Topic: Neutral size for 200A feeders to residential shop, detached structure, 3/0 CU ungrounded conductors?

User: Apprenti, Location: Idaho

Asked on: Friday, October 18, 2024 at 3:27 pm EDT
Answered on: Thursday, March 6, 2025 at 4:07 am EST

Question: Neutral size for 200A feeders to residential shop, detached structure, 3/0 CU ungrounded conductors?400A Meter Base -> 3/0 CU ungrounded conductors from MB to 200A disconnect -> 3/0 CU ungrounded conductors from 200A disco to underground to 200A Main Breaker panel in shop.Please and thank you!

Okay, let's break down the neutral sizing requirements for this situation. This is a common scenario for a detached shop or garage.

Understanding the Basics Feeder Conductors

These are the wires running from the service (meter base) to a subpanel in another building.


Neutral Conductor's Role

The neutral conductor carries the unbalanced load back to the source (meter base). Its size is often determined by the anticipated maximum unbalanced load and voltage drop considerations.

Article 220.61
dictates the allowable reduction in size of the neutral conductor in certain situations. Important Note

This advice is for informational purposes only and does not constitute professional electrical engineering or contracting services. Always consult with a licensed electrician or qualified electrical engineer for your specific installation and to ensure compliance with all applicable codes and regulations.

Calculations and Considerations
1. Demand Load Calculation

Per 220.42, general lighting loads are computed at 3 VA per square foot. Per 220.14(H), receptacle outlets are calculated at 180 VA each, and are typically adjusted based on the load being served. Fixed Appliances: Any large fixed appliances (welder, compressor, etc.) will need to be individually calculated based on their nameplate ratings, and take into account noncontinuous vs continuous loads.2.

Article 220.61 Reduction Permitted

Since this is a 200A residential shop subpanel, you may be able to reduce the size of the neutral conductor compared to the ungrounded conductors. This is assuming that the conditions described in 220.61 are met. Namely, that you don't anticipate major non-linear loads (electronics/LED lighting/etc).

Key Point

Section 220.61(B)(1) states that the neutral load must not be assumed to be less than the sum of the loads on the 2 largest ungrounded conductors.
It is recommended to size the neutral to the same size as the ungrounded conductors (3/0 Cu).3.

Minimum Size Requirements



250.24(C)(1)

Requires the grounding electrode conductor (GEC) to the feeder neutral to be sized per Table 250.66. Table 250.66 states that for 3/0 AWG copper ungrounded conductors, you must have an 4 AWG copper GEC to ground the neutral at the detached structure.


250.32(A)

If the detached building has multiple circuits, a grounding electrode must be installed.

Conclusion and Recommendation
Considering the potential for unbalanced loads and the code requirements: I strongly advise using a 3/0 AWG copper neutral conductor. While a smaller neutral may be permitted based on load calculations, the small cost savings is not worth the potential liability that could arise from improper operation or damage to equipment. Using a full-sized neutral (same size as the ungrounded conductors) provides a safety margin and ensures you are adequately handling any potential unbalanced loads. Install a Grounding Electrode System (GES) at the detached structure. Common choices are ground rods or connection to the rebar of the concrete slab.

Important Reminders



Local Codes

Local jurisdictions may have additional requirements or amendments to the NEC. Always check with your local building department.


Voltage Drop

Remember to calculate voltage drop for your feeder run. Undersized conductors can lead to poor performance and potential damage to equipment.

Professional Consultation:
This information is for educational purposes only and should not be considered a substitute for professional electrical engineering advice. Engage a qualified electrician or electrical engineer to perform the necessary load calculations and ensure that your installation complies with all applicable codes and regulations.Disclaimer: I am an AI chatbot and cannot provide electrical advice. Consult a qualified electrician for all electrical work.* Flag for review