Question: I have this situation: A (50y old) building is flooding on the first floor with stormwater. Two 5HP sump pumps need to be added, but the emergency panel has no capacity. There are 395A connected, and the maximum capacity is 400A for the panel, transfer, main disconnect, and generator.However, in the existing plans, there’s a note in the panel schedule that says the following:"Provide lockout on both domestic water when fire pump is operating on emergency power."If this is correct, I could remove the load calculation of the new sump pumps from the generator.Additionally, I could increase the capacity of the transfer, main disconnect (normal power), add a subpanel and connect the new pumps to it. Generator should be the same because the removal of domestic water pumps calcs.Is my solution feasible? Do you have any other ideas?

Okay, let's break down your situation and potential solutions

Understanding the Problem
Overloaded Emergency Panel

Your emergency panel is maxed out at 400A, and adding two 5HP sump pumps will exceed this capacity. This is a serious problem as it violates electrical codes and creates a safety hazard.


Reliance on Generator

The sump pumps need to function during power outages, making connection to the emergency system essential.

Opportunity with Domestic Water/Fire Pump Interlock

The existing design includes an interlock that shuts off the domestic water when the fire pump is running on emergency power. This presents an opportunity to free up capacity on the generator circuit.

Your Proposed Solutions - Assessment
1. Leveraging the Domestic Water/Fire Pump Interlock Feasibility

Potentially very feasible, and the preferred first step. If you can accurately calculate and remove the load of the domestic water pumps from the generator load calculation and legally use that freed-up capacity for your sump pumps, this is the simplest and most cost-effective solution.

Important Considerations



Verification is CRITICAL

Meticulously verify the actual load of the domestic water pumps. Don't rely solely on nameplate data. Use a clamp meter to measure the actual current draw during operation under load.

Code Compliance

Ensure that the interlock and load shedding scheme meet all applicable electrical codes and fire codes. You'll need to demonstrate to the AHJ (Authority Having Jurisdiction) that the fire pump operation is prioritized and that the water pumps are reliably shed.


Domestic Water Pump Control

How are the domestic water pumps controlled? Are they simple pressure-activated, or do they have complex control systems? You need to understand this to ensure the interlock works correctly.

Documentation

Update all panel schedules and drawings to reflect the changes. Add a clear note explaining the interlock and the resulting load reduction on the emergency panel.


Testing

Thoroughly test the interlock to ensure it works as designed. Document the test results.

Why this is good

Reduces costs, avoids extensive rewiring.2.

Increasing Capacity of Normal Power Components + Subpanel
Feasibility

Potentially feasible, but more involved and likely more expensive. This involves upgrading the main disconnect, transfer switch (normal power side), and possibly the service entrance to the building. You would then add a new subpanel fed from the upgraded normal power system specifically for the sump pumps. The generator stays as it is now, without the sump pumps.

Important Considerations



Electrical Service Upgrade

The limiting factor here is likely the existing electrical service to the building. You need to determine if the existing service can handle the increased load. This may require a new transformer from the utility company. This can be costly and time-consuming.

Space

Do you have physical space for a larger disconnect, transfer switch, and a new subpanel?


Cost

This is a more expensive option due to equipment costs, labor for installation, and potential utility company fees.

Coordination

You'll need to coordinate with the utility company, electrical contractors, and potentially structural engineers.


Redundancy

This approach does not provide emergency backup power to the sump pumps. If utility power fails, the sump pumps will not operate unless you add a separate backup generator. This may not meet your requirements.

Other Ideas and Important Considerations
Sump Pump Efficiency



Consider ECM (Electronically Commutated Motor) Pumps

These pumps are significantly more energy-efficient than standard induction motor pumps. While more expensive upfront, they can reduce the load and operating costs. Calculate the reduced load requirements with ECM pumps vs standard pumps.

Load Shedding - More Aggressive Approaches



Analyze Other Emergency Loads

Carefully review all other loads connected to the emergency panel. Are there any non-essential loads that could be shed during a prolonged power outage? This might involve manual switching or an automated load shedding system. Consider these:

Emergency Lighting Levels

Can lighting levels be reduced during an emergency?


HVAC

Can HVAC be throttled back?

Elevators

Can elevators be switched to a "call-down" mode?


Professional Engineering Assessment



Hire a Qualified Electrical Engineer

This is the most important step. A qualified electrical engineer can:
Perform a thorough load calculation. Evaluate the existing electrical system. Develop code-compliant solutions. Prepare drawings and specifications. Work with the AHJ to obtain approvals.

Prioritized Action Plan
1. Engage an Electrical Engineer

This is crucial.2.

Verify Domestic Water Pump Load

Measure the actual load of the domestic water pumps under real-world operating conditions.3.

Analyze Existing Emergency Loads

Identify any non-essential loads that can be shed.4.

Evaluate ECM Sump Pumps

Investigate the potential for using more efficient sump pumps.5.

Develop a Solution

Based on the above data, the engineer will develop a solution that meets your requirements and complies with all applicable codes.6.

Obtain Approvals

The engineer will work with the AHJ to obtain the necessary permits and approvals.7.

Implement the Solution

Hire qualified electrical contractors to install the solution.8.

Test and Document

Thoroughly test the system and document the results.

Key Takeaways
Safety First

Don't attempt to overload the electrical system. It's a safety hazard.


Code Compliance is Essential

Ensure that all work complies with the National Electrical Code (NEC) and any local codes.

Professional Help is Required

This is not a DIY project. Hire a qualified electrical engineer and licensed electrical contractors.


Documentation is Key:
Keep detailed records of all work performed, including load calculations, drawings, specifications, and test results.By following these steps, you can develop a safe and reliable solution to address the stormwater flooding issue. Remember that the interlock is your best bet, but it needs a complete and professional approach. Good luck! Flag for review