Topic: Neutral to Ground Bond

User: cgamad550, Location: United States

Asked on: Sunday, October 20, 2024 at 10:30 am EDT
Answered on: Thursday, March 6, 2025 at 4:11 am EST

Question: I guys I have a question. I put a new panel in my grandmother's house it was probably 70 years old and a huge mess.In the old panel neutral to ground was bonded.At the panel right below the meter ( also very very old ) the service wires comes down into main lugs only ( no main breaker/ disconnect ) the first panel with a main breaker is the one I installed inside.My question is would the inside panel with a main breaker be the actual first means of disconnect? And if do would I need to bond neutral to ground at the inside panel I just installed?Thanks in advance guys

Okay, let's break this down to ensure you have a safe and code-compliant installation.

Understanding the Situation Old Panel Replaced

You replaced a very old panel inside the house.


Old Panel's Bonding

The old panel had neutral and ground bonded together (common practice historically in older installations).

Meter Setup

You describe the service wires coming directly from the meter into
main lugs only in a panel outside, below the meter. There is NO main breaker/disconnect at this location.

New Panel Location

Your new panel with a main breaker is installed inside the house.

Key Question: Where is the First Means of Disconnect?


This is the critical point. The National Electrical Code (NEC) requires a readily accessible service disconnect. Based on your description: Your new panel with the main breaker is the first means of disconnect. This is because the outside "panel" with just lugs does not have a breaker or disconnecting means. It is only a junction point.

Bonding Neutral to Ground: A CRITICAL NO-NO at the New Panel
Do NOT bond neutral to ground at the new panel. This is absolutely crucial for safety. The NEC (National Electrical Code) requires that the neutral-to-ground bond only occur at the service entrance.

Why NOT Bond Neutral to Ground at the new Panel?

Bonding the neutral and ground at more than one location creates parallel paths for neutral current. This can lead to:1. Stray Voltage

Voltage on the grounding conductors.2.

Overheated Neutral

Overloading the neutral conductor.3.

Increased Risk of Electric Shock

If a ground fault occurs, the return current will be split between the neutral and the ground, increasing the chance of voltage on the grounding system.

How to Properly Wire the New Panel


Four-Wire Feed

You need a four-wire feed from the service entrance lugs outside to the new panel: Two Hot (ungrounded) conductors. One Neutral (grounded) conductor. One Equipment Grounding conductor.2.

Separate Neutral and Ground

Connect the neutral conductor to the neutral busbar in the new panel. This busbar should be isolated from the panel enclosure. Connect the equipment grounding conductor to the ground busbar in the new panel. This busbar is bonded to the panel enclosure.

Important Considerations and Recommendations



NEC Compliance

What you have described is not up to code. The first means of disconnect must be accessible.

Inspection



I strongly urge you to have a qualified, licensed electrician inspect your work.
This is not just a suggestion; it's a matter of safety and ensuring compliance with local codes. Electrical work done incorrectly can create serious hazards (fire, electric shock). Upgrading the Service Disconnect

The ideal solution would be to install a proper service disconnect (main breaker) in a suitable enclosure outside, right after the meter. This would then become the service entrance, and you would bond neutral to ground only in that outdoor enclosure.

Local Codes

Local codes may have specific requirements that go beyond the NEC. An electrician will be familiar with these.


Grandmother's Safety

Given the age of the house and the previous state of the electrical system, ensure that all outlets are properly grounded and consider installing GFCI (Ground Fault Circuit Interrupter) protection in appropriate areas (bathrooms, kitchen, outdoors).

In summary

1. The new panel, with a breaker, is your first means of disconnect.
2.


DO NOT
bond neutral and ground at the new panel.3. Have a licensed electrician inspect your work and advise on the best way to bring the entire system up to code. This likely involves installing a proper service disconnect outside.Safety is paramount. Please don't hesitate to ask more questions if you're unsure about anything. Good luck! Flag for review