User: Kevin.hndz, Location: New york
Asked on: Wednesday, October 16, 2024 at 11:03 am EDT
Answered on: Thursday, March 6, 2025 at 3:59 am EST
Question: I have about 5 one inch emts going into the same pull box my question is do I need a ground for each pipe to the box or is one ground in one of the pipes enough (from the pull box I have 3 one inch emts exiting into another pull box for another room and from that box 2 more into a last office )
Okay, let's break down the grounding requirements for your EMT conduit system and pull boxes according to the National Electrical Code (NEC). I need to provide a disclaimer that I am an AI and cannot provide official electrical advice. You should always consult with a licensed electrician for your specific project to ensure it meets all applicable codes and safety standards.Here's a general outline of the NEC's grounding requirements and how they apply to your situation
NEC Requirements Overview (Simplified):
Purpose of Grounding
Grounding provides a low-impedance path for fault current back to the source, allowing overcurrent devices (circuit breakers or fuses) to trip and clear the fault, protecting people and equipment.
Metal Conduit as Grounding Conductor
EMT conduit can serve as an Equipment Grounding Conductor (EGC) if properly installed and connected. The connections must be electrically continuous.
Grounding at the Source
The metal pull box needs to be effectively grounded. This usually means connecting it back to the main grounding electrode system at the service entrance.
Continuity
The entire metal raceway system (conduit and boxes) must be electrically continuous to provide a reliable grounding path.
Applying to Your Specific Scenario
Given your setup of multiple EMT conduits entering and exiting pull boxes, here's how grounding generally applies:1.
Grounding the First Pull Box
This is the most critical point. You must ground the first pull box effectively. The preferred method is to run a grounding electrode conductor (GEC) from the building's grounding electrode system (ground rod, water pipe, etc.) to the first pull box. This GEC must be sized appropriately for your electrical service. Consult NEC Table 250.66. Connect this GEC to a grounding busbar within the pull box, if it has one, or to the metal box itself with an approved grounding connector (e.g., a grounding lug). If you are feeding from a panelboard very nearby, you may be able to run an equipment grounding conductor (EGC) back to the panelboard.2.
Bonding Each EMT Conduit
Each EMT conduit entering and exiting the pull box must be properly bonded to the pull box to ensure electrical continuity. This is accomplished with proper conduit fittings, locknuts and bonding bushings.
Concentric or Eccentric Knockouts
If you are using concentric or eccentric knockouts in the pull box, you must use bonding bushings with a jumper wire. These types of knockouts can compromise the grounding path. Standard locknuts are not sufficient in these cases.3.
Downstream Pull Boxes
The subsequent pull boxes will be grounded through the EMT conduit connecting them to the first pull box (provided all connections are properly made). Ensure that all connections in these boxes are tight and properly bonded. As with the first box, use bonding bushings and jumpers if you have concentric or eccentric knockouts.4.
Equipment Grounding Conductor (EGC) Inside Conduit
You still have to run an EGC inside your EMT. This is sized according to the overcurrent device protecting the circuit. You must bond this EGC to each pullbox.
Answer to your question
One ground is not enough. You need to ensure each EMT conduit entering and exiting each pull box is properly bonded to the box to maintain electrical continuity. A common way to do this is with properly installed locknuts, conduit bodies or bonding bushings. The internal EGC must be bonded to each box as well.
Important Considerations
NEC Table 250.122
This table is used to determine the size of the equipment grounding conductor (EGC) based on the size of the overcurrent device (breaker or fuse) protecting the circuit.
Conduit Fittings
Use UL-listed fittings suitable for grounding.
Torque
Torque the conduit fittings to the manufacturer's specifications.
Insulated Grounding Bushings
Consider using insulated grounding bushings to prevent damage to the conductor insulation and to provide a smoother entry for the grounding conductor.
Best Practice (and often required)
Run a Supplemental Grounding Conductor
While the EMT can* serve as a grounding conductor, many electricians and inspectors prefer to also run a dedicated, insulated equipment grounding conductor (EGC) inside the conduit along with the circuit conductors. This provides a redundant grounding path and is often required, particularly in sensitive electronic environments or where increased safety is desired.
In summary:
Each EMT conduit needs to be mechanically and electrically connected to the pull boxes using appropriate fittings and methods to create a continuous grounding path. Grounding the first pull box back to the building's grounding electrode system is crucial. And an EGC run in the conduit and bonded to each box is also required. Always consult a licensed electrician to ensure compliance with local codes and safe installation practices. Flag for review