Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Overhead Electrical Conductor Clearances

User: ROHM, Location: USA

Asked on: Friday, October 18, 2024 at 6:11 pm EDT
Answered on: Thursday, March 6, 2025 at 4:07 am EST

Question: I have a project to install a fire barrier wall near a transformer. The fire barrier will be grounded. The wall will be in close proximity to one of the overhead conductors on the transformer. It is a 13.8 KV conductor. Is there a minimum clearance requirement from that conductor to the fire barrier? I have not been able to find any specific NEC literature which states specific distances. If anyone can point me to such documents, that would be much appreciated. General opinions on the application are also welcome.

You're right to be concerned about clearance in this situation. While the NEC doesn't provide specific distances for fire barrier walls relative to energized conductors, it does have requirements for working spaces and clearances for other grounded objects that can be applied by analogy, along with considerations for induced voltage and potential fault scenarios. Here's a breakdown of where to look and what to consider

1. NEC Article 110.26 - Spaces About Electrical Equipment:
110.26(A) - Working Space

This section is the most relevant. While it primarily addresses working space
around electrical equipment requiring examination, adjustment, servicing, or maintenance while energized, the principle of maintaining safe clearance applies. You'll need to determine if the area around the transformer (including the fire barrier) is considered a working space. If so, 110.26(A) dictates a minimum clear distance based on voltage. For 13.8kV, you'll need to refer to Table 110.26(A)(1). The required clearance depends on the condition of the equipment and the grounded surface.

Condition 1

Exposed live parts on one side and no grounded parts or exposed live parts on the other side of the working space.

Condition 2

Exposed live parts on one side and grounded parts on the other side.


Condition 3

Exposed live parts on both sides of the working space (guarded as provided in 110.27(A) or guarded by suitable partitions or screens).For 13.8kV, the clearance is typically 3'6" to 4'0" depending on the condition. Condition 2, with a grounded object (the fire barrier) likely applies.



Why this matters for your fire barrier

Even if the fire barrier isn't directly considered
part of the electrical equipment itself, it's in very close proximity. If personnel might need to access the transformer for maintenance or inspection, the presence of the fire barrier could significantly restrict the necessary working space. This could make working on the energized transformer unsafe and violate NEC 110.26. Therefore, you should design to maintain the required working space even with the fire barrier in place.

2. ANSI C2 (National Electrical Safety Code - NESC)

While the NEC primarily covers building wiring, the NESC addresses utility and industrial power systems. While not legally binding unless adopted by the local authority, it offers valuable guidance on clearances.

NESC Rule 232 deals with vertical clearances of conductors from ground or other surfaces. It's geared more toward overhead lines, but the principles apply to your situation. It may have more stringent requirements than the NEC.


NESC Rule 233 covers horizontal clearances. Again, useful for assessing risks.3. Manufacturer's Recommendations

Consult the transformer manufacturer's documentation. They may specify minimum clearances around the transformer, including for grounded structures.

4. IEEE Standards

IEEE standards (like IEEE 1584 - Guide for Performing Arc-Flash Hazard Calculations) aren't legally binding, but they provide engineering best practices. While not directly addressing fire barriers, understanding potential arc flash hazards can influence your clearance decisions. Reduced clearances can exacerbate arc flash risks.

5. Local AHJ (Authority Having Jurisdiction)



Crucially, consult your local electrical inspector or building department. They have the final say on what's acceptable. They may have local amendments to the NEC or other relevant codes that you
must follow. Present your design and ask for their specific requirements.

Key Considerations Beyond Direct Code Requirements



Induced Voltage

A grounded object close to a high-voltage conductor can have induced voltage on it. Ensure the fire barrier is adequately grounded to prevent a shock hazard. This typically means multiple grounding connections.

Fault Current

Consider what would happen during a fault in the overhead conductor. Could the fire barrier become a path for fault current? Ensure it's properly grounded to handle potential fault currents.


Arc Flash Hazard

As mentioned above, proximity to energized conductors increases arc flash risk. An arc flash study might be required to determine safe working distances and PPE requirements. The fire barrier's presence might necessitate even greater PPE.

Maintenance

Will the fire barrier impede maintenance activities on the transformer?


Material of the Fire Barrier

Is the fire barrier material conductive? If so, the clearance requirements become more critical.

Future Modifications

Consider potential future additions or modifications to the transformer or surrounding area. Plan for adequate clearance to accommodate these changes.


Engineering Judgement

If you are not comfortable making the decision, it is best to consult a licensed Professional Engineer (PE).

Recommendations


Start with the NEC

Treat the area as a working space and adhere to Table 110.26(A)(1).
2.


Consult the NESC

Consider its more conservative clearance requirements.3.

Consult the Transformer Manufacturer

See if they have specific clearance requirements for the equipment.4.

Grounding

Ensure robust grounding of the fire barrier.5.

Arc Flash Study

Consider conducting an arc flash study, especially if clearances are tight.6.

Engage the AHJ

Discuss your design with the local electrical inspector before installation. This will save you potential rework and ensure compliance.7.

Documentation

Document your design decisions, including the rationale for the chosen clearances and grounding methods.

In summary: There's no single "magic number" in the NEC for the clearance between a grounded fire barrier and a 13.8kV conductor. However, by applying the principles of safe working space, considering induced voltage and fault current scenarios, and consulting the AHJ, you can design a safe and compliant installation. The most conservative approach is generally the best, as it prioritizes safety and minimizes potential hazards. Flag for review

Previous Question Next Question