Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Wiring 4-20mA splitter

User: Electromatic, Location: Virginia

Asked on: Wednesday, October 16, 2024 at 12:00 pm EDT
Answered on: Thursday, March 6, 2025 at 3:59 am EST

Question: I have a 4-20mA level sensor wired to a pump PLC. In addition to the level signal controlling a drive, the PLC is supposed to output the signal to a telemetry/data-logging unit. That output isn't responding, and I don't have access to the PLC programming to try a different output channel. I want to install a signal splitter to get the sensor signal to the PLC and the telemetry unit, but when I went to do it, I kept confusing myself on where/how to insert the splitter into the existing loop.Below is a sketch of how I think it should be done and a spec sheet on the splitter. Any input would be appreciated. TIA

Okay, I understand your situation. You have a 4-20mA level sensor already wired to a PLC, and you need to tap that signal to send to a telemetry unit without altering the PLC programming or existing wiring too much. You want to use a signal splitter for this. Let's analyze how to properly insert the signal splitter into the existing 4-20mA loop.

Understanding the Basics 4-20mA Current Loop

A 4-20mA current loop works on the principle that the current flowing through the entire loop is consistent. The sensor modulates the current (4mA represents the minimum level, 20mA the maximum, and values in between for corresponding levels). Devices in the loop are powered by the same current flow and can read the signal voltage developed across a load resistance (typically a precision resistor).


Signal Splitter

A signal splitter takes a single 4-20mA input signal and creates two (or more, depending on the model) isolated 4-20mA output signals. Critically, a good signal splitter should not significantly impact the original loop's operation or accuracy. Isolating the output(s) is essential for avoiding ground loops and interference.

Analyzing Your Proposed Wiring (Based on your likely sketch - since I can't see it, I'll assume the common scenarios)

I am going to assume you have some common issues in mind and address them. The most likely scenarios are:1.

Incorrect Power Supply/Load Resistor Configuration

Attempting to simply parallel wire the telemetry unit into the existing loop without a splitter is the most common error. Or incorrect power supply configuration for the splitter.2.

Confusion on Wiring the Splitter's Input and Outputs

Misunderstanding which terminals are for input, output, and power on the splitter.3.

Forgetting Required Power for the Splitter

Most signal splitters require their own DC power supply.

Correct Wiring Procedure (Based on Assumptions Above)

Here's the recommended procedure for wiring the signal splitter, based on the common errors I often see when assisting customers with 4-20mA loop issues:1.

Verify Power Supply Requirements

Crucially, check the splitter's spec sheet for its power supply requirements (voltage, DC or AC, current). You will need a suitable power supply to power the splitter itself.2.

Disconnect the Sensor

Disconnect the two wires running between the level sensor and the PLC input terminals. Note which wire goes to which terminal on the PLC. (Positive/Negative)3.

Wiring the Splitter Input

Wire the level sensor + wire to the splitter input + terminal Wire the level sensor - wire to the splitter input - terminal4.

Wiring Splitter Output to PLC

Connect a wire from the Splitter Output #1 + terminal to the PLC's original input + terminal. Connect a wire from the Splitter Output #1 - terminal to the PLC's original input - terminal.5.

Wiring Splitter Output to Telemetry Unit

Connect a wire from the Splitter Output #2 + terminal to the Telemetry Unit's + input terminal. Connect a wire from the Splitter Output #2 - terminal to the Telemetry Unit's - input terminal.6.

Connect Power to the Splitter

Connect the appropriate DC power supply to the splitter's power input terminals.7.

Double-Check Everything

Verify all wiring connections before applying power. Especially polarity.8.

Apply Power

Apply power to the splitter and the PLC.9.

Verify Operation

Check the level readings at both the PLC and the telemetry unit. They should be consistent.

Key Considerations and Troubleshooting Tips



Ground Loops

Ensure that the signal splitter provides
isolation between the input and both outputs. If you experience erratic readings, ground loops are a possible cause.

Wiring Errors

Always double-check the wiring. Incorrect polarity can damage equipment.

Splitter Configuration

Some splitters have configuration options (e.g., range settings, output scaling). Refer to the splitter's manual for details.


Power Supply Quality

Use a stable, regulated power supply for the splitter.

Testing

If possible, use a multimeter to measure the current in each loop (PLC and telemetry) to verify that it is within the expected 4-20mA range.

Example Scenario (Assuming a typical setup)


Let's assume:
Level Sensor: Two-wire, loop-powered 4-20mA PLC Input: Reads 4-20mA signal Telemetry Unit: Reads 4-20mA signal Splitter: Two-output, isolated, 24VDC powered.Then the wiring steps above would be a good guide.

Important Disclaimer

Electrical work can be dangerous. If you are not comfortable working with electrical wiring, consult a qualified electrician or instrumentation technician. Always follow all applicable safety regulations and manufacturer's instructions. I have provided general guidance based on typical scenarios, but you are responsible for verifying compatibility and safety for your specific equipment and application.

Providing More Information:


If you can provide more specific details about your level sensor, PLC input specifications, telemetry unit input specifications, and the
exact* model number of your signal splitter (or ideally, a link to its datasheet), I can provide even more tailored advice. Good luck! Flag for review

Previous Question Next Question