Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 3ph 480v wrt htr

User: timmer, Location: Phila PA

Asked on: Thursday, October 17, 2024 at 7:45 am EDT
Answered on: Thursday, March 6, 2025 at 4:02 am EST

Question: replacing an existing water heater that is 3000w with new one that is 3500w ,3ph 480v water heater .wire size? breaker size?

Okay, let's break down the wiring and breaker requirements for a 3.5kW, 3-phase, 480V water heater replacing a 3kW single-phase water heater. Here's what we need to consider, along with the relevant calculations.1. Calculate the Current (Amps)

First, we need to determine the current draw of the new water heater. For a 3-phase circuit, the formula is: Amps = (Watts) / (Voltage √3)

Where: Watts = 3500 Voltage = 480 √3 (Square root of 3) ≈ 1.732So: Amps = 3500 / (480 1.732) Amps = 3500 / 831.36 Amps ≈ 4.21 Amps2. Overcurrent Protection (Breaker Size) NEC Requirement for Continuous Load

Water heaters are considered continuous loads. The National Electrical Code (NEC) requires that overcurrent protection (the breaker) be sized at no less than 125% of the continuous load current.

Calculate 125%

4.21 Amps
1.25 = 5.26 Amps

Standard Breaker Size

You'll need a breaker that's
at least 5.26 Amps. The smallest standard breaker size above that is typically

15 Amps
. Although 5 amps is the calculated minimum, the smallest breaker available to install is 15 amps.

Important Note

A 15 Amp breaker is what
I calculate. Because of the inherent dangers of electrical wiring, it is very important that a certified electrician do the work.

3. Wire Size


Now, let's determine the appropriate wire size. NEC Table 310.16 (or the equivalent table in your local code) provides ampacity ratings for different wire types and sizes. We need to choose a wire that can safely carry the
125% of the load current (5.26 Amps). Considerations



Wire Type

Common wire types for this application are THHN/THWN (thermoplastic high heat-resistant nylon-coated/thermoplastic heat and water-resistant nylon-coated) copper conductors. The ampacity rating varies depending on the insulation type, temperature rating (60°C, 75°C, 90°C), and installation method.


Temperature Rating

Choose a wire with a temperature rating appropriate for the environment where it will be installed.

Installation Method

The ampacity rating also depends on how the wires are installed (e.g., in conduit, cable, open air).


Typical Recommendation

For a 15 Amp breaker,

14 AWG copper wire
rated for 75°C or 90°C is generally sufficient.

Important Note

Although this is what I calculate, it is important that a licensed electrician is involved.

4. Grounding
Importance

Proper grounding is absolutely essential for safety. The water heater must be grounded according to NEC requirements.


Equipment Grounding Conductor (EGC)

You'll need an equipment grounding conductor (EGC) that is sized appropriately for the overcurrent protection device (the breaker). Refer to NEC Table 250.122 to determine the correct size of the EGC. For a 15 Amp breaker,

14 AWG
copper wire is generally sufficient for the EGC.5. Disconnect Switch (Highly Recommended) Install a local disconnect switch near the water heater. This allows for safe servicing and maintenance without having to go back to the main electrical panel. The disconnect switch must be rated for the voltage and current of the water heater.

Summary and Important Considerations
Breaker Size

15 Amp, 3-pole breaker.

Wire Size

14 AWG copper conductors (THHN/THWN or equivalent), 3 conductors plus a grounding conductor.


Grounding

14 AWG copper grounding conductor.

Disconnect

Local disconnect switch rated for 480V and at least 15 Amps.

Crucial Notes and Disclaimer



This information is for general guidance only. It is NOT a substitute for professional advice from a licensed electrician.
Electrical work can be dangerous, and incorrect wiring can lead to fire, injury, or death. Local Codes

Always comply with all applicable local electrical codes and regulations. Local codes may be stricter than the NEC.


Electrician is Required

Hire a qualified and licensed electrician to perform the installation. They will be able to assess your specific situation, ensure compliance with all applicable codes, and perform the work safely.

Voltage Compatibility

Confirm that the existing electrical panel and wiring are compatible with the 480V, 3-phase power required by the new water heater. You will need 3 phase power available at the location.


Existing Wiring

Have the electrician inspect the existing wiring to ensure it is in good condition and suitable for the new water heater. If the existing wiring is old, damaged, or not properly sized, it will need to be replaced.*

Permits:
Obtain any necessary permits from your local building department before starting the work.By following these guidelines and using a qualified electrician, you can ensure a safe and compliant installation of your new water heater. Good luck! Flag for review

Previous Question Next Question