Question: I am working on adding office space to a manufacturing plant. I need a transformer to supply this space. 480V-208/120V. My secondary load is a 125A main lug 24 space panel feeding (18) duplex receptacles and (16) 110V LED fixtures. There will also be (4) 20A ptac units.Choosing a transformer, I assumed 200A secondary.sqrt(3) * 200A * 208V = 72 KVA --> 75KVA transformerShould I need this big of a transformer? What does the NEC state about load currents in this environment? Also, calculations in 120V vs 208V?
Okay, let's break down the transformer sizing calculation based on the National Electrical Code (NEC) and the information you've provided. You are on the right track, but we need to do a more detailed load calculation to avoid oversizing the transformer unnecessarily.
Here's a step-by-step approach, incorporating NEC guidance
1. Calculate the General Lighting & Receptacle Load (Article 220.14(H))
Receptacles
NEC 220.14(I) states that for other than dwelling units, each receptacle outlet shall be calculated at not less than 180 VA. However, in a commercial setting, demand factors for receptacles are often permitted. We'll calculate it both ways to see the difference and use the more conservative approach.
Method 1: 180VA per Receptacle (No Demand Factor) 18 receptacles 180 VA/receptacle = 3240 VA Method 2: Apply Demand Factor (NEC 220.44) Demand factors depend on the type of occupancy. Since this is office space connected to a manufacturing plant, we might be able to apply a demand factor. Let's conservatively assume we can use a 50% demand factor for general-use receptacles beyond the first 10 kVA (NEC 220.44) First 10 kVA: 10,000 VA (full load) Remaining Load: 3240 - 10,000 VA = -6760 Since the original load is less than 10,000VA no demand factor can be applied. 18 receptacles 180 VA/receptacle = 3240 VA Lighting (LED Fixtures)
You have 16 LED fixtures. We need to know the wattage per fixture. Let's assume each fixture is 50W. (You MUST verify the actual wattage on the fixture or its documentation). 16 fixtures 50 W/fixture = 800 VA
Total General Lighting & Receptacle Load
3240 VA (receptacles) + 800 VA (lighting) = 4040 VA
2. Calculate the PTAC Load
You have 4 PTAC units, each on a 20A, 120V circuit. We'll assume they are running at full load (important: check the nameplate data on the PTAC units for actual power consumption). VA per PTAC = 20A 120V = 2400 VA Total PTAC Load = 4 PTACs 2400 VA/PTAC = 9600 VA
NEC 440.35 - Where the air-conditioning equipment is the largest load connected to a panel board or other equipment, the total calculated load shall not exceed the rating of the service. NEC 440.34 - A disconnect supplying a fixed motor-compressor air conditioning equipment shall have an ampere rating not less than 115% of the nameplate rated-load current or branch circuit selection current, whichever is greater. In a commercial environment, it is likely that a larger load would not be allowed to exist on a transformer that only supplies the single unit, therefore, we should use 125% to determine the actual KVA of the compressor. VA per PTAC w/ 125% Load: 2400VA 1.25 = 3000 VA Total PTAC load: 4 3000 = 12,000 VA3. Total Connected Load
Total Load = 4040 VA (lighting & receptacles) + 12,000 VA (PTACs) = 16,040 VA
4. Apply Demand Factors (Carefully!)
Demand factors can be applied, but only if you can justify them based on the actual usage patterns of the office.
Lighting
It's unlikely you can apply a large demand factor to the lighting. People need light to work. Let's assume a demand factor of 90% (allowing for some fixtures being off occasionally): 800 VA 0.9 = 720 VA. This only reduces the total a small amount so we should use 100%
Receptacles
As discussed earlier, NEC 220.44 might allow a demand factor. Only apply a demand factor if you have historical data or a solid understanding of the actual load profile. If in doubt, use 100%.
PTACs
It's difficult to justify a demand factor on PTACs, especially if comfort is critical. People will adjust them as needed. Assume 100% (NEC 440.35 supports the assumption).
Demand Factors (Assuming Conservative)
Lighting: 100% Receptacles: 100% PTACs: 100%
Adjusted Total Load (Using Conservative Demand Factors)
4040VA + 12,000VA = 16,040VA
5. Calculate the Required Transformer KVA
Total Load = 16,040 VA Transformer KVA = Total Load / 1000 = 16.04 kVA
6. Apply NEC 450.3 (Transformer Overcurrent Protection)
NEC 450.3 dictates the maximum overcurrent protection allowed for the transformer primary and secondary. This can influence your choice if the calculated full-load amps of the transformer fall close to standard breaker sizes. You must consider both primary and secondary overcurrent protection.
7. Choose the Transformer
Based on the 16.04 kVA calculated load, a
25 kVA transformer would be a reasonable choice. It provides some headroom for future expansion and handles the calculated load comfortably.
Important Considerations
Future Expansion
Always consider future needs. If you anticipate adding more loads in the next few years, it's better to upsize the transformer now to avoid costly replacements later.
Motor Starting
If you have any significant motor loads (even small ones connected to receptacles), they can create inrush currents that can momentarily overload the transformer.
Power Quality
Harmonics from electronic loads (LEDs, computers, etc.) can affect transformer performance. If you have a high concentration of such loads, consider a K-rated transformer.
Efficiency
Choose an energy-efficient transformer to minimize operating costs.
Local Codes and Regulations
Always check with your local electrical inspector for any specific requirements.
Why 75 kVA is Likely Overkill (Given the Information)
Your initial assumption of a 200A secondary and a 75 kVA transformer was likely based on the capacity of the 125A panel. However, the connected load is significantly less than the panel's rating. You are essentially using a panel that is larger than the load that is placed on it.
120V vs. 208V Calculations
120V
Used for lighting, receptacles, and small appliances.
208V
Line-to-line voltage (used for PTAC Units and other 208V equipment)The transformer provides both. The calculations need to consider the voltage at which the load is operating to determine the current draw.
In Summary
1. Carefully calculate your connected load, including lighting, receptacles, and PTACs.2. Justify any demand factors you apply based on actual usage.3. Select a transformer that provides sufficient capacity for the connected load, considering future expansion and motor starting.
4. Ensure the transformer's overcurrent protection meets NEC requirements.5. Check with your local electrical inspector.By following these steps, you can select the appropriate transformer size for your office space addition and ensure a safe and reliable electrical system. Using a 25KVA transformer, instead of 75KVA transformer will provide better performance of the transformer, save money by being a smaller size.
Disclaimer: Consult with a qualified electrical engineer for specific design and installation recommendations. This information is for educational purposes only. Always adhere to the NEC and local codes. Flag for review