Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Zigzag Transformers for Islanding TOV on PV Projects

User: cyriousn, Location: ME / CT

Asked on: Thursday, October 17, 2024 at 10:23 am EDT
Answered on: Thursday, March 6, 2025 at 4:02 am EST

Question: I'm trying to understand why grounding transformers are put on solar projects where the transformer is Yg-Yg. Is it due to the condition where the ground source is lost if the breaker at the local substation is tripped and the PV site is islanded with the distribution circuit until the PV site shuts down in 2 seconds or less due to islanding detection?I'm working on a project where there is a zigzag transformer connected on the 600V side of the 23kv/600v Yg-Yg Transformer. The zigzag is fed from a 400A electronic breaker in a switchboard that shunt trips the 2500A MCB. Typically I see Yg - Delta grounding transformers on solar projects so this is a new one for me.Wouldn't the grounding transformer, under steady state conditions, be a grounding source for the local distribution circuit for imbalances? The rating of the transformer is 867A continuous on the neutral. Is there an easy way to determine what conditions on the distribution circuit could trip the circuit breaker and dump the project?

You've touched on several important points regarding grounding in solar projects with Yg-Yg transformers. Let's break down the reasons for grounding transformers, why zigzag transformers are sometimes used, and how they might interact with the distribution system.

Why Grounding Transformers on Solar Projects (Especially with Yg-Yg Transformers)



Ground Fault Current Path

The primary reason for a grounding transformer is to provide a reliable, low-impedance path for ground fault current. This is absolutely critical for protective relaying to function correctly. Without a solid ground reference, ground faults can be low magnitude, difficult to detect, and potentially damaging.


Yg-Yg Transformer Issues

Yg-Yg transformers can have issues with circulating third harmonic currents and ferroresonance, but the main issue is that a Yg-Yg transformer connected to a grounded grid will cause voltage distortion as it will pass zero sequence current and create a virtual ground on the site.



Islanding Mitigation

Your islanding scenario is a key consideration. When a solar plant islands with a portion of the distribution circuit, the grounding source from the substation may be lost. The grounding transformer provides a local ground reference to ensure ground faults can still be cleared during this brief islanded period (until the islanding detection shuts down the PV). Without it, faults during islanding could be prolonged and damaging.


Grid Requirements

Many utilities require a dedicated grounding source for solar plants, regardless of the transformer configuration. This is for overall grid safety and protection coordination.

Zigzag vs. Yg-Delta Grounding Transformers



Functionally Similar (Mostly)

Both zigzag and Yg-Delta grounding transformers achieve the same primary goal: creating a neutral grounding point from an ungrounded or poorly grounded system.


Zigzag Advantages



Better Harmonic Performance

Zigzag transformers tend to have better harmonic performance, particularly in suppressing third harmonics. This can be an advantage if the solar inverters are injecting significant harmonic currents into the system.


Lower Impedance to Ground Faults

Often, zigzag transformers can be designed with a lower zero-sequence impedance than Yg-Delta transformers of comparable size. This means they can provide a more robust ground fault current path.

Smaller Footprint

For the same kVA rating, a zigzag transformer can sometimes be physically smaller than a Yg-Delta transformer.


Zigzag Disadvantages



Continuous Neutral Current

Zigzag transformers, by their nature, will carry a small amount of continuous current in the neutral under normal conditions due to slight imbalances in the system. This current is usually small but needs to be considered in the neutral conductor sizing.

Analyzing the Zigzag Transformer and Breaker Tripping


Steady-State Neutral Current

The 867A continuous neutral current rating of your zigzag transformer is quite high. This implies the manufacturer anticipates significant imbalance in the 600V system or the potential for harmonics.
Monitor Neutral Current: Use a power quality meter to monitor the actual neutral current flowing in the zigzag transformer under various operating conditions. This will give you a baseline.2.

Ground Fault Protection on the 400A Breaker

Your 400A breaker is designed to shunt trip the 2500A main breaker. This is a common scheme to quickly disconnect the solar plant for ground faults.3.

Potential Causes of Breaker Tripping

Here's where you need to investigate:

Ground Faults in the PV Array

A ground fault in the solar panels, combiner boxes, DC wiring, or inverters is the most likely cause of a trip. These faults will create a large current flow through the zigzag transformer's neutral, tripping the 400A breaker.
Insulation Testing: Thoroughly test the insulation of all DC components to look for weak spots or existing faults. Ground Fault Detection Settings: Review the ground fault detection settings of your inverters. Are they too sensitive? Are they properly coordinated with the 400A breaker?

Ground Faults in the 600V AC System

A fault in the 600V AC wiring, switchgear, or the low-voltage side of the Yg-Yg transformer could also cause a trip.

Harmonic Issues

Excessive harmonic currents from the inverters can overload the zigzag transformer, potentially causing the 400A breaker to trip. While the zigzag transformer helps
mitigate harmonics, it can also be overloaded by them.

Utility-Side Imbalances

This is important. If there are significant voltage or current imbalances on the 23kV distribution circuit, these can couple through the Yg-Yg transformer and create current flow in the zigzag transformer's neutral. This is not ideal and can indicate a problem on the utility side. Power Quality Monitoring: Install power quality meters on both the 600V and 23kV sides of the Yg-Yg transformer to monitor voltage and current balance, harmonic distortion, and any other abnormalities. Coordination with the Utility: Discuss your grounding scheme and the potential for utility-side imbalances to affect your plant with the utility engineers. They may be able to provide data or insights into the stability of their distribution circuit.

Islanding Events

If the islanding detection fails to operate correctly, the system might try to clear faults on its own while islanded, potentially causing trips.

Determining Conditions that Could Trip the Breaker



Fault Studies

Conduct detailed fault studies (using software like ETAP, SKM, or EasyPower) to simulate ground fault conditions at various points in your PV system and the 600V AC system. This will help you determine the fault current magnitude and how it flows through the zigzag transformer and protective devices.

Protective Device Coordination Study

A protective device coordination study will ensure that the 400A breaker is properly coordinated with the other protective devices in the system (inverter protection, 2500A breaker, utility relays).


Power Quality Monitoring (Critical)

Continuous power quality monitoring is essential. You need to log data to see what's happening before a trip occurs. Look for: High neutral current Voltage or current imbalances Harmonic distortion Voltage sags or swells

In Summary: The zigzag transformer is providing a critical grounding function, especially given the Yg-Yg transformer configuration. The 867A neutral current rating suggests the system anticipates significant imbalance or harmonic issues. Investigate potential causes of breaker tripping, focusing on ground faults, harmonic distortion, utility-side imbalances, and protective device coordination. Power quality monitoring and fault studies are crucial for understanding the system behavior and preventing nuisance trips.* Communicate with the utility about their system conditions and any potential impacts on your solar plant's grounding.I hope this detailed explanation helps you understand the role of the zigzag transformer and troubleshoot your project. Good luck! Flag for review

Previous Question Next Question