User: jjwitty, Location: Indianapolis
Asked on: Wednesday, October 16, 2024 at 6:34 pm EDT
Answered on: Thursday, March 6, 2025 at 4:01 am EST
Question: I have been working on a stretch wrapper, and the wrapper motor won’t kick on. I have 2 issues, one is the resistance of the strain beams, and two is my control power.When I turn machine on without control power, I have 120 to ground. When I have control power, I get 60 to ground on hot and neutral. I cannot for life of me find any buried neutrals or loose wires. I’m not sure is this alone is even enough to stop the machine from working. I thought it would work but be unsafe, that’s why I am fixing it. I realize something in my control circuit is not wired correctly. I’ve tried unplugging each device while measuring voltage back to ground and nothing changes. Any thoughts?
Okay, let's break down this electrical puzzle systematically. You have two primary concerns: strain gauge resistance issues and control power issues, both of which could be contributing to your wrapper motor not starting.
Understanding the Issues Strain Gauge Resistance
Without knowing the expected resistance and measured resistance, it's hard to diagnose if this is a problem. Strain gauges are typically used for tension control in stretch wrappers, and incorrect readings could prevent the motor from starting if the control system thinks the film is already at the desired tension.
Control Power Issues (120V dropping to 60V)
This is a significant problem and likely the primary cause of your motor not working. A 50% voltage drop indicates a massive impedance issue (resistance or other factor) in your control circuit. This can definitely prevent control relays, PLCs, or other components from functioning correctly. The fact that you're seeing this on both hot and neutral is very suspicious.
Troubleshooting Steps1. Control Power Analysis (Priority #1 - Safely) Safety First
Before doing anything,
lock out and tag out (LOTO) the machine. Treat this like a potentially lethal situation (because it could be!). Disconnect the Load (Most Important)
Completely disconnect all loads from your control power transformer (or power supply). This means disconnecting everything powered by that 120V. Leave ONLY the incoming power leads connected to the transformer/power supply.
Incoming Voltage
Verify the correct input voltage to the control power transformer/power supply (e.g., 240V, 480V, etc.) Is it stable and within the acceptable range of the transformer?
Measure Output Voltage (No Load)
With ALL loads disconnected, measure the voltage between the 120V output terminals. It should be very close to 120V.
If the voltage is still low (around 60V with no load)
The problem is the control power transformer/power supply itself. It's likely failing or has an internal short. Replace it. Do not proceed further until you have a stable 120V output with no load.
If the voltage is good (close to 120V with no load)
The problem is somewhere in the control circuit. Proceed to the next step.2.
Isolate the Problematic Control Circuit Component
Re-connecting Loads Methodically
With the control power transformer outputting 120v correctly (no load), carefully re-connect components to the 120V circuit one at a time. After connecting each component, check the voltage on the 120V circuit. The instant the voltage drops to 60V (or lower), you've found the problematic circuit.
Check Components for Shorts
Once you've identified the problem circuit, you can then investigate the components in that circuit further. Look for:
Visually Damaged Components
Burned or melted components are a sign of a short or overload.
Wiring Issues
Loose connections, pinched wires, or wires rubbing against metal can cause shorts.
Component Testing
Use a multimeter to check the resistance of components. A near-zero resistance reading across a component that should have a higher resistance indicates a short.
Relays/Solenoids
A shorted coil in a relay or solenoid is a common culprit. Test the coil resistance.
PLC Inputs/Outputs
If the PLC is involved, disconnect the wires connected to the PLC's I/O points in the problem circuit and check the voltage. If the voltage returns to normal when disconnected, the PLC I/O could be damaged.
Wiring Harnesses
Carefully examine the entire wiring harness in the problem circuit. Look for signs of damage or wear, especially where the harness passes through metal panels or is subjected to movement.
Document Your Work
Keep detailed notes of your tests and findings. This will help you track your progress and avoid retracing your steps.3.
Strain Gauge Evaluation
Obtain Specifications
Find the datasheet or technical specifications for the strain gauges being used. This will tell you their nominal resistance (usually in ohms) and their expected output voltage change under different tension levels.
Measure Resistance
Disconnect the strain gauges from the control system and measure their resistance with a multimeter. Compare the measured resistance to the specifications.
Check for Damage
Visually inspect the strain gauges and their wiring for any signs of physical damage.
Simulate Tension (Carefully)
If possible (and safely – do not exceed any limits!), apply a small amount of tension to the film while monitoring the output voltage of the strain gauges. See if the output changes as expected.
Calibration
Strain gauge systems often require calibration. Check the machine's documentation for calibration procedures.
Addressing the Low Voltage to GroundThe fact that you're seeing 60V to ground on both hot and neutral only when the control power is on points to a significant problem in your control circuit's grounding.
Grounding Integrity
Verify a Solid Ground Connection
Ensure the control power transformer/power supply has a good, solid ground connection to the machine's frame and to the main electrical panel's ground.
Check Grounding Conductors
Inspect all grounding conductors in the control circuit for damage or loose connections.
Eliminate Ground Loops
Ensure there is only one point where the control circuit's ground is connected to the machine's frame. Multiple ground connections can create ground loops, which can cause unpredictable voltage readings and interference.
Specific Thoughts on Your Situation
Buried Neutrals
While you haven't found one yet, the 60V on both hot and neutral suggests that a neutral wire is making unintended contact with ground somewhere in the circuit when powered. This is the "phantom voltage" that is causing the issue.
Control Transformer Polarity
Double-check that the incoming and outgoing wires on the control transformer are wired correctly. If the polarity is reversed (unlikely, but worth checking), it could cause some weird voltage readings.
Capacitor in the Circuit
Sometimes capacitors are used in control circuits for noise suppression. A failing capacitor could create a path to ground, causing voltage drops.
Important Considerations
Qualified Electrician
If you're not comfortable working with electrical systems or are unsure about any of these steps, it's best to consult with a qualified electrician. Electrical work can be dangerous if not done properly.
Machine Documentation
Refer to the machine's electrical schematics and manuals. These will be invaluable for troubleshooting and understanding the control system.
Component Datasheets: Obtain datasheets for all the major components in the control circuit. These will provide valuable information about voltage and current ratings, resistance values, and other critical parameters.By systematically working through these steps, you should be able to isolate the problem and get your stretch wrapper back up and running safely. Remember safety first! Flag for review