Topic: Maximum distance you are allowed to run a feeder cable

User: sick boy 73, Location: North Carolina

Asked on: Thursday, October 17, 2024 at 4:55 pm EDT
Answered on: Thursday, March 6, 2025 at 4:04 am EST

Question: Is there a maximum distance that you can run a feeder cable .. the run will consist of a 4/0 SER cable running from a 200 amp meter base to a 200 amp sub panel inside.. from termination point at meter base to termination point at main lug panel is approximately 205 ft.. the wire size is for all and it is xhhw style rated at 600 volts maximum but the actual voltage I'm using is 240v

Yes, there is a maximum distance you can run a feeder cable, and it's determined by voltage drop. While your 4/0 SER XHHW cable is perfectly capable of carrying 200 amps at 240 volts, you need to calculate the voltage drop to ensure you're within acceptable limits.Here's why and how: Why Voltage Drop Matters

Voltage drop is the loss of voltage along the length of a conductor. Excessive voltage drop can cause appliances and equipment to malfunction, overheat, or operate inefficiently. It can also reduce the lifespan of electrical components.


Acceptable Voltage Drop

The National Electrical Code (NEC) recommends a maximum voltage drop of 3% for feeders and 5% overall (feeder + branch circuit). For a 240V system, 3% is 7.2 volts (240V 0.03 = 7.2V).

Calculating Voltage Drop

You'll need to use a voltage drop calculator or formula to determine if your 205-foot run is acceptable. Here's the simplified formula: Voltage Drop (VD) = (2 K I D) / CM VD = Voltage Drop (in volts) K = Resistance Factor of the conductor material (Copper: 12.9, Aluminum: 21.2) Since you said it's an SER Cable I will assume it's Aluminum

I = Current (Amps) - In your case, you're feeding a 200 amp panel, so use 200 amps, but consider the actual load. If you know the actual expected load will be lower, using that value will give you a more accurate voltage drop calculation.
It's best practice to calculate this on the actual load
D = Distance (One-way length of the conductor in feet) - In your case, 205 feet. CM = Circular Mils (A measure of the conductor's cross-sectional area). For 4/0 Aluminum conductor = 211,600 CM (Check the specifications for your specific cable. This is a standard value) Calculation for your scenario (Using Aluminum 4/0 SER and 200A)

VD = (2 21.2 200 205) / 211,600 VD = 16.42 volts

Analysis

A voltage drop of 16.42 volts on a 240-volt system is about 6.8%. This exceeds the recommended 3% voltage drop for feeders.

Therefore, based on a 200 amp load, 4/0 Aluminum SER cable for a 205-foot run would likely NOT be acceptable.
How to Fix It


Increase Wire Size

The most common solution is to increase the wire size. Larger conductors have lower resistance and thus lower voltage drop. You can use an online calculator like the one linked below to determine the proper wire size.2.

Reduce the Load

If possible, try to reduce the actual load on the subpanel. However, this isn't always feasible.3.

Move the Subpanel

If you can move the subpanel closer to the meter base, that would significantly reduce the distance and voltage drop. However, this is often not practical.

Important Considerations



Code Compliance

Always consult your local electrical codes and regulations, as they may have specific requirements or restrictions on voltage drop.

Future Loads

Consider future load additions when calculating voltage drop. It's better to err on the side of caution and use a larger wire size than necessary.


Professional Advice

It's highly recommended that you consult with a qualified electrician for this type of installation. They can perform accurate voltage drop calculations and ensure that your electrical system is safe and code-compliant.

In conclusion, based on the information provided and using a 200 amp load, a 4/0 Aluminum SER cable is likely not sufficient for a 205-foot run due to excessive voltage drop. You'll likely need to upsize the cable to a larger gauge.
Disclaimer: I am an AI Chatbot and not a qualified electrician. This information is for general guidance only and should not be considered a substitute for professional advice. Always consult with a licensed electrician for electrical work.* Flag for review