Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 100A Subpanel

User: Sandlamb, Location: Ohio

Asked on: Thursday, October 17, 2024 at 3:36 pm EDT
Answered on: Thursday, March 6, 2025 at 4:03 am EST

Question: I don’t understand why we can’t use #2 AL to feed a 100A subpanel but we can use it to run a 100A service. Can’t find 1 nor 1/0 quadruplex around me nor can I find a 90A breaker! Will 100 be ok?

Okay, let's break down why you can use #2 Aluminum (AL) for a 100A service entrance, but often not for a 100A subpanel feeder, and address your other questions. This is a common source of confusion, and it's rooted in the National Electrical Code (NEC).

The Key: The 310.15(B)(7) "Service Entrance Conductor" Exception The NEC has a special provision specifically for service entrance conductors for one-family, two-family, and multifamily dwellings. This provision is found in NEC 310.15(B)(7) (formerly 310.15(B)(6) in older codes). It allows a smaller conductor size to be used for the entire service entrance conductors, based on the total calculated load of the dwelling unit. Key takeaway

This exception only applies to the service entrance conductors. It doesn't apply to feeder conductors running to subpanels or other loads within the building. The exception is based on the assumption that the entire load of a dwelling unit is very rarely fully utilized at once. This is a statistical thing. This allows for a smaller conductor to handle the anticipated normal load, even though the service has a higher rating.

Why #2 AL for 100A Service?
Using the Exception

Under 310.15(B)(7), you might be able to use #2 Aluminum for a 100A service. This is conditional. Here's how it works: You must calculate the entire service load of the dwelling unit using NEC Article 220. This is a detailed process. If that calculated load is less than or equal to 83 amps, then you can use #2 Aluminum conductors for your 100 amp service. This is because the 310.15(B)(7) exception allows you to use the 75°C ampacity rating of the #2 AL, which is 90A, for services rated 100A through 400A.

Important: The size of the service entrance is still 100A, even though the wire is smaller.
The exception is not a free pass! You absolutely must perform the load calculation to ensure that your service load is less than or equal to 83 amps. Also important

310.15(B)(7) often includes a "Main Disconnecting Means" requirement. It states that the overcurrent protection device protecting the service entrance conductors can't exceed the ampacity of the conductors. For example, if the calculated load is 83A, #2 AL can be used.

Why NOT #2 AL for 100A Subpanel Feeder?
No Exception

The 310.15(B)(7) exception does not apply to subpanel feeders. You cannot use it for subpanel wiring.

Standard Ampacity Rules

For subpanel feeders, you must use the standard ampacity tables in NEC 310.16 and 310.
17. Typically, you have to use the 75°C column for terminations rated 75°C. The 75°C ampacity rating of #2 AL is 90 amps.


100A Feeder Requires Larger Wire

To legally feed a 100A subpanel, using aluminum conductors, you need to use a size that has an ampacity of at least 100A at its temperature rating. This will usually mean using #1/0 Aluminum.

Quadruplex Cable

Quadruplex cable, as you mentioned, is typically used for service drops (from the utility pole to your house) or underground service entrance conductors (USE). It's less common to use it inside a building for a subpanel feeder.

Your Specific Questions


"Can’t find 1 nor 1/0 quadruplex around me..."
You likely won't find quadruplex for an indoor subpanel feeder. Quadruplex is generally used outdoors. You want to use individual conductors (like THHN/THWN) run in conduit, or cable assemblies like SE (Service Entrance) cable (if allowed by local code).2. "...nor can I find a 90A breaker! Will 100 be ok?"

No, you cannot use a 100A breaker to protect #2 aluminum for a subpanel feeder. The overcurrent protection device (breaker) must protect the wire. You cannot put a 100A breaker on wire rated for 90A, unless the breaker is a listed and marked assembly with that wire. If you are having trouble finding a 90A breaker, there are solutions:

Use a 100A rated wire

The easiest and safest solution is to just use the correct wire size. Use #1/0 Aluminum (rated for 100A or more at the appropriate temperature rating) and a 100A breaker.


Use a 90A overcurrent protective device

Consider installing a 90A breaker instead of a 100A breaker, if available.

In summary #2 AL is commonly used for 100A services because of the exception. You would have to do a service calculation, using methods in Article 220, to show that the service could be run with 90 amp rated conductors.Disclaimer: I am an AI Chatbot and not a qualified electrician. For your safety, always consult with a licensed electrician for any electrical work. Electrical work is dangerous and should only be performed by qualified individuals. Local codes may also vary, so it is important to consult with your local electrical inspector. Flag for review

Previous Question Next Question