Question: 250.119 allows the equipment ground in a multi conductor cable to be re identified. It seems to specifically allow this in NM cable. What is the need for this change?
You're referring to NEC section 250.119, which deals with the use of insulated or covered equipment grounding conductors. Let's break down the issue and the reasoning
The Specific Rule (Simplified)
NEC 250.119 permits re-identification of an insulated grounding conductor, under specific circumstances, when it's larger than 6 AWG. This means you can take a green insulated wire (or bare wire that you've covered with green sleeving or tape) and, using green tape, green sleeving, or green paint, mark it to serve as the equipment grounding conductor. Critically, the re-identification has to be permanent and readily visible at every point where the conductor is accessible (termination, junction, splice, etc.).
Why is Re-identification Allowed, and What About NM Cable?
The underlying and unwritten part of the question is, "Why do we need to re-identify an already green wire if it's already the right color?" And you're right, that wouldn't make sense!The trick is in the size. NM cable (Romex) that contains large conductors (larger than #6 AWG) is rare. Therefore, we need to look at other types of cable and wiring that are typically much larger, such as THHN/THWN conductors run in conduit.The scenario where 250.119 comes into play is when you might have a situation where you are using a non-green insulated conductor for the equipment grounding conductor.Here's the reasoning and a common scenario where this comes up:1. Larger Conductors are Expensive
Large green insulated conductors (THHN/THWN larger than #6) are often more expensive and less readily available than other colors (typically black or white). This price and availability difference can be significant for larger installations, especially in commercial or industrial settings.2.
Flexibility and Inventory Management
Allowing the use of other colors, marked green, gives electricians and contractors more flexibility. They might have a large spool of black #4 AWG THHN/THWN on hand, but not the same size in green. This allows them to use the existing stock and re-identify it, reducing downtime and inventory costs.3.
No Safety Reduction (When Done Correctly)
When properly and permanently marked with green tape, sleeving, or paint at all accessible points, the safety is not compromised. The electrician and any future person working on the system can easily identify the conductor as the equipment grounding conductor.4.
Note on NM cable
As mentioned previously, most NM cable will not be larger than #6 AWG. This is because most residential services are 200A or smaller, and the size of the service entrance conductors will be typically no larger than #4. However, if you were to encounter NM cable with conductors larger than #6 AWG, you could theoretically use the same rule for a non-green equipment grounding conductor. But this is very unlikely.
Important Caveats Sizes 6 AWG and Smaller
You CANNOT re-identify a conductor as a grounding conductor if it is 6 AWG or smaller. Grounding conductors of this size MUST be green or bare. This prevents confusion and ensures easy identification in smaller wiring systems.
Permanent and Readily Visible
The markings MUST be durable and easily seen at all points where the conductor is accessible. Think about the long-term life of the installation. Will the tape peel off after a few years?
Not for the Neutral (Grounded) Conductor
This rule ONLY applies to the
equipment grounding conductor, NOT the neutral (grounded) conductor. The grounded (neutral) conductor must be white or gray throughout its entire length, as per NEC 200.6. Only Insulated Conductors
Only insulated conductors can be re-identified.
In Summary
The re-identification rule in 250.119 is a practical exception to the color-coding rules, primarily aimed at reducing costs and increasing flexibility in larger electrical installations while maintaining safety through clear and permanent identification of the equipment grounding conductor. It is unlikely you would encounter this scenario in typical NM cable applications. It is not meant to let people get away with not using green or bare wire when those options are readily and cost-effectively available. It is only a tool to be used where needed. Flag for review