Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Full Load Amps for VFD or Motor

User: Stubby78, Location: Oklahoma

Asked on: Friday, October 18, 2024 at 2:05 pm EDT
Answered on: Thursday, March 6, 2025 at 4:06 am EST

Question: Hello all,My company designs custom HVAC units that are designed to be used primarily for data centers. We have various designs of different products but for the most part, these units consist of a few motor pumps that pump water throughout some coils, and some EC fans that pull the air across the coils to chill the water inside the coils. There are several damper actuators and other sensors involved as well but those aren't really in question right now.I am posting this question as this has got our Electrical engineering department divided right now. It is over the topic of how we are calculating the FLA of a custom HVAC unit. My question is, which FLA do we need to use in our load calculations for these units, the FLA of the VFD, or the FLA of the motor itself?Traditionally, I have always calculated the FLA based on the nameplate data from the motor itself. The OCPD upstream of the VFD and the wire gauge is determined by the FLA of the VFD on the line side. However, some of the engineers I work with are stating that the FLA of the VFD is what should be used in the load calculations. The FLA then helps determine the MCA and the MOP of the units which is required by UL.My concern with this is that we could potentially oversize the MCA and MOP and leave our electrical components susceptible to damage.I have been told by a few of our engineers that supposedly this is a new standard to use the FLA of the “conversion device” (the VFD in this case) and not the FLA of the Motor. However, when I question them on this, they can not find the specific standard that states this. In all fairness, I can’t find anywhere that states the other side of the argument either.If there is anything in the NEC, UL508A, UL1995, or 60335 that state the FLA of the VFD’s should be used, please help point me in the right direction so that we can reference one of these standards moving forward.

This is a common point of confusion, and the correct approach depends on the specific situation and what you're calculating. Here's a breakdown to clarify

Understanding the Different FLA Values:
Motor FLA (Nameplate)

This is the
Full Load Amps the motor is designed to draw when operating at its rated horsepower, voltage, and frequency under full load.

VFD Input FLA (Line-Side)

This is the Full Load Amps the VFD draws from the power source. It represents the current the VFD needs to operate itself and supply power to the motor.

VFD Output FLA (Load-Side)

This is the
Full Load Amps the VFD can deliver to the motor. This value is close to the nameplate FLA of the motor.

The General Rule: Motor FLA for Load Calculations, VFD Input FLA for Upstream Protection


In most scenarios, the best practice is to use the motor FLA for calculating the load contributed by that motor to the total connected load of the HVAC unit. The VFD input FLA should be used for sizing upstream overcurrent protection and conductors.

Here's the reasoning behind it



Load Calculation

The purpose of a load calculation is to determine the total current drawn by all the loads within the equipment. The motor itself is the load, not the VFD. Therefore, the motor's FLA is the relevant value.

Branch Circuit Protection and Conductor Sizing

You need to protect the circuit supplying the VFD, and size the conductors appropriately for the current the VFD will draw from the power source. Therefore, the VFD input FLA is used for overcurrent protection.

Code References and Standards

You're right, there isn't one single, explicitly worded statement that solves this debate. However, let's examine the relevant sections of the codes and standards you mentioned:


NEC (National Electrical Code)



Article 430 (Motors, Motor Circuits, and Controllers)

This is the primary article for motor installations. Several sections are relevant:


430.6(A)(1)

Says that for calculating ampacity, the nameplate current rating of a motor is used.

430.22(A)

Conductor ampacity for a single motor must be at least 125% of the motor's full-load current rating (FLA).


430.52

Overcurrent protection for motor branch circuits. While it doesn't specifically address VFDs, it establishes the principles for protecting motor circuits.

Article 440 (Air-Conditioning and Refrigeration Equipment)

This article supplements Article 430 and is
highly relevant to your application. Look specifically at sections related to Motor-Compressor Equipment. Pay close attention to the definitions of Rated-Load Current and Branch-Circuit Selection Current.

