Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Breaker Amperage

User: dalhovera, Location: Las Vegas

Asked on: Thursday, October 17, 2024 at 5:37 pm EDT
Answered on: Thursday, March 6, 2025 at 4:04 am EST

Question: What is the maximum Amperage of breakers can you have in a panelboard?Example Circuits 1,3,5 have a 3 pole 100 ampCircuits 2,4,6 have the same 3 pole 100 amp breaker. I believe the max is 140 amps total

You're asking about the maximum total amperage of breakers you can have in a panelboard, and the example you provided is a good start. However, there's a critical misunderstanding of how panelboard amperage ratings work.Here's the breakdown

Key Concept: Panelboard Rating vs. Breaker Amperage
Panelboard Rating

This is the
maximum amount of current the panelboard itself is designed to safely handle. It's like the capacity of a bridge – it can only support so much weight. Common residential panelboard ratings are 100A, 125A, 150A, 200A, and sometimes higher. The panelboard rating is clearly marked on the panelboard's label.

Breaker Amperage

This is the amount of current that a specific circuit is protected to handle. It's like the weight limit on a specific truck using the bridge.

The Misconception

You cannot simply add up the amperage ratings of all the breakers in the panel to determine if you're within the panelboard's capacity. It doesn't work that way. You're not limited to a total sum of breaker amperages.

The Reality: Load Calculation is Key


The crucial thing is to perform a load calculation to determine the actual amount of current that the circuits connected to the panelboard are likely to draw at any given time. This calculation is based on the connected loads (lights, appliances, outlets, etc.) and factors in things like: Demand Factors

Not everything runs at its maximum power simultaneously. Demand factors are percentages that reduce the calculated load based on the likelihood of simultaneous operation. For example, not all lighting circuits will be fully loaded at the same time.


Diversity

Different types of loads have different usage patterns.

Continuous vs. Non-Continuous Loads

Continuous loads (run for 3 hours or more) are calculated at 125% of their rating.

The Correct Process


Identify All Loads

List every device, appliance, and lighting fixture connected to the panelboard.2.

Determine Wattage/Amperage

Find the wattage (or amperage) of each item (usually on a nameplate).3.

Apply Demand Factors (If Applicable)

Use the National Electrical Code (NEC) or local codes to determine appropriate demand factors for different types of loads.4.

Calculate Total Demand Load

Sum up the adjusted load values.5.

Compare to Panelboard Rating

Ensure that the
calculated demand load is less than or equal to the panelboard's amperage rating.

Example (Simplified)

Let's say you have a 100A panelboard. You
could theoretically have the following breakers: (2) 3-pole 100A breakers as you mentioned (for a total of 200A in breaker ratings)

BUT


You can ONLY do this if your load calculation shows that the actual maximum current the panelboard will ever need to supply is less than or equal to 100A.

Why This Matters



Safety

Exceeding the panelboard's rating can cause overheating, fire, and equipment damage.


Code Compliance

Electrical codes (like the NEC) require load calculations to ensure safe and proper installations.

Performance

An overloaded panel can cause voltage drops, flickering lights, and appliance malfunctions.

Important Considerations



NEC and Local Codes

Always follow the National Electrical Code (NEC) and any local electrical codes when performing load calculations and installing electrical equipment.

Professional Help

If you're not experienced with electrical work and load calculations, it's
highly recommended to consult a qualified electrician. Incorrect calculations can have serious consequences.

Service Entrance

Don't forget to check the amperage rating of the service entrance conductors feeding the panelboard. The panelboard rating cannot exceed the service entrance conductor's ampacity.

In Summary:


The maximum total amperage of breakers in a panelboard is NOT the determining factor. The crucial aspect is to perform a proper load calculation and ensure that the calculated demand load does not exceed the panelboard's amperage rating.Your original assertion that the max is 140 amps is incorrect. The key is to calculate the load. Flag for review

Previous Question Next Question