Question: I have existing floor mounted transformer and plans show that panelboard is going to be mounted on uni strut on top of it. The panel front would be aligned with transformer front edge.Is there any maximum distance the panel has to be mounted on top of the floor mounted transformer in the NEC 2017?
The NEC doesn't explicitly prohibit mounting a panelboard above a transformer. However, there are several considerations and potential violations you need to address
Key Considerations and Potential NEC Violations (NEC 2017):
1. Working Clearance (110.26)
This is the most likely issue. You must maintain adequate working clearance in front of both the panelboard and the transformer. This is the distance to the nearest grounded object (including the other equipment) or to the front of the enclosure if exposed live parts exist.
Depth of Working Space (110.26(A)(1))
This depends on the voltage to ground and the conditions present (refer to Table 110.26(A)(1)). The panelboard and the transformer will likely be in each other's working space. You must meet the requirements for each independently. The depth is measured from the front of the equipment.
Width of Working Space (110.26(A)(2))
Must be the width of the equipment or 30 inches, whichever is greater. This space needs to be clear and dedicated. The panel can affect working space of the transformer and vice versa.
Height of Working Space (110.26(A)(3))
Must be 6'6" or the height of the equipment, whichever is greater. The height is measured from the working surface.2.
Dedicated Equipment Space (110.26(E))
Space above and below electrical equipment for the dedicated purpose of installing that equipment. Piping and ductwork can't encroach on the dedicated equipment space.3.
Heat Dissipation
Ensure the panelboard doesn't impede the transformer's ability to dissipate heat. Transformers generate heat, and if the panelboard blocks ventilation, it could lead to overheating and premature failure. Check the transformer's documentation for ventilation requirements.4.
Accessibility (110.25)
The panelboard must be readily accessible for maintenance, inspection, and operation. Mounting it high up on a transformer could make it difficult to reach.5.
Panelboard Orientation
A general rule of thumb is that the highest overcurrent protection device (OCPD) shouldn't be higher than 6'7" from the floor or working platform.
So, what is the maximum distance the panel has to be mounted?
There is no single maximum distance specified in the NEC. The maximum height will depend on what satisfies these things: Working Clearances for both the panel and transformer are achieved. The panel is readily accessible. The panel does not interfere with the ventilation of the transformer. The highest OCPD isn't higher than 6'7" from the floor.Recommendations
Consult the Transformer's and Panelboard's Installation Instructions
Follow all manufacturer's recommendations for clearance, ventilation, and mounting.
Consult with the local AHJ (Authority Having Jurisdiction)
Before proceeding, discuss your plans with the electrical inspector. They may have specific requirements or interpretations of the NEC in your area.
Consider Alternatives
If possible, explore alternative locations for the panelboard that don't involve mounting it directly above the transformer. This might simplify compliance with the NEC and improve accessibility.*
Professional Engineer
This configuration is outside of standard practice, you should hire a licensed electrical engineer for a design sign-off.
In summary, while the NEC doesn't explicitly forbid mounting a panelboard on top of a transformer, the combination of working clearance requirements, dedicated equipment space, heat dissipation concerns, and accessibility issues makes it a challenging and potentially non-compliant installation. Careful planning, consultation with the AHJ, and a thorough understanding of the relevant NEC articles are crucial. Flag for review