User: sixexx6, Location: Southern California
Asked on: Saturday, October 19, 2024 at 1:46 am EDT
Answered on: Thursday, March 6, 2025 at 4:08 am EST
Question: Trying to install a flood light, when I identified the breaker it is a 20 amp. Looks like it has been one of the couple that has been replaced before. I'm using existing 14/2 romex which makes me question if the breaker is correct. (I thought that generally 14g goes with 15 amp) It is an old panel, probably 1988 with no identification labels except one small yellow sticker that says UL class CTR wich is not much information. If it is not a compatible breaker, what can I use instead and is there a way to tell what kind of panel this is without any labels? Most the breakers in the panel are BRYANT BRD BD, the one in question is CURTIS HAMMER BRD & A.
You are correct to be concerned. Here's a breakdown of the situation and what you should do
1. 14/2 Wire with a 20 Amp Breaker is a Problem:
Code Violation
National Electrical Code (NEC) and most local codes require that 14-gauge wire be protected by a 15-amp breaker. A 20-amp breaker on 14-gauge wire creates a significant fire hazard. The breaker is designed to trip if there's an overload, but a 20-amp breaker might not trip quickly enough to protect the 14-gauge wire from overheating and potentially causing a fire.
Over-Current Protection
Breakers are designed to protect the wire, not the device connected to it. While your floodlight might draw only a few amps, the wire needs to be protected from larger currents caused by shorts, faults, or overloads.
2. Immediate Action
Replace the 20-Amp Breaker with a 15-Amp Breaker IMMEDIATELY. This is the most crucial step. Go to your local hardware store (Lowe's, Home Depot, etc.) and purchase a 15-amp breaker that is compatible with your panel (see Step 3).3. Identifying the Panel Type
Bryant/Eaton
The fact that most of your breakers are Bryant BRD/BD strongly suggests your panel is a Bryant panel. Eaton acquired Bryant, so Eaton breakers are often compatible.
Check the Bus Bars
Carefully (with the breaker OFF and after verifying voltage is not present with a meter), look inside the panel where the breakers connect. Note the shape and configuration of the "bus bars" (the metal bars the breakers clip onto). Compare this to images online of Bryant/Eaton bus bar configurations. This is the best visual way to confirm panel compatibility.
Curtis-Hammer: The Curtis-Hammer breaker is a bad sign since it means it's a replacement breaker that is not the same brand and may be incompatible.4. Breaker Compatibility
Critical Importance
Breakers are NOT universally interchangeable. Using the wrong type of breaker can damage the panel, prevent proper tripping, and create a dangerous situation.
Bryant/Eaton BR or BD
Look for a 15-amp Bryant BR or BD series breaker, or an Eaton BR series breaker. These are generally compatible with older Bryant panels.
The Curtis-Hammer is Incorrect
The Curtis-Hammer breaker is definitely not a perfect match, which further supports that the previous breaker was incorrect.
5. Additional Considerations
Why the 20-Amp Breaker? Someone likely replaced the original 15-amp breaker with a 20-amp because it was tripping too often. This is a dangerous "fix." It indicates there might be a problem with the circuit – overload, short circuit, or faulty device. Investigate this after replacing the breaker. Floodlight Wattage
While it's likely the floodlight will be fine on a 15-amp circuit, double-check the wattage of your floodlight. 15 amps at 120 volts is 1800 watts (15 120 = 1800). Your total load on that circuit should not exceed 80% of the breaker's capacity (1440 watts).
Other Devices on the Circuit
What else is on that same circuit? Outlets? Other lights? Add up the wattage of everything to ensure you're not overloading the circuit.
Aluminum Wiring
If your home was built in the late 1960s or early 1970s, it might have aluminum wiring. Aluminum wiring has its own set of issues and requires special connectors and precautions. If you suspect aluminum wiring, consult a qualified electrician.
GFCI Protection
If the floodlight is in a wet or damp location (e.g., outdoors, near a faucet), it should ideally be on a GFCI-protected circuit for safety. You can either use a GFCI breaker or install a GFCI outlet upstream of the floodlight.
6. Steps to Replace the Breaker Safely
Turn off the main breaker in your panel to kill power to the entire panel.2. Test
Use a non-contact voltage tester to confirm that there is no power to the breaker you will be replacing. Test the surrounding breakers as well.3.
Remove the Panel Cover
Carefully remove the panel cover.4.
Remove the 20-Amp Breaker
Most breakers clip into the bus bar and are held in place by a retaining clip. Carefully unclip the 20-amp breaker and pull it out.5.
Install the 15-Amp Breaker
Clip the new 15-amp breaker into the same spot, making sure it's securely attached to the bus bar.6.
Replace the Panel Cover
Reinstall the panel cover.7.
Turn on the Main Breaker
Turn the main breaker back on.8.
Turn on the 15-Amp Breaker
Turn on the new 15-amp breaker and test your floodlight.
7. Important Warnings
Electricity is Dangerous
If you are not comfortable working with electricity, hire a qualified electrician. Incorrect wiring can cause fires, shocks, and even death.
Local Codes
Your local electrical codes may have specific requirements. Check with your local building department.
Don't just replace a tripping breaker with a larger one. This is a serious fire hazard. Diagnose the underlying problem.
In Summary
Replace the 20-amp breaker with a 15-amp Bryant/Eaton BR or BD breaker immediately.2. Carefully investigate the panel to confirm it is Bryant/Eaton.3. Determine why the original breaker was likely replaced with a 20-amp breaker.4. Consider GFCI protection for the floodlight if required by code.5. If you're unsure about anything, call a qualified electrician. Flag for review