Topic: Ideas for outdoor con box or other ideas

User: fastline, Location: midwest usa

Asked on: Friday, October 18, 2024 at 1:06 pm EDT
Answered on: Thursday, March 6, 2025 at 4:06 am EST

Question: I am having to work a design that is turning into a cluster F... Basically 150ft from a building, I need to serve up 120V to a powered gate, a 2 conductor low energy switching circuit to activate gate, 2 CAT6 cables for each card reader at gate, then at least 2 CAT6s for 2 cameras out there. What I am trying to do is clean up how all this enters the building, rather than a line of LBs... Looks like crap, but.....I am also torn on that 2 conductor going to gate opener. Really would like to ride it in the pipe with the power, but I know it should not be in there.More to the point, due to distance and complexity, I was thinking of setting a con box or similar at about the 100ft mark because I have to come out of the ground there anyway. My thought was to do pull loops in there so if something gets damaged out there, there is an easier way to repair rather than a complete home run. I was looking at communications type pedestals. Never have really used them though. Not even sure this is the right strategy.

Okay, let's break down this cluster situation and strategize a cleaner, more maintainable solution. You're right, a row of LB fittings coming out of the building isn't ideal. Your idea of an intermediate access/pull point is a good one, and communication pedestals or similar enclosures are worth considering.

Here's a structured approach



1. Conduit Strategy



Separate Conduits

You absolutely
must separate the 120V power from the low-voltage control circuit (gate activation). This is not just a best practice, it's a code requirement in most jurisdictions. Mixing power and low-voltage signaling creates a safety hazard and can induce noise into the low-voltage circuit, causing malfunctions.

Conduit Count

Based on your requirements, I recommend planning for at least three conduits to run from the building to your intermediate box (and then from the box to the gate):

Conduit 1

120V Power for the gate. Size appropriately for the conductors required by your gate motor/power supply.


Conduit 2

All the low-voltage data cables: (2) CAT6 for each card reader (total 4), (2) CAT6 for the cameras. That's 6 total CAT6 cables.

Conduit 3

Low-voltage control (2-conductor gate activation).

2. Intermediate Access/Pull Box (100ft Mark)



Purpose

This is your key to simplifying the run and providing future serviceability.

Enclosure Type

A communication pedestal
could work, but let's consider alternatives:

NEMA 3R/4X Enclosure (Weatherproof)

A robust, weatherproof junction box or enclosure designed for outdoor use. These come in various sizes and materials (steel, stainless steel, fiberglass, plastic). This may be your best bet for flexibility. You can mount things inside, splice cables, and easily access everything.

Handhole/Pull Box

A buried handhole (typically concrete or plastic) can also be used. These are typically used for direct burial applications and often have a removable cover flush with the ground. Less visible, but access can be more difficult.


Communication Pedestal

These are often designed with specific features for communication cables (grounding bars, cable management). They may be overkill and potentially more expensive, but worth considering if you like the layout and features they offer.

Sizing the Box

This is critical. You need enough space to:
Accommodate the conduit entries and connectors. Provide adequate working space for pulling and managing the cables. Leave enough extra cable for pull loops (more on that below). Consider future expansion.

Features to Look For



Weatherproof/Waterproof

Essential for outdoor use. NEMA 3R or 4X is common.


Lockable

To prevent unauthorized access.

Grounding

A solid grounding lug inside the box is crucial.


Cable Management

Look for features to help organize and secure the cables (e.g., cable ties, strain relief, mounting brackets).

3. Cable Considerations



Direct Burial vs. Conduit

Since you're underground, you'll
likely need to use direct burial-rated cable, even if it's inside conduit. This provides an extra layer of protection against moisture and damage. Check your local codes for specifics.

CAT6

Use outdoor-rated CAT6 cable (or CAT6a) designed for burial or conduit use. This cable has a more robust jacket to withstand moisture and UV exposure.

Power Cable

Use appropriately sized THWN/THHN conductors (or direct burial-rated cable like UF) inside the conduit, sized for the gate motor's power requirements.


Low-Voltage Control Wire

Use appropriately rated direct burial or conduit-rated low-voltage wire for the gate activation signal.

4. Pull Loops and Serviceability



Pull Loops in the Intermediate Box

This is a great idea. Leave several feet (at least 5-10 feet) of extra cable coiled neatly inside the intermediate box for each cable run.


Benefits of Pull Loops



Repair

If a cable gets damaged between the building and the box, you can pull the damaged section out, splice in a new section, and use the extra cable to make the connection. You avoid having to re-pull the entire length of the cable.


Relocation

If the gate or camera positions need to be adjusted slightly, you have some slack to work with.

Testing

Easier to test cables from an accessible location.


Coiling Technique

Coil the cable neatly and secure it with cable ties. Don't make the coils too tight, as this can damage the cable.

5. Grounding



Ground the Conduit

Ground the conduit at both the building entry point and the intermediate box, using appropriate grounding bushings and conductors.


Ground the Enclosure

Connect the grounding lug inside the intermediate box to the grounding system.

Ground the Equipment

Make sure all equipment (gate operator, card readers, cameras) are properly grounded according to their manufacturer's instructions.

6. Bringing Cables into the Building



Single Point of Entry

Instead of multiple LB fittings, consider a larger LB fitting or a small pull box just inside the building where the conduits enter. This allows you to organize the cables before they run to their final destinations inside the building.

Cable Management Inside

Use cable trays, raceways, or conduit inside the building to keep the cables neat and organized.

7. Code Compliance



Local Codes

Crucially, consult your local electrical codes and building codes before starting any work. Requirements vary by jurisdiction. You might need permits for this type of installation.

NEC (National Electrical Code)

The NEC provides general guidelines for electrical installations. Pay close attention to articles related to:
Underground wiring Conduit installations Grounding Low-voltage wiring

Example Scenario (Using NEMA 3R Enclosure)


Dig a trench
from the building to the gate location.2. Install three separate conduits (120V, data, low-voltage control) in the trench. Consider using schedule 40 or schedule 80 PVC conduit.3. At the 100ft mark, install a NEMA 3R enclosure on a concrete pad or post to keep it above ground. Ensure the enclosure is properly grounded.4. Pull the 120V power cable, data cables (CAT6), and low-voltage control wire through their respective conduits, leaving ample pull loops inside the enclosure.5. Terminate the power cable to a suitable junction block inside the enclosure.6. Connect the data cables to surge protection devices inside the enclosure (optional, but recommended for outdoor data cables).7. Run the conduits from the enclosure to the gate location.8. Terminate the cables at the gate, card readers, and cameras.9. Back at the building, run the conduits into a larger LB or pull box just inside the wall.10. Route the cables to their respective destinations inside the building

power to a breaker panel, data cables to network switches, and low-voltage control wire to the appropriate control circuit.

Addressing Your Specific Concerns



Running low-voltage wire with power



DO NOT DO IT.
It's a code violation and a safety hazard. Use a separate conduit. Intermediate Box

Your instinct about the intermediate box is spot on. It's a key element for simplifying the installation and making future maintenance easier.

Key Takeaways



Separate Power and Low-Voltage

Critical for safety and performance.

Intermediate Access Point

Makes installation and maintenance much easier.


Generous Pull Loops

Save you time and money in the long run.*

Code Compliance:
Essential to ensure safety and avoid problems with inspections.This plan provides a foundation. You'll need to adapt it to your specific site conditions, local codes, and budget. Good luck taming that cluster! Flag for review