Question: I have a 3 phase 45 kva, step down, 480 delta to 240/120 high leg delta with a center tap nuetral, and I'm a little confused with regard to grounding and bonding.Xfmr Primary: 70A 3ph (Cu)3-#4 + #8 EGC.Xfmr Secondary: 150A 3ph (Al)4-2/0 + #2 SSBJGEC: (Cu) #4This is one of many step down xfmrs at a new construction, production facility, with GECs being bonded to the grounding system through building steel.One thing that's throwing me off is the riser diagram is calling for 3ph 4 wire, but the panel schedule is calling for 3ph 3 wire, which, that may be neither here nor there.I have my primary EGC bonded to transformer case, and my secondary SSBJ bonded to the transformer case. Does the GEC bond to the transformer case as well? Or does it have to terminate to x-4? Similar to how you would terminate your GEC to x-0, in a typical step down 480 delta to 208/120 wye xfmr, with a bonding jumper bonded to xfmr case?The buss on the x-4 is sized to only accommodate one lug, which seems to indicate there is no bonding jumper. Is there even a nuetral ground bond required on this type of system, being that it's separately derived? Is that taken care of internally? Is the nuetral even a "grounded conductor" in a center tap high leg delta system? If this were to be a corner grounded high leg delta transformer, what would be different? Am I even in the ballpark?Regardless I appreciate any advice and insight you guys may be able to provide me, and I appreciate you taking the time out your day. I hope this is an appropriate thread for this forum and doesn't veer too far off topic. Thanks again. P.S. I Tried to upload a picture to this post not sure if it made it through though.~muddyboots
Okay, let's break this down. High-leg delta systems are tricky, and it sounds like you're right to be cautious. This is crucial to get right for safety and code compliance.
Understanding the High-Leg Delta High-Leg (or "Wild-Leg")
In a high-leg delta, one phase (the "B" phase, typically, though NEC 110.15 requires it to be the center phase) is center-tapped, creating a neutral point. The voltage from this phase to the neutral is half the phase-to-phase voltage. In your case, that's 120V. The voltage from the other two phases to the neutral is also 120V. However, the voltage from the "high leg" to the neutral is approximately 208V.
Uses
High-leg deltas are often used when you need both 3-phase power for motors and 120V single-phase power for lighting and receptacles, and you want to avoid the complexity and expense of two separate transformers.
Potential Problems
The high leg's unusual voltage requires careful marking and awareness to prevent accidental misconnection. Also, phase balancing is often poor.
Your Specific Situation1. Riser Diagram vs. Panel Schedule
The discrepancy between the riser diagram (4-wire) and the panel schedule (3-wire) is important. You should have a neutral conductor (the center tap) for a high-leg delta system, making it a 4-wire system. If the panel schedule is wrong, correct it. If there's a good reason for it, you need to understand it. The panel may be labeled to provide a 3 wire service to equipment that doesn't require a neutral (Delta service).2.
Grounding and Bonding (NEC Article 250 is your friend here!) Separately Derived System
Your transformer is considered a separately derived system (SDS) because it creates a new voltage system independent of the utility service.
Grounded Conductor (Neutral)
In a high-leg delta, the center-tapped point is the grounded conductor (neutral). This neutral must be bonded to ground.
System Bonding Jumper (SBJ)
This is the key to correctly grounding your transformer.
The system bonding jumper (SSBJ in your case, sized per 250.28(D)) is what connects the transformer's grounded conductor (X4 – the neutral) to the transformer case (or other suitable ground electrode conductor connection point). This bond is what establishes the electrical system's connection to earth. Grounding Electrode Conductor (GEC)
The GEC (your #4 Cu) connects the transformer case (or the neutral bus, if that's where your SBJ terminates) to a grounding electrode system. Since you're in a new construction facility, bonding to the building steel is a common and acceptable grounding electrode (NEC 250.52).
Equipment Grounding Conductors (EGCs)
These are the #8 Cu in your primary side and the EGC included with your 2/0 Al conductors on the secondary. The EGCs provide a low-impedance fault current path back to the source (the transformer) to facilitate the operation of overcurrent protective devices (circuit breakers or fuses).3.
Correct Connections (Important!) Primary Side
The primary EGC must connect to the transformer case.
Secondary Side
System Bonding Jumper (SSBJ - #2 Cu)
This must connect between the grounded conductor (X4/Neutral) and the transformer case. If the bus on X4 only has one lug, you'll likely need to replace it with a lug that can accommodate both the SBJ and the GEC.
Grounding Electrode Conductor (GEC - #4 Cu)
This connects to the transformer case (or, if necessary, to the X4 bus along with the SBJ).4.
Neutral-Ground Bond Requirement
Yes, a neutral-ground bond is absolutely required at this transformer (the location of the SDS). This is accomplished via the System Bonding Jumper (SBJ). It is not handled internally by the transformer. This bond is what makes the neutral a "grounded conductor."5. Corner-Grounded Delta
In a corner-grounded delta, one of the phase conductors (e.g., A, B, or C) is intentionally grounded. This is a very different system. The key differences are: No neutral conductor exists. The system bonding jumper would connect the grounded phase conductor to the transformer case and the grounding electrode system. All line-to-ground voltages would be equal.
In Summary1. Clarify the Riser Diagram/Panel Schedule discrepancy. Make sure the documentation accurately reflects the 4-wire high-leg delta system.2. Install the System Bonding Jumper (SBJ) between X4 (Neutral) and the transformer case.3. Connect the Grounding Electrode Conductor (GEC) to the transformer case (or to the X4 bus, along with the SBJ).4. Verify that all equipment grounding conductors (EGCs) are properly connected.5. Ensure proper labeling
Clearly mark the high leg (B phase) with orange tape or other approved means (NEC 110.15 and 230.56). This is critical to prevent accidental connection of 120V equipment to the 208V high leg.
Important Considerations Local Codes
Always check with your local electrical inspector for any specific requirements or interpretations of the NEC.
Qualified Electrician
This type of work must be performed by a qualified and licensed electrician. Grounding and bonding are critical safety aspects of electrical systems.
Transformer Instructions: Consult the transformer manufacturer's instructions for specific grounding and bonding recommendations.By following these guidelines and consulting the relevant NEC articles (especially Article 250), you should be able to properly ground and bond your high-leg delta transformer and ensure a safe and code-compliant installation. Good luck! Flag for review