Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: SPD Requirements

User: AJ Electric, Location: Massachusetts

Asked on: Wednesday, October 16, 2024 at 11:42 am EDT
Answered on: Thursday, March 6, 2025 at 3:59 am EST

Question: Question,If I install an SPD at the main panel in a dwelling, do I also need an SPD at the sub panel?215.18 seems to say so, but 242.13 say I don't? Please advise...Inspector is asking for both..

You've hit on a common area of confusion with SPD (Surge Protective Device) requirements in the NEC, and you're right to question the inspector. Let's break down the code sections and provide clarity.

Understanding the Code Sections 215.18 Surge Protection

This section falls under Article 215, "Feeders." It mandates SPD installation at the
service equipment of a dwelling unit. This is the main panel where the power enters the building. This section does not explicitly require an SPD at a subpanel.

242.13 Surge Protection

This section falls under Article 242, "Overvoltage Protection." It deals with where SPDs are required based on the structure of the facility. This is where the confusion may come into play with your inspector. This section states:>

(A) Services.
A surge protective device (SPD) shall be installed on services of dwelling units in accordance with 230.67.>> (B) Separately Derived Systems. A surge protective device (SPD) shall be installed on all separately derived systems where the voltage to ground does not exceed 1000 volts nominal, except as permitted by 242.12(B).>> (C) Feeder Supplied Panelboards or Equipment. A surge protective device (SPD) shall be installed in or on all feeder-supplied panelboards or equipment where the voltage to ground does not exceed 1000 volts nominal, except as permitted by 242.12(B).>> (D) Branch-Circuit Supplied Panelboards or Equipment. A surge protective device (SPD) shall be installed in or on all branch-circuit supplied panelboards or equipment where the voltage to ground does not exceed 1000 volts nominal, except as permitted by 242.12(B).

The Key Point: Separately Derived Systems and Feeder Supplied Panelboards Is your subpanel a "Separately Derived System"? A separately derived system (SDS) is a power source like a generator, solar inverter, or a transformer that creates a new neutral point. The crucial point here is that the main panel feeds the sub-panel. It is NOT a separately derived system. Feeder Supplied Panelboards. This is where the inspector likely believes your subpanel requires surge protection. This rule requires that the feeder supplying your subpanel also have surge protection. However, since you are installing it at the main panel, this satisfies the requirement, so long as the subpanel is fed from the main panel.

The Verdict

Based on a plain reading of the NEC, installing an SPD at the main service panel of a dwelling unit satisfies the basic requirement for surge protection. You are not necessarily required to install an SPD at the subpanel.

Why the Inspector Might Be Insisting

Even though the code may not require it, there are some valid reasons why an inspector might suggest or even insist on an SPD at the subpanel: Better Protection

While the main panel SPD offers some protection, it may not completely protect sensitive electronics connected to the subpanel. A local SPD can provide better protection against surges originating
within the home or induced on the feeder.

Long Feeder Runs

If the feeder run between the main panel and the subpanel is long, the SPD at the main panel may not be as effective in clamping voltage surges at the subpanel end.

Specific Equipment

If the subpanel feeds very sensitive or expensive equipment, the inspector might deem additional surge protection prudent.

How to Proceed
1. Politely Discuss with the Inspector

Explain your understanding of the code, highlighting that you're meeting the
minimum requirement with the main panel SPD. Ask the inspector to point out the specific code section requiring an SPD at the subpanel, considering it's not a separately derived system.2.

Show Them This Discussion (if appropriate)

You can show the inspector this conversation. We've outlined the relevant code sections and the logic.3.

Document Everything

Keep a record of the conversation, the inspector's rationale, and any specific requirements they're imposing.4.

Consider the Inspector's Reasoning

Even if not strictly required by code, an SPD at the subpanel
can offer additional protection. Weigh the cost of the additional SPD against the potential benefits.5.

Appeal (if necessary)

If you strongly disagree with the inspector and they're adamant, you can appeal their decision through the local building department's established process.

In summary:
While an SPD at the subpanel may provide enhanced protection, the NEC, in most interpretations, only requires* an SPD at the service equipment (main panel) for a dwelling unit. Have a respectful discussion with the inspector, understand their reasoning, and make an informed decision. If they can cite the code that justifies their reasoning, you may have to install it. If not, hopefully this explanation helps! Flag for review

Previous Question Next Question