Question: Trying to get information about voltage drop for a 205 ft SER feeder run..My feeder consist of three 4/0 cables and one 2/0.. it is to be ran 205 ft from the inside main lug panel to the outside 200 amp meter base.. to the best of my knowledge the cable is only rated for 180 amps .. my question is does my wire need to be upsized to carry the voltage drop from such a far distance.. the cable is XHHW rated for 600volts and is in the 90° temp column
Okay, let's break down the voltage drop calculation and the ampacity of your SER cable. This is important for safety and code compliance.1. Ampacity (Current Carrying Capacity)
You are correct
SER cable (even with XHHW insulation) has ampacity limitations compared to individual conductors in conduit. Your 4/0 Aluminum SER cable (assuming aluminum since you mention a 2/0 neutral) is likely rated for
180 amps, as per NEC Table 310.15(B)(16), specifically the 75°C column, which is typically required for termination limitations. Consequence
This means your 200-amp service is already undersized based on the ampacity of the cable. This must be addressed. You cannot supply a 200 amp load through a cable rated for 180 amps. This is a major safety concern.
2. Voltage Drop Calculation (Assuming the Undersized Cable is corrected)
We need to calculate the voltage drop to determine if upsizing is needed after correcting the ampacity issue. Here's the approach. To do this precisely, we need more information:
Material
Are the 4/0 and 2/0 conductors
Aluminum or Copper? (I'll assume aluminum in my example calculations, since you mentioned a 2/0 neutral) Load (Amps)
What is the actual expected continuous load (in amps) you anticipate on this service? Don't just use the 200 amp breaker size. A common general formula to calculate the expected load is to use 80% of the max breaker size which would be 160 ampsHere's the general formula for voltage drop (using the simplified single-phase formula, which is applicable to one leg of your 240V service):
VD = (2 K I D) / CM VD = Voltage Drop (in volts) K = AC Resistance factor. For Aluminum, use 17. For Copper, use 12.
9. (NEC Chapter 9, Table 8 is most accurate). I = Current (Amps) (Your actual expected load, as described above). I will assume 160 amps for this example D = Distance (One-way distance in feet) = 205 ft CM = Circular Mils (Area of the conductor). For 4/0 Aluminum, CM = 211,600.
Calculation (Example using 160 amps & Aluminum)
VD = (2 17 160 205) / 211,600VD = (1118720) / 211,600VD = 5.28 Volts
Percentage Voltage Drop
Voltage Drop Percentage = (Voltage Drop / Source Voltage) 100 Voltage Drop Percentage = (5.28 / 120) 100 = 4.4%
NEC Guidelines
The NEC (National Electrical Code) recommends limiting voltage drop to
3% for feeders and a total of 5% for feeders plus branch circuits. This is a recommendation, not a hard rule, but it's good practice.
Analysis and Recommendations
Ampacity Violation - Critical
Your current 4/0 SER cable is NOT rated for a 200-amp service. This must be corrected immediately. You cannot simply rely on the breaker to protect the wire in this scenario.2.
Voltage Drop (Assuming Correct Ampacity)
In my example calculation with 160 amps, your voltage drop is 4.4%, which exceeds the recommended 3% limit. If your actual load is lower than 160 amps, the voltage drop will be lower.3.
Upsizing is Necessary (Most Likely)
To address BOTH the ampacity and the voltage drop, you will likely need to upsize the conductors.
Possible Solutions (You Need to Choose One)
Option 1: Individual Conductors in Conduit This is often the best approach. Run individual THHN/THWN conductors in conduit. Use 3/0 Copper or 4/0 Aluminum. 3/0 Copper in conduit gives you 200 amps at the 75°C rating. 4/0 Aluminum in conduit gives you 200 amps at the 75°C rating. Calculate voltage drop using the exact load and conductor type (Cu or Al) to ensure it's within acceptable limits. Upsize if necessary. You can use online voltage drop calculators for this. Option 2: Larger SER Cable (If Available)
Find a larger SER cable rated for 200 amps or more. This may be difficult to find and will likely be very expensive. Also, consider the bending radius and termination space requirements of larger SER cable. Again, calculate voltage drop after confirming the cable meets the ampacity requirement.
Option 3: Reduce the Breaker Size If the expected load is truly under 180 amps you may be able to reduce the breaker to 175 amps. However, reducing the breaker size alone does NOT address the voltage drop concern.
Important Considerations
Local Codes
Always consult your local electrical codes and the electrical inspector for specific requirements in your area. They have the final say.
Load Calculation
Perform an accurate load calculation to determine the actual demand you expect on this service. Don't just assume the breaker size is the load.
Termination Temperature
Ensure your equipment (breakers, panels, meter base) is rated for the temperature rating of the conductors you select (usually 75°C).
Neutral Sizing
Double-check that the neutral conductor (2/0 in your case) is appropriately sized based on the expected unbalanced load and any potential for harmonics.
Professional Help
If you are not comfortable with electrical calculations and installations, hire a qualified electrician. Electricity is dangerous, and improper installations can be hazardous.
In summary, your primary concern is the insufficient ampacity of your existing SER cable. Address this first* and then recalculate the voltage drop with the correct cable size and actual load to determine if further upsizing is required. Flag for review