danger

The lack of a proper neutral and the imbalanced voltages to ground create a significant shock hazard.

Why This Doesn't Work with Most Solar Inverters (Including SMA TriPower)
Inverter Design

Most modern grid-tie solar inverters are designed to work with specific, well-defined grid configurations:

Split-phase 120/240V

Common in residential installations.


Three-Phase Wye (Star) 208V, 277/480V, etc.

Common in commercial/industrial settings. Many inverters require a neutral connection for proper operation and safety. The absence of a consistent neutral makes this impossible.

Voltage Monitoring and Protection

Inverters constantly monitor grid voltage and frequency to ensure they are within acceptable ranges. If the voltage is too high, too low, or unbalanced, the inverter should disconnect for safety reasons.

Ground Fault Detection

Inverters have built-in ground fault detection circuitry. The configuration you describe would likely trigger these protections and prevent the inverter from operating.


SMA TriPower (Specifics)

The SMA TriPower is designed for three-phase Wye (Star) connections with a neutral. The installation manuals explicitly state the required grid voltage and grounding configurations. Connecting it to a system like the one described would almost certainly damage the inverter and void any warranty.

Can Anything Be Done?
The short answer is: NO. Do not connect a standard inverter to this system. This is likely a dangerous condition that needs to be investigated and corrected by a qualified electrician.

Here's why:1. Safety First

This is not a situation to experiment with. The voltages and grounding are highly irregular and could be lethal.2.

Qualified Electrician is MANDATORY

A licensed electrician with experience in three-phase power systems needs to diagnose the root cause of this voltage arrangement. They will need to: Verify the incoming utility feed and grounding. Check the service panel and all downstream wiring for faults. Confirm the transformer configuration (if any). Correct any wiring errors or ground faults.3.

Do NOT Try To "Hack" It

Attempting to force a standard inverter to work with this system is extremely dangerous and will likely damage the inverter.4.

Possible, Very Specific Exception (Highly Unlikely)

If the electrician determines this is a legitimate, intentionally designed corner-grounded delta system (again, unlikely), and if you can find an inverter specifically designed for corner-grounded delta systems, then maybe it could be made to work. However: These inverters are rare. You would need to provide the inverter manufacturer with detailed system information to ensure compatibility. The installation would need to be performed by a highly experienced electrician familiar with corner-grounded delta systems and* the specific inverter.

In Conclusion

The voltage readings you describe indicate a highly unusual and likely dangerous electrical configuration.

Do not attempt to connect any solar inverter to this system until a qualified electrician has thoroughly investigated and corrected the problem.
The safety risks and potential for equipment damage are far too great. Flag for review