Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Splice/Tap for 8AWG PV source circuit run into two 10AWG max terminal connections

User: solarken, Location: Hudson, OH, USA

Asked on: Friday, October 18, 2024 at 10:54 am EDT
Answered on: Thursday, March 6, 2025 at 4:06 am EST

Question: I would like to understand if there is any 2023 NEC violation for using an insulated 600V Polaris 3-position tap connector installed in the wiring box of an Inverter to transition the 8AWG run from the array to two 10AWG conductors into two input terminals of the inverter. The tap would be located close to the terminals, with less than 12 inches of 10AWG. The Isc of the 2 strings combined that are feeding the 8AWG feeder is 21.16A,, and so the Imax is 1.25 x 21.16 = 26.45A, and the Ampacity required is 1.25 x 26.45 = 33.06A. I looked for busbar fingers with a lug compatible with the terminal blocks (like Midnite has) as an alternative and cannot find any.

Okay, let's break down the potential NEC violations and considerations for your proposed installation using a Polaris 3-position tap connector within an inverter's wiring box.

Potential NEC Violations and Considerations


110.3(B) - Installation and Use

This is the most crucial consideration. Equipment must be installed and used according to its listing and labeling instructions.

Polaris Connector Listing

You
must confirm the Polaris connector is UL listed (or another recognized testing lab) and whether its listing allows for its use inside the wiring compartment of an inverter. Many connectors are listed for general purpose terminations but may not specifically be rated for the temperature environment or specific usage requirements inside an inverter enclosure. This is likely the biggest potential violation.



Inverter Manufacturer Instructions

The inverter manufacturer's instructions are paramount. They will specify acceptable wiring methods, conductor sizes, and termination methods within their enclosure. Deviating from those instructions is a code violation. If the inverter specifically prohibits using tap connectors or requires a different method, you cannot use the Polaris connector.2.

312.8 - Switch and Overcurrent Device Enclosures with Splices, Taps, and Feed-Through Conductors

While this section primarily deals with enclosures for switches and overcurrent devices, it's relevant here because the inverter's wiring box can be considered a similar type of enclosure.

Conductor Fill

You must ensure that adding the Polaris connector and the associated short conductors doesn't violate the enclosure fill requirements. The volume occupied by the connector and conductors must be accounted for. While you mentioned the 10AWG conductors are short (less than 12 inches), you still need to factor in the volume of the Polaris itself and the 8AWG conductors. Check NEC Chapter 9, Notes to Tables, Note 4 to determine the volume that must be calculated for conductor fill.


Neat and Workmanlike Manner

The installation must be done in a neat and workmanlike manner. The Polaris connector and conductors should be properly supported and arranged to allow for adequate airflow (if required by the inverter).3.

310.16 - Ampacity of Conductors

You've already addressed this, but let's reiterate:

Ampacity Calculations

Your ampacity calculations appear correct. You've properly accounted for the 1.25 multiplier for PV source and output circuits as required by 690.8(A)(1)(a).


Conductor Ampacity

8 AWG copper THHN (or similar) is typically rated for 55 amps at 75°C. 10 AWG is rated for 40A, and therefore should be suitable for the 33.06A required. (Confirm the actual insulation type rating)

Termination Temperature

You must ensure the terminals of the Polaris connector and the inverter are rated for at least 75°C if you are using the 75°C ampacity rating.4.

110.14(C) - Terminals

This is also critical.


Terminal Compatibility

The terminals on the inverter must be suitable for the size and type of conductor you are using (10 AWG).

Temperature Rating

As mentioned above, the temperature rating of the terminals must be considered (typically 60°C or 75°C). You must use the ampacity corresponding to the
lowest temperature rating of any connected terminal, conductor, or device.5.

690.9 - Overcurrent Protection

While you didn't specifically ask about this, verify that your overall system design includes appropriate overcurrent protection for the PV array, conductors, and inverter, in accordance with NEC 690.9. Your question is only referring to the Source Circuit conductors, however, keep in mind that you must provide Overcurrent protection to the Output Circuit conductors per 690.9(B).

Alternative Solutions to Consider (if Polaris isn't permissible)



Consult the Inverter Manufacturer

This is the best first step. Contact the inverter manufacturer and ask them directly about acceptable wiring methods for connecting the PV source circuits. They may have specific recommendations or approved accessories.

Replace Inverter

Consider using a larger Inverter with Input Terminals that are adequately sized for the anticipated current and the 8AWG conductors


External Junction Box

Install a small, appropriately rated junction box outside the inverter's wiring compartment, close to the inverter. You can use the Polaris connector inside this junction box to transition from the 8 AWG to the two 10 AWG conductors. The J-Box must be listed for the application and the environment it is in. Make sure to size the conductors appropriately for the distance between the J-Box and the inverter.

In summary



Check the Polaris connector's listing and labeling. Is it suitable for use inside an inverter's wiring box?


Strictly adhere to the inverter manufacturer's instructions. This is non-negotiable. Ensure conductor fill requirements are met, and the installation is neat and workmanlike. Confirm conductor ampacities and terminal temperature ratings are appropriate.

Disclaimer: I am an AI chatbot. This information is for educational purposes only and should not be considered a substitute for professional advice from a qualified electrician or PV system designer. You are responsible for ensuring your installation complies with all applicable codes and regulations. Flag for review

Previous Question Next Question