Topic: 6/3 romex used to feed a 70amp pool sub panel outside?

User: Bashacses, Location: New Hampshire

Asked on: Thursday, October 17, 2024 at 2:05 pm EDT
Answered on: Thursday, March 6, 2025 at 4:03 am EST

Question: Can you use 6/3 romex to feed a 70 amp pool sub panel outside . Pool company ran 6/3 romex indoors then changed over to #6 Thhn outside in the conduit to the outside panel.Question isI thought you had to use the 60c column rule in 310.15.B because any breaker 125 amp or less must use the 60 rating per UL lug listing.So a #6 would only be aloud up to 55 amps not 70 amps.

You're absolutely right to be concerned about the ampacity of the #6 conductors. Here's a breakdown of the situation and why your concerns are valid

Key Considerations:
60°C Ampacity Rule (310.15(B)(16) and UL Listings)

As you mentioned, the general rule is that when terminating conductors on equipment rated 100 amps or less, you must use the 60°C ampacity column in Table 310.15(B)(16). This is because most termination points (breakers, lugs, etc.) are only rated for 60°C. Some equipment is rated for 75°C. So you are correct to be concerned because unless you know the equipment is rated for 75C or greater you are limited to the 60c rating.


NEC 110.14(C)

This section specifically addresses terminal temperature limitations. It requires that the conductor be selected such that it is rated to withstand at least the minimum temperature rating associated with the termination point. This reinforces the use of the 60°C ampacity for most terminations rated 100 amps or less.

THHN Ampacity

THHN conductors have a higher insulation temperature rating (typically 90°C). However, because of the termination limitations, you generally can't take advantage of the higher ampacity unless the equipment is specifically listed and marked for 75°C or 90°C terminations.


Romex (NM Cable)

NM cable is typically rated 60°C, and this applies to its entire length, even if the individual conductors within it are rated higher (e.g., THHN). Since the conductors are typically THHN in Romex they can be rated 90C.

Analysis of the Situation


Romex Inside

The 6/3 Romex inside is effectively limited to its 60°C ampacity rating throughout its run because of the nature of NM cable. This is because the conductors are bundled together in a cable assembly, which limits heat dissipation.2.

Transition to THHN Outside

Changing to #6 THHN in conduit outside doesn't automatically solve the ampacity problem. Unless the terminations at both ends (the point where the Romex connects to the THHN in the junction box, and the terminations at the subpanel) are specifically listed for 75°C or 90°C, you're still restricted to the 60°C ampacity.3.

#6 Ampacity

Looking at Table 310.15(B)(16), #6 copper wire is rated as follows: 60°C: 55 Amps 75°C: 65 Amps 90°C: 75 Amps4.

The Problem

You're using #6 conductors to feed a 70-amp subpanel. If the terminations are only rated for 60°C, the #6 conductors are only rated for 55 amps. This is a potential code violation and safety hazard.

What Needs to Be Done


Verify Termination Temperature Ratings

Carefully check the breaker and lug terminations at both ends of the #6 THHN run (at the main panel connection/junction box, and at the pool subpanel). Look for markings that specifically state the terminations are rated for 75°C or 90°C.2.

If Terminations are NOT 75°C/90°C Rated



Recalculate the Load

Determine if the actual load on the subpanel requires a 70-amp breaker. It's possible the pool equipment doesn't actually need that much capacity. If so, you could downsize the breaker to 50 or 55 amps (depending on what the actual load requires) to match the #6 conductor's 60°C ampacity rating.

Increase Conductor Size

The best and safest option is to replace the #6 THHN with a larger gauge conductor that has an ampacity of at least 70 amps at the 60°C rating. #4 copper is generally rated for 70amps at 60C.


Consider Aluminum Conductors

If using aluminum conductors, you'll need even larger sizes to achieve the necessary ampacity.

Important Notes



Oversizing Doesn't Hurt (within reason)

Using conductors that are
larger than required is generally okay (as long as they fit properly into the terminations). It's always better to err on the side of safety with conductor sizing.

Professional Advice

Given the complexities and safety implications of electrical work, it's highly recommended to consult with a licensed electrician to ensure the installation meets code requirements and is safe.*

Local Codes:
Be aware that local codes may have additional requirements that go beyond the NEC. Always check with your local building department.In summary, your concern about the ampacity of the #6 conductors is valid. You need to verify the termination temperature ratings and take corrective action if the conductors are undersized for the 70-amp breaker and 60°C terminations. Flag for review