Question: Simple problem that I’m not sure of the answer: 120/240V panel. All loads are 120VI’m assuming you just take A phase minus B phase to calculate the Amps on the neutral. Am I correct?Thanks
You are correct. In a 120/240V panel with only 120V loads, the current on the neutral is the difference between the current on phase A and phase B.Here's why: 120/240V Split-Phase System
This type of panel has two "hot" legs (A and B), each providing 120V to neutral. The voltage between A and B is 240V.
120V Loads
A 120V load is connected between either phase A or phase B and the neutral.
Current Flow
Current flows from the source (either A or B) through the load and back to the source through the neutral conductor.
Neutral as a Return Path
The neutral serves as the return path for both phase A and phase B currents.
Current Summation
If the current on phase A exactly matches the current on phase B, the neutral current would be zero (because the currents are 180 degrees out of phase and would cancel each other out).
Imbalance Creates Neutral Current
However, in almost all real-world scenarios, the loads on phase A and phase B are not perfectly balanced. The difference between the current on phase A and phase B is the current that flows on the neutral.
Formula
Neutral Current = |Current on Phase A - Current on Phase B|
Example
Phase A: 15 amps Phase B: 10 ampsNeutral Current = |15 amps - 10 amps| = 5 amps
Important Considerations
Harmonics
In reality, harmonic currents can complicate this. Triplen harmonics (3rd, 9th, 15th, etc.) are additive in the neutral and can cause the neutral current to exceed the current on either phase A or phase B. However, for typical residential or small commercial installations without significant non-linear loads (like variable frequency drives or large numbers of electronic devices), this is usually not a major concern.
Safety: It is critical that the neutral connection is solid and unbroken. A broken neutral can cause dangerous overvoltages on 120V circuits.In summary, your understanding is accurate for calculating neutral current in a balanced 120/240V system with only 120V loads. Just remember that harmonic currents can introduce additional complexity in certain situations. Flag for review