NEC 430.122(A)

Overcurrent protection for a VFD would be based on the manufacturer’s instructions and VFD nameplate.

UL 508A (Standard for Industrial Control Panels)

This standard governs the construction of industrial control panels, which is likely how your HVAC units are wired. It emphasizes the need to follow NEC guidelines and manufacturers' instructions. It does not provide FLA calculation procedures in the same way the NEC does.

UL 1995 (Heating and Cooling Equipment)

This standard focuses on the safety requirements for HVAC equipment. It will likely reference the NEC for electrical safety aspects and motor protection.

IEC 60335 (Household and Similar Electrical Appliances - Safety)

This standard is less directly applicable unless your data center HVAC units fall under the definition of "household and similar appliances." It's primarily focused on consumer appliances.

Breaking It Down to Specific Calculations

Here's how to apply the different FLA values:1.

Unit Total Load Calculation (MCA, MOP)

For each motor: Use the motor nameplate FLA. Add the FLA values for all motors and other loads (e.g., damper actuators, controls) to determine the total load current of the unit. Apply the NEC factors for non-continuous and continuous loads (125% for continuous loads). This total load current is used to calculate the Minimum Circuit Ampacity (MCA) and Maximum Overcurrent Protection (MOP).2.

VFD Branch Circuit Overcurrent Protection and Conductor Sizing

Use the VFD's input FLA (line-side). Refer to the VFD manufacturer's documentation for specific overcurrent protection requirements (fuse type, breaker size, etc.). This is crucial. The manufacturer knows the specific characteristics of their drive and how it behaves under fault conditions. Size the conductors supplying the VFD based on the VFD's input FLA and any applicable NEC derating factors.

Addressing Your Concerns



Oversizing and Susceptibility to Damage

Your concern about oversizing the MCA and MOP is valid. Using the VFD input FLA for the overall load calculation could lead to unnecessarily large conductors and overcurrent protection, making the equipment more expensive and potentially less sensitive to smaller overload conditions. The motor FLA more accurately reflects the actual load being placed on the system.

The "Conversion Device" Argument

Your colleagues' argument about using the FLA of the "conversion device" is a misinterpretation. The VFD
controls the motor, but the motor is still the load.

MCA and MOP

To determine the Minimum Circuit Ampacity (MCA) and Maximum Overcurrent Protection (MOP) rating, you'll be following the NEC's requirements based on the motor's FLA and the manufacturer's recommendations for the VFD protection. It's a multi-step process that considers both the motor and the VFD.

Example Scenario


Let's say you have an HVAC unit with: 10 HP motor driving a pump with a motor nameplate FLA of 14 amps. VFD controlling the motor with a VFD Input FLA (line-side) of 20 amps.1. Unit Load Calculation (MCA/MOP)

Use the motor FLA (14 amps) for the load calculation. Add this to the FLA of any other components.2.

VFD Branch Circuit

Use the VFD input FLA (20 amps) to size the conductors and overcurrent protection supplying the VFD itself. Also, verify and follow the VFD manufacturer's documentation.

Key Takeaways and Recommendations



Consult the VFD Manufacturer's Documentation

This is
critical. The VFD manufacturer will specify the correct overcurrent protection and conductor sizing for their specific VFD model. This often takes precedence over general NEC rules because VFDs have unique operating characteristics.

Document Your Calculations

Keep detailed records of all your calculations and the NEC sections/manufacturer's data sheets you used.

Standardize Your Approach

Develop a company-wide standard operating procedure for calculating HVAC unit loads and sizing electrical components. This will prevent future confusion and ensure consistency.


Continue the Discussion

Show your colleagues this breakdown. It's essential to have a clear, agreed-upon approach based on sound engineering principles and code compliance.*

Consider a Professional Review:
If the debate continues and involves complex or unusual installations, consider having a qualified electrical engineer review your designs and calculations.By following these guidelines and consulting the relevant codes and manufacturer's data, you can ensure the safety, reliability, and code compliance of your HVAC units. Flag for review

Previous Question Next Question