Topic: Overhead Feeder Aerial Cable Without Equipment Ground

User: 3oFElectric, Location: Tennessee

Asked on: Thursday, October 17, 2024 at 10:16 pm EDT
Answered on: Thursday, March 6, 2025 at 4:05 am EST

Question: A client wants me to run a feeder to a 2nd shed from a subpanel in an adjacent outdoor shed. The adjacent shed is being fed from the service panel, and is coming off the house from an aerial cable over to the shed's subpanel. When I opened the panel to check spacing, I found no EGC.Looking at the aerial cable, I only see 3 wires - two hots and a neutral. No EGC. Is this allowed? To have NO EGC for a feeder running from the service panel to an outdoor shed?If I pull a feeder from the 1st shed subpanel to power the 2nd shed, how will there be any ground fault path back to the utility service without an EGC from the service panel to the 1st shed subpanel?Attached are pictures of the current setup.

Okay, this is a common but potentially dangerous situation. Let's break down the issues and the code implications

Is it allowed to have NO EGC for a feeder running from the service panel to an outdoor shed?
NO. Generally speaking, no, it is not allowed to run a feeder to a detached building without an equipment grounding conductor (EGC). The National Electrical Code (NEC) mandates an EGC for feeders to detached buildings. Exceptions

There might be an extremely limited and unlikely exception if the feeder is supplying only a single circuit (e.g., a single 120V lighting circuit) and meets very specific requirements. However, based on your description of a subpanel in the first shed, that exception is extremely unlikely to apply.

Why is an EGC so important?
Fault Current Path

The EGC provides a low-impedance path for fault current to return to the source (the service panel). This is critical for rapidly tripping the overcurrent protection device (circuit breaker or fuse) in the event of a ground fault (e.g., a hot wire contacting a metal enclosure). Without a low-impedance EGC, the fault current might be insufficient to trip the breaker, leaving the enclosure energized at a dangerous voltage. This presents a severe shock hazard.


Voltage Stabilization

The EGC also helps stabilize the voltage on non-current-carrying metal parts, reducing the risk of nuisance tripping and improving overall system reliability.

Analysis of Your Situation


Based on your description and the pictures:1. Missing EGC

You've correctly identified a critical safety issue. The absence of an EGC between the service panel and the first shed's subpanel is a code violation and a shock hazard.2.

Three-Wire Aerial

The fact that the aerial cable only has two hots and a neutral is a major red flag. While it might have been installed under older codes in some jurisdictions, it's almost certainly not compliant with current NEC requirements. Older methods might have relied on grounding at the remote structure, which is generally not allowed anymore due to potential differences in ground potential.3.

Risk to Second Shed

Running a feeder from the first shed's subpanel to the second shed without addressing the lack of an EGC in the first feeder compounds the problem. You would be extending a dangerous situation to the second shed, creating a potentially lethal hazard.

What to Do IMMEDIATELY
1. Do not proceed with any further wiring until the first shed feeder is corrected. Adding to a faulty system only makes things worse.2. De-energize the subpanel in the first shed if possible. This will minimize the risk of someone coming into contact with an energized enclosure in the event of a ground fault.3. Consult a qualified electrician immediately. This is not a DIY situation. A licensed electrician can properly assess the existing installation, determine the correct method for adding an EGC, and perform the necessary work safely and in compliance with the NEC.4. Consider replacing the aerial cable. The most reliable and compliant solution is usually to replace the existing three-wire aerial cable with a four-wire cable (two hots, neutral, and EGC). Depending on the distance and load requirements, this might require upgrading the cable size.

How to Correct the Situation (Likely Scenarios)

Here are some potential solutions, but only a qualified electrician can determine the correct approach for your specific situation: Replace the Aerial Cable

This is the preferred and generally safest solution. Replace the three-wire cable with a four-wire cable that includes an EGC. The EGC must be sized according to the NEC based on the overcurrent protection device protecting the feeder.


Install a Grounding Electrode System at the Shed (Not Recommended as a Primary Solution)

While a grounding electrode system (ground rod) is required at the detached building in addition to the EGC, it is not a substitute for a proper EGC. Ground rods are designed to dissipate fault current during lightning events and stabilize voltage but are generally insufficient to carry the fault current needed to trip a breaker quickly in a ground fault situation. In other words, the ground rod is there for the purposes of properly grounding the shed, but it does not serve as the EGC for a feeder.

Combined Neutral and Ground (Not Allowed)

Under no circumstances should you combine the neutral and ground conductors at the subpanel in the first shed. This is a dangerous practice that creates a path for neutral current to flow on the grounding conductors, leading to energized enclosures and potential shock hazards. Doing so violates NEC 250.32(B).

Wiring the Second Shed (After Correcting the First)


Once the EGC issue with the feeder to the first shed is resolved, you can proceed with the feeder to the second shed. Here's how:1. Four-Wire Feeder

Run a four-wire feeder (two hots, neutral, and EGC) from the first shed's subpanel to the second shed.2.

Separate Neutral and Ground

In the second shed's subpanel,
do not bond the neutral conductor to the enclosure or the grounding electrode system. Keep the neutral and ground conductors completely separate.3.

Grounding Electrode System

Install a grounding electrode system (e.g., ground rod) at the second shed and connect it to the grounding busbar in the subpanel.

Important NEC References
NEC 250.32 Detached Buildings or Structures NEC 250.4(A)(5) Effective Ground-Fault Current Path NEC 310.16 Ampacities of Conductors (for sizing conductors and EGCs)In summary, the situation you've described is a serious safety concern and a code violation. Contact a qualified electrician immediately to correct the missing EGC before proceeding with any further work. Don't compromise on safety; electrical work is not something to cut corners on. Flag for